Index
Overview about the ASCII objects/commands of the AX2000 resp. AX2500 drive, effective from dedicated firmware revisions on (VER).
ASCII Object
Short Description
ACC
Acceleration Ramp
ACCR
Acceleration Ramp for homing/jog modes
ACCUNIT
Type of acceleration setpoint for the system
ACTFAULT
Active Fault Mode
ACTIVE
Output stage active/inhibited
ACTRS232
Activate RS232 Watchdog
ADDR
Multidrop Address
ADDRFB
Fieldbus address at AX2500 Slave
AENA
Software Auto-Enable
ALIAS
Drive Name
AN10TX
AN11NR
No. Of INxTRIG variable, that is changed analog
AN11RANGE
Range of the analog change of INxTRIG
AN1TRIG
Scaling of the analog output 1
AN2TRIG
Scaling of the analog output 2
ANCNFG
Configuration of Analog Input
ANDB
Dead Band of the Analog Velocity Input Signal
ANIN1
Voltage at Analog Input SW1
ANIN2
Voltage at Analog Input SW2
ANOFF1
Analog Offset for input SW1
ANOFF2
Analog Offset for input SW2
ANOUT1
Configuration of the Analog Output 1
ANOUT2
Source of the Analog Output 2
ANZERO1
Zero Analog Input SW1
ANZERO2
Zero Analog Input SW2
AUTOHOME
AVZ1
Filter Time Constant Input SW1
Selection of Remote Address
BCC
EEPROM check sum
BOOT
Type of Boot Initialization
BQDC
Defines the Center Damping of the Bi-quad Filter
BQDR
Defines the Damping Ratio of the Bi-quad Filter
BQFC
Center Frequency of the Bi-Quad Filter
BQFR
Frequency Ratio of the Bi-quad Filter
BQMODE
Select Compensation Filter Mode for the Velocity Control
CALCCOG
Determing the Cogging Table
CALCHP
Determining the Hiperface Parameters
CALCRK
Calculate resolver parameters
CALCRP
Calculate resolver phase
CBAUD
Baud Rate CAN Bus
CDUMP
Current Loop Parameter Dump
CLRFAULT
Clear Drive Fault
CLRHR
Bit 5 of status register STAT is cleared
CLRORDER
Deleting a Motion Task
CLRWARN
Warning mode
CMDDLY
Command Delay Time for RS232
COGGING
Enable of Cogging Compensation
COLDSTART
Drive Reset
CONFIG
Adaption and Conversion of Entered Parameter
CONTINUE
Continue last position order
CPHASE
Deactivate Motor Connection Detection
CTUNE
Calculate current parameters
CUPDATE
Program Update (CAN Bus)
DAOFFSET1
Analog Offset Output 1
DAOFFSET2
Analog Offset Output 2
DEC
Deceleration Rate
DECDIS
Deceleration used on Disable Output Stage
DECR
Deceleration Ramp for homing/jog modes
DECSTOP
Quick Stop – braking ramp for emergency situations
DENA
DPR software disable reset mode
DEVICE
Device ID
DICONT
Drive Continuous Current
DIFVAR
List Variables with Values
DILIM
DPR current limit
DIPEAK
Drive Peak Rated Current
DIR
Count Direction
DIS
Software-Disable
DISDPR
Disable DPR access
DOVRIDE
Digital Override Factor
DPRILIMIT
Digital Limiting of the peak Current via DPR
DPWM
Output Frequency of the Power Stage
DREF
Direction for Homing
DRVCNFG
Configuration Variable for CAN-Bus
DRVSTAT
internal Status information
DR_TYPE
Gives the Output Stage Indentification
DUMP
List All EEPROM Variables with Values
DUMPDIF
List of Parameter unequal default setting
EN
Software-Enable
ENCCAPT
no function
ENCIN
Encoder Pulse Input
ENCLINES
SinCos Encoder Resolution
ENCMODE
Selection of Encoder Emulation
ENCOUT
Resolution Encoder Emulation EEO (ROD)
ENCZERO
Zero Pulse Offset EEO (ROD)
ERND
End position of modulo axes
ERRCODE
Activated Fault Messages
ERRCODES
Output Error Register
ESPEED
Maximum velocity corresponding to the Feedback Type
EXTLATCH
Selection of the Source of the Latch Inputs
EXTMUL
ext. Encoder multiplier
EXTPOS
Position Feedback + Control Type
EXTWD
external watch dog (Fieldbus)
FB2RES
Number of Counts of an ext. Encoder per Motorturn
FBTYPE
Selection of Encoder or Resolver
FBTYPEX
Display the detected feedback device
FILTMODE
Feedback Filter Mode
FLASH
FLTCNT
Fault Frequency
FLTCNTS
Fault Frequency
FLTHIST
Fault History: Display last 10 faults
FLTHISTS
FLUXM
Rated Flux Level of Permanent Magnet Motor
FOLDMODE
Foldback Mode
FPGA
Select different FPGA functionalities
FW
Displays the Version Number of the Firmware
GDTX
Number of Actual Value Data Words via Modbus
GEARI
Input Factor for Electronic Gearing
GEARMODE
Electronic Gearing Mode
GEARO
Output Factor for Electronic Gearing
GET
Scope: output data
GF
Proportional Gain of the Flux Controller
GFTN
Integral Action Time of the Flux Controller
GKC
Compensation Gain of the Flux Controller
GP
Position Control Loop: Proportional Gain
GPFBT
Position Control Loop: Feed Forward for Actual Current
GPFFT
Position Control Loop: Feed Forward for Current Setpoint
GPFFV
Position Control Loop: Feed Forward for Velocity
GPTN
Position Control Loop: Integral-Action Time
GPV
Proportional Gain of the Velocity Controller
GV
Velocity Control Loop: Proportional Gain
GVD
Derivate Part in the Velocity Controller
GVDT
Filter Time Constant of the D-Part of the Velocity Controller
GVFBT
Velocity Control Loop: Time Constant First Order Tacho Filter
GVFILT
Velocity Control Loop: Part of the Output that is filtered [%] by GVT2
GVFR
PI-PLUS Actual Velocity Feedforward
GVT2
Velocity Control Loop: Second Time Constant
GVTN
Velocity Control Loop: I-Integration Time
HACOFFS
Hiperface Cosinus Offset (absolut)
HAFACT1
Hiperface Gain Factor (absolut)
HASOFFS
Hiperface Sinus Offset (absolut)
HDUMP
Output all sin/cos (Hiperface) variables
HELP
Output Parameter Help Information
HICOFFS
Hiperface: Cosine-Offset (incremental track)
HIFACT1
Hiperface: Sin/Cos Gain Factor (incremental track)
HISOFFS
Hiperface: Sin/Cos Offset (incremental track)
HRESET
Hiperface: Load Default Parameters
HSAVE
Hiperface: Save Parameters in Encoder
HVER
Output the Hardware Version
I
Current Monitor
I2T
Average (rms) current [[I2T Loading]
I2TLIM
I2T Warning
ICMD
Current Setpoint
ICMDVLIM
Velocity Limit in Current Control
ICONT
Rated Current
ID
D-component of Current Monitor
IDUMP
Output Current Limit List
IMAX
Current Limit for Drive/Motor Configuration
IN
List Analog Voltage Values
IN1
Status of Digital Input 1
IN1MODE
Function of Digital Input 1
IN1TRIG
Variable for IN1MODE
IN2
Status of Digital Input 2
IN2MODE
Function of Digital Input 2
IN2PM
In-Position 2 Mode
IN2TRIG
Variable for IN2MODE
IN3
Status of Digital Input 3
IN3MODE
Function of Digital Input 3
IN3TRIG
Variable for IN3MODE
IN4
Status of Digital Input 4.
IN4MODE
Function of Digital Input 4
IN4TRIG
Variable for IN4MODE
INHCMD
Command buffer for high level
INHCMDX
Command buffer for high level (INxMODE=31,34)
INLCMD
Command buffer for low level
INLCMDX
Command buffer for low level (INxMODE=31,34)
INPOS
Status of In-Position Signal
INPT
In-Position Delay
INS0
State of Input A0 of the I/O Option Card
INS1
State of Input A1 of the I/O Option Card
INS2
State of Input A2 of the I/O Option Card
INS3
State of Input A3 of the I/O Option Card
INS4
State of Input A4 of the I/O Option Card
INS5
State of Input A5 of the I/O Option Card
INS6
State of Input A6 of the I/O Option Card
INS7
State of Input A7 of the I/O Option Card
INS8
State of FSTART_IO of the I/O Option Card
INTERPOL
Type of Interpolation in OPMODE 5 and 6
IO11A
Behaivior of the start input at the I/O expansion
IO11IN
Functionality of the Inputs of the I/O Option Board
IPEAK
Application Peak Current
IPEAKN
Negative Peak current Limit
IQ
Q-Component of Current Monitor
ISCALE1
Scaling of Analog Current Setpoint 1
ISCALE2
Scaling of Analog Current Setpoint 2
ISTFR
Velocity dependant Friction Compensation
J
Service Function: Constant Velocity
K
Kill (=Disable)
KC
I-Controller Prediction Constant
KEYLOCK
Locks the push buttons
KTN
Current Controller Integral-Action Time
L
Stator Inductance of the Motor
LASTWMASK
Fault history of WMASK
LATCH16
Latched 16-bit Position (positive edge)
LATCH16N
Latched 16-bit Position (negative edge)
LATCH32
Latched 32-bit Position (positive edge)
LATCH32N
Latched 32-bit Position (negative edge)
LATCHX16
LATCHX16N
LATCHX32
Latched External 32-bit Position (positive edge)
LATCHX32N
Latched External 32-bit Position (negative edge)
LDUMP
Parameter Output of Motor Data
LED1
State of Display 1 Segment
LED2
State of Display 2 Segment
LED3
State of Display 3 Segment
LEDSTAT
Display page
LIST
List All ASCII Commands
LOAD
Load parameters from serial EEPROM
M
Read/write Macro Variable
MAXSDO
Number of Objects of the Parameter Channel
MAXTEMPE
Ambient Temperature Switch off Threshold
MAXTEMPH
Heat Sink Temperature Switch off Threshold
MAXTEMPM
Motor Temperature Switch off Threshold
MBPDRVSTAT
State of the Modbus+ Network
MBPSET
Address selection of Modbus+
MBRAKE
Select Motor Holding Brake
MCFW
The Correction Factor of the Field Weakening
MCTR
Correction Factor of the rotor time constant
MDBCNT
Number of Motor Data Sets
MDBGET
Get Actual Motor Data Set
MDBLIST
List of Motor Data Sets
MDBSET
Set Actual Motor Data Set
MDRV
Selection of Multidrive Functionality
MDUMP
Display Present Motor Parameters
MH
Start Homing
MICONT
Motor Continuous Current Rating
MIMR
Magnetizing Current (Induction Motor)
MIPEAK
Motor Peak Current Rating
MJOG
Start Jog Mode
MKT
Motor KT
MLGC
Current Control loop Adaptive Gain (Q-component at rated current)
MLGD
Adaptive Gain for Current Control loop, D-component
MLGP
Current Control loop Adaptive Gain (Q-component at peak current)
MLGQ
Absolute Gain of Current Control loop
MNAME
Motor Name
MNUMBER
Motor Number
MONITOR1
Monitor 1 Output voltage
MONITOR2
Monitor 2 Output Voltage
MOVE
Start Motion Task
MPHASE
Motor Phase, Feedback Offset
MPOLES
Number of Motor Poles
MRD
Homing to Resolver Zero, Mode 5
MRESBW
Resolver Bandwidth
MRESD
Damping of the Luenberger Observer
MRESPOLES
Number of Resolver Poles (Multispeed)
MRS
Winding Resistance of the Stator Phase-Phase
MSERIALNO
Serial no of the motor for encoder feedback
MSG
Enable / Disable All Messages via RS232
MSLBRAKE
DEC ramp at sensorless emergency stop
MSPEED
Maximum Rated Motor Velocity
MTANGLP
Current Lead
MTMUX
Presetting for motion task that is processed later
MTR
Rotor Time Constant
MTYPE
Motor Type
MUNIT
Unit of the Velocity dependant motor parameters
MVANGLB
Velocity-dependent Lead (Start Phi)
MVANGLF
Velocity-dependent Lead (Limit Phi)
MVANGLP
Velocity-dependent Lead (Commutation Angle)
MVR
Beginning Velocity of the field weakening
M_1000
Display 1 msec Macro Program
M_125
Display 125 microsecond Macro Program
M_1600
Display 16 msec Macro Program
M_250
Display 250 microsecond Macro Program
M_250P
M_4000
Display 4 msec Macro Program
M_DISABLE
Display the “Disable” Macro Program
M_ENABLE
Display the “Enable” Macro Program
M_INIT
Display the “Init” Macro Program
M_IRQ
Display the “Interrupt” Macro Program
M_RESET
Recompile Macro Programs
M_SMACRO
Display System Macros
M_TASK
Display the Main Macro Program
M_UMACRO
Display User Macros
NONBTB
Mains-BTB Check On/Off
NREF
Homing Mode
NREFMT
Homing wih following motion task
O1
State of Digital Output 1
O1MODE
Function of Digital Output 1
O1TRIG
Auxiliary Variable for O1MODE
O2
State of Digital Output 2
O2MODE
Function of Digital Output 2
O2TRIG
Auxiliary Variable for O2MODE
OBJCO
Mirror CAN - Objects for debug
OCOPY
Save/copy Motion Tasks
OLIST
List of Motion Task Data
OPMODE
Operating Mode
OPTION
Option Slot ID
ORDER
Set Motion Task Parameters
OS1
Set/Reset of "Posreg1" of the I/O Option Card
OS2
Set/Reset of "Posreg2" of the I/O Option Card
OS3
Set/Reset of "Posreg3" of the I/O Option Card
OS4
Set/Reset of "Posreg4" of the I/O Option Card
OS5
Set/Reset of "Posreg5" of the I/O Option Card
OVRIDE
Override Function for Motion Tasks
O_ACC1
Acceleration Time 1 for Motion Task 0
O_ACC2
Acceleration Time 2 for Motion Task 0
O_C
Control Variable for Motion Task 0
O_DEC1
Braking Time 1 for Motion Task 0
O_DEC2
Deceleration Time 2 for Motion Task 0
O_FN
Next Task Number for Motion Task 0
O_FT
Delay before Next Motion Task
O_P
Target Position/Path for Motion Task 0
O_V
Target Speed for Motion Task 0
P1P16
Fast Position Register 1 ... 16
PASSCNFG
Password Function
PBAL
Actual Regen Power
PBALMAX
Maximum Regen Power
PBALRES
Select Regen Resistor
PBAUD
Profibus Baud Rate
PDUMP
List All Position Control Variables
PE
Actual Following Error
PEERCOP
Number of Data Words (Command) at Modbus+
PEERCOPS
PEINPOS
In-Position Window
PEMAX
Max. Following Error
PFB
Actual Position from Feedback Device
PFB0
Position from External Encoder
PGEARI
Position Resolution (Numerator)
PGEARO
Position Resolution (Denominator)
PIOBUF
Profibus data
PMODE
Line Phase Error Mode
PNOID
PROFIBUS ID
POP
Generate Current Step
POPI
Current Level for POP Command
POPI2
POPV
Max. Speed Level for POP Command
POSCNFG
Axes Type
POSRSTAT
Status of Fast Position Registers 1 ... 16
PPOTYP
Profibus PPO Type
PRBASE
Position Resolution
PRD
20-bit Position Feedback
PROMPT
Select RS232 Protocol
PSTATE
Profibus Status
PTARGET
Last Target Position
PTBASE
Time base for the external trajectory
PTEACH
Teach-In Function
PTMIN
Min. Acceleration Ramp for Motion Tasks
PUNIT
Set Resolution of the Position
PV
Actual Velocity (Position Control Loop)
PVMAX
Max. Velocity for Position Control
PVMAXN
Max. (Negative) Velocity for Position Control
RDP
Activate Racjk Drive Panel Mode
RDPBIAS
Rack Drive Panel Bias Current
RDPCLAMP
Max. Velocity Offset of the Rack Drive Panel Circuit
RDPINT
Rack Drive Panel Test Variable
RDPKI
Integral gain of Rach Drive Panel
RDPKP
Proportional Gain of Rach Drive Panel
RDPON
Test Variable Rack Drive Panel
READNIMP
Read/Set the EEO (ROD) Zero-Pulse Offset
READY
Status of the Software Enable
RECDONE
Scope: Recording Done
RECING
Scope: Recording in Progress
RECOFF
Scope: Cancel Scope Recording
RECORD
Scope: Capture Data for Recording
RECRDY
Scope: Status of RECORD Function
RECTRIG
Scope: Activate Recording Function
REFIP
Peak Rated Current for Homing 7
REFLS
Behavior of the Hardware Limit switches at Homing Move
REFMODE
Source of the Zero Pulse in Homing Mode
REFPOS
Reference Switch Position
REMOTE
Status of the Hardware Enable
RESPHASE
Resolver Phase
RK
Gain Adjust for Resolver Sine Signal
ROFFS
Reference Offset
ROFFS0
Reference Offset for the second Encoder Feedback
ROFFS2
Position offset for "absolute Gearing"
RS232T
RS232 Watch Dog
RSTFW
RSTVAR
Restore Variables (Default Values)
RXPDO1A
RX-PDO 1 parameter selection
RXPDO1B
RX-PDO 1 Mapping Settings
S
Stop Motor and Disable Drive
SAVE
Save Data in EEPROM
SBAUD
Sercos: Baud Rate
SCAN
Detect CAN Stations
SCANX
Restart internal communication of AX2500
SDUMP
List Speed/Velocity Limits
SERCERR
Display Error State of Object SERCOS
SERCLIST
Set Sercos IDN Pointer
SERCOS
Read the Data of an Sercos IDN
SERCSET
Set Sercos Settings
SERIALNO
Drive Serial Number
SETREF
Set Reference Point
SETROFFS
Automatic setting of ROFFS
SETVCT
Select a VCT Entry
SLEN
Sercos Optical Range
SLOTIO
I/O-Expansion Card: I/O States
SMNUMBER
Stored Motor Number in the feedback Device
SPHAS
Sercos Phase
SPSET
Enable for S-curve
SRND
Start Position of Modulo Axes
SSIGRAY
Select SSI Code
SSIINV
SSI Clock
SSIMODE
SSI Mode
SSIOUT
SSI Baud Rate
SSTAT
Sercos Status
STAGECODE
Power Stage Identification
START
STAT
Drive Status Word
STATCODE
Plain Text Warnings
STATCODES
Status Variable “Warnings”
STATIO
I/O Status
STATUS
Detailed Amplifier Status
STEP
Service Operation (STEP Command)
STOP
Stop Motion Task
STOPMODE
Brake Response for Disable
SWCNFG
Configuration of Position Registers 1 ... 4
SWCNFG2
Configuration of Position Registers 0 and 5
SWE0
Position register 0
SWE0N
Position register 0 (Cam)
SWE1
Position register 1
SWE1N
Position register 1 (Cam)
SWE2
Position register 2
SWE2N
Position register 2 (Cam)
SWE3
Position register 3
SWE3N
Position register 3 (Cam)
SWE4
Position register 4
SWE4N
Position register 4 (Cam)
SWE5
Position register 5
SWE5N
Position register 5 (Cam)
SYNCSRC
Source for Fieldbus Synchronization
T
Digital Current Setpoint
TASK
Task Workload
TBRAKE
Disable Delaytime with Holding Brake
TBRAKE0
Enable Delaytime with Holding Brake
TEMPE
Ambient Temperature
TEMPH
TEMPM
Motor Temperature
TIMEMBP
TRJSTAT
Status2 Information
TRUN
Run-time counter
TXPDO1A
TX-PDO1 Mapping - Setup
TXPDO1B
UCOMP
Backlash Compensation
UID
User-ID
UID1
Unused Variable for Customer use
UPDATE
Program Update via RS232
UVLTMODE
Undervoltage Mode
V
Actual Velocity
VBUS
DC-bus voltage
VBUSBAL
Maximum Line Voltage
VBUSMAX
Maximum DC-bus Voltage
VBUSMIN
Minimum DC-bus Voltage
VBW
Generate Bode Diagram
VCMD
Internal Velocity Setpoint in RPM
VCOMM
Velocity Threshold for Commutation error
VCTAB
Define a VCT Entry
VDUMP
List all Velocity Controller Variables
VEL0
Standstill Threshold
VER
Firmware Version
VEXTRES
Adjustment of the speed of the external Encoder
VF
Actual Velocity in Floating Point Format
VJOG
Speed for Jog Mode
VLIM
Max. Velocity
VLIMN
Max. Negative Velocity
VLO
Software Resolver/Digital Converter Feedforward
VMAX
Maximum System Speed
VMIX
Velocity Mix: Feedback / external Encoder
VMUL
Velocity Scale Factor
VOSPD
Overspeed
VREF
Speed for Homing
VREF0
Homing Mode Reduction factor
VSCALE1
SW1 Velocity Scaling Factor
VSCALE2
SW2 Velocity Scaling Factor
VSTFR
Velocity for max. Friction Compensation
VTUNE
Calculate Velocity Control Loop Parameters
VUNIT
Systemwide Definition of Velocity / Speed
WMASK
Warning as Fault Mask
WPOS
Enable Position Registers
WPOSE
Enable Fast Position Registers 1 ... 16
WPOSP
Polarity of Fast Position Registers 1 ... 16
WPOSX
Mode of Fast Position Registers 1 ... 16
WSAMPL
Minimum Move of W&S Mode
WSTIME
Action Time of the W&S - Funktion