BAC_AC_SE_3_4_1_1_1_0
Application
Plant call template for a temperature-controlled ventilation system.
The main tasks of the template are:
- Plant control with the different operation modes and set values
- Temperature control for the selected sequence elements
Plant key
Ventilation system with inlet and outlet air fan and thermal air treatment
Type: BAC_AC_SE
Strategy | Fan | Preheater | Cooler | Energy recovery | Mixed air |
Inlet air control (simple) | 1 | 1-stage | 1 | No | 0 | No | 0 | No | 0 | No | 0 |
Inlet air control | 2 | 2-stage | 2 | Yes | 1 | Yes | 1 | plate | 1 | Yes | 1 |
Outlet air/inlet air cascade (simple) | 3 | Speed | 3 |
| Recuperative | 2 |
Outlet air/inlet air cascade | 4 | Pressure | 4 |
| Rotation | 3 |
| Volume rate of flow | 5 |
Outlet air/inlet air cascade (simple) | 3 | Pressure | 4 | Preheater | 1 | Cooler | 1 | Energy recovery | 1 | Mixed air | 0 |
Interface
System diagram
Block diagram
Operation modes
The plant is switched on via a timer program or a manual system switch (software).
The plant can assume the operation modes listed in the table.
udiOpMod | ||
OPMOD_AC_OFF | 1 | Aus//Off |
OPMOD_AC_ON | 2 | Ein//On |
OPMOD_AC_EMERG | 3 | Notfall//Emergency |
OPMOD_AC_MANOFF | 4 | Hand aus//Manual off |
OPMOD_AC_MANON | 5 | Hand ein//Manual on |
OPMOD_AC_FRST | 6 | Frost//Frost |
OPMOD_AC_SMEXTTPRG | 7 | Entrauchung Programm//Smoke extraction programm |
OPMOD_AC_SMEXTTSUA | 8 | Entrauchung Zuluft//Smoke extraction supply |
OPMOD_AC_SMEXTTEXHA | 9 | Entrauchung Fortluft//Smoke extraction exhaust |
OPMOD_AC_FIRE | 10 | Feuer//Fire |
OPMOD_AC_NGTCOL | 11 | Nachtkühlung//Night cooling |
OPMOD_AC_COLDWNPRTC | 12 | Stützbetrieb,Auskühlschutz//Cool down protection |
OPMOD_AC_OVRHTGPRTC | 13 | Überhitzungsschutz//Over heating protection |
OPMOD_AC_ALM | 14 | Störung//Alarm |
OPMOD_AC_FORCVENT | 15 | Zwangsbelüftung//Forced ventilation |
OPMOD_AC_CENTSWIOFF | 16 | Zentralabschaltung//Central switch-off |
Fire alarm
In case of a fire alarm, all switch-on conditions are overridden, and the system switches off. The smoke extraction functions are enabled. The two binary inputs SmExttSuA / SmExttExhA can be used for the 3 smoke extraction scenarios listed above.
Fault shutdown
The plant switches off in the event of the following faults or status messages:
- Status message fire alarm (BAC_AC_StartT_01)
- Status message frost alarm (BAC_FrstPrt_01)
- Fan fault (BAC_AC_ExtAFan_FC_01 / BAC_AC_SuAFan_FC_01)
- Fault in the outside or exhaust air damper (BAC_AC_OuADmp2P_01_15 / BAC_AC_ExhADmp2P_01_15)
Plant startup
If the plant is switched on in cold weather, control of the return temperature of the hot-water air heater is activated in the prerinsing plant step PLTSTP_AC_PRERI. This procedure is intended to prevent the freezing of the hot-water air heater during the plant start-up.
Temperature control
In this plant template a room air inlet air cascade is realized as control strategy.
In the templates BAC_AC_SpRmT_01 / BAC_AC_CasCtrlT_01 , the set values for the plant are generated and relayed to the sequence controllers.
Program description
Instance | Type | Task |
Alm | Plant alarms | |
ComnMsg | Collective plant messages | |
ExhAT | Call template exhaust air temperature | |
ExtAT | Call template outlet air temperature | |
OuAT | Call template outside air temperature | |
RmT | Call template room temperature | |
SuAT | Call template inlet air temperature | |
Sched | Call template plant timer program | |
FireDetc | BI object for logging the fire alarm event | |
SuAFan | Call template with integrated pressure regulator for a speed-controlled inlet air fan | |
ExtAFan | Call template with integrated pressure regulator for a speed-controlled outlet air fan | |
ExhADmp | Call template exhaust air damper with spring return actuator and limit switch monitor | |
OuADmp | Call template outside air damper with spring return actuator and limit switch monitor | |
SpRmT | Set value room air/inlet air cascade | |
SeqT | Call template sequence control | |
OpMod | Plant operation mode | |
Start | Call template system start program for temperature-controlled ventilation system | |
SumNgtCol | Night cooling | |
PreHtr | Call template for a hot-water air heater | |
Erc | Call template for the control of a plate heat exchanger for the recovery of energy in a ventilation system. | |
ColT | BAC_AC_ColT_02 | Call template of a temperature controlled cold-water air cooler (valve) |
Plant alarm logging
The alarm priority ALM_PRIO_CRITICAL is a fault that results in plant shutdown.
Template | Subtemplate | Instance | Type | Alarm priority |
ExhAT |
| AlmAI | ALM_PRIO_ALARM |
ExtAT |
OuAT |
RmT |
SuAT |
SuAFan | SuAFanFU | AlmThOvrld | ALM_PRIO_CRITICAL |
AlmDstFC | ALM_PRIO_CRITICAL |
AlmMntnSwi | ALM_PRIO_ALARM |
SuAFanDiffPrssMonit | AlmDiffPrss | ALM_PRIO_CRITICAL |
ExtAFan | ExtAFanFU | AlmThOvrld | ALM_PRIO_CRITICAL |
ExtAFanDiffPrssMonit | AlmDiffPrss | ALM_PRIO_CRITICAL |
ExhADmp |
| AlmFnct | ALM_PRIO_CRITICAL |
OuADmp |
PreHtr | PreHtrRetWtrT | AlmAI | ALM_PRIO_ALARM |
PreHtrFrstThermostat | AlmBI | ALM_PRIO_ALARM |
PreHtrFrstPrt | AlmFrst | ALM_PRIO_ALARM |
PreHtrFrstPrtT | AlmAI | ALM_PRIO_ALARM |
PreHtrPu | AlmDst | ALM_PRIO_ALARM |
PreHtrVlv | AlmFdbMonit | ALM_PRIO_WARNING |
Erc | ErcDmp | AlmFdbMonit | ALM_PRIO_WARNING |
ColT | ColTVlv | AlmFdbMonit | ALM_PRIO_WARNING |
Version history
Version number | Comments |
1.0.1.0 | First release |
