BAC_AC_ExhADmp2P_01_xx
Functional description
The sub template BAC_AC_ExhADmp2P_01_xx is used for control and monitoring of an exhaust air damper with spring return actuator and limit switch monitor. The damper is controlled via a binary output.
![]() | The output variable bOpn outputs the actual state of the damper, if feedback from limit switch SwiOpn is available in the template used. If no end position monitoring is available, it is emulated internally. If the damper is controlled, output bOpn becomes TRUE. As a result, in the start program for a ventilation system BAC_AC_StartT_01, the delay time for starting the fans (SuAFanDlyOn / ExtAFanDlyOn) has to be adjusted to the time it takes for the damper to open. |
The template BAC_AC_ExhADmp2P_01_xx is available in different versions.
The damper versions are identified by means of a key. The identification key is derived from the table below.
Options | mechanical | mechanical | Final position | Final position |
Instance | LocSwi | FdbOut | SwiOpn | SwiCls |
Data point type | BI | BI | BI | BI |
| 8 | 4 | 2 | 1 |
BAC_AC_ExhADmp2P_01_00 | 0 | 0 | 0 | 0 |
BAC_AC_ExhADmp2P_01_02 | 0 | 0 | 1 | 0 |
BAC_AC_ExhADmp2P_01_03 | 0 | 0 | 1 | 1 |
BAC_AC_ExhADmp2P_01_08 | 1 | 0 | 0 | 0 |
BAC_AC_ExhADmp2P_01_10 | 1 | 0 | 1 | 0 |
BAC_AC_ExhADmp2P_01_11 | 1 | 0 | 1 | 1 |
BAC_AC_ExhADmp2P_01_12 | 1 | 1 | 0 | 0 |
BAC_AC_ExhADmp2P_01_14 | 1 | 1 | 1 | 0 |
BAC_AC_ExhADmp2P_01_15 | 1 | 1 | 1 | 1 |
Interface
Plant diagram 01
Plant diagram 02
Block diagram for controlling the damper
Block diagram for monitoring the limit switches
udiPltStp : UDINT;
udiOpMod : UDINT;
udiPltStp: Steps during startup of the air-conditioning plant. See also BAC_AC_StartT_01
udiOpMode: Plant operation mode. See also BAC_AC_OpMod_01
bOpn : BOOL;
bOpn: End position 'open' of the damper has been reached.
VAR CONSTANT
PLT_NUM : BYTE := 1;
PLT_NUM: all alarms and events of all plant components within a controller are included in a global alarm and event list. The assignment of events and alarms to a plant is defined by the assignment of a PLT_NUM plant number.
The recording and processing of an alarm from an aggregate or a device takes place within the templates by means of the alarm function block FB_BA_Alarm.
The evaluation of the alarms of a plant, e.g. for the generation of a collective message or for plant shutdown in case of relevant faults, takes place within the template BAC_PltAlm_01 by means of the function block FB_BA_AlarmPlt.
The evaluation of different plant events within the templates of a plant, takes place within the template BAC_PltComnMsg_01 by means of the function block FB_BA_ComnMsg.
Important! The assignment and evaluation of the alarms and events of a plant can only be done correctly if all templates of a plant have the same plant number!
The plant number can be assigned in the Project Builder in the parameter menu for the templates or via a column in the Excel import.
Program description
Instance | Type | optional | Task | ||||
SwiOpn | X | BI object for connecting the limit switch 'open' | |||||
SwiCls | X | BI object for connecting the limit switch 'closed' | |||||
OpMod |
| MV object for manual control of the damper via the MCL or a local operator display | |||||
LocSwi | X | BI object for feedback from mechanical priority operation. (manual/emergency operating level) | |||||
FdbOut | X | BI object for logging the mechanical priority operation position feedback relay | |||||
TiOpn | X | AV object for entering the opening time value | |||||
TiCls | X | AV object for entering the closing time value | |||||
OpModSfty |
| The multiplexer defines the safety priority of the exhaust air damper depending on the plant operation mode udiOpMod | |||||
udiOpMod | Damper state | ||||||
OPMOD_AC_SMEXTTPRG | Smoke extraction program | Open | |||||
OPMOD_AC_SMEXTTSUA | Smoke extraction supply air | Close | |||||
OPMOD_AC_SMEXTTEXHA | Smoke extraction exhaust air | Open | |||||
OPMOD_AC_FIRE | Fire | Close | |||||
OpModDst |
| The multiplexer defines the disturbance priority of the exhaust air damper depending on the plant operation mode udiOpMod | |||||
OPMOD_AC_FORCVENT | Forced ventilation | Open | |||||
OPMOD_AC_EMERG | emergency | Close | |||||
OPMOD_AC_FRST | Frost | Close | |||||
OPMOD_AC_CENTSWIOFF | Central shutdown | Close | |||||
OPMOD_AC_ALM | Fault | Close | |||||
OpModPrio |
| The multiplexer defines the plant operation mode udiOpMod. | |||||
OPMOD_AC_MANON | Manual on | Damper does not close until the plant step udiPltStp < PLTSTP_AC_DMP if no longer required | |||||
OPMOD_AC_ON | On | Damper does not close until the plant step udiPltStp < PLTSTP_AC_DMP if no longer required | |||||
OPMOD_AC_NGTCOL | Night cooling | Damper does not close until the plant step udiPltStp < PLTSTP_AC_DMP if no longer required | |||||
OPMOD_AC_COLDWNPRTC | Support operation, cooling protection | Damper does not close until the plant step udiPltStp < PLTSTP_AC_DMP if no longer required | |||||
OPMOD_AC_OVRHTGPRTC | Overheating protection | Damper does not close until the plant step udiPltStp < PLTSTP_AC_DMP if no longer required | |||||
BO |
| BO object for controlling the damper | |||||
Priority: | Enable | Value | |||||
PRIO_SAFETY (1) | see multiplexer OpModSftyudiOpMod | see multiplexer OpModSfty Damper state | |||||
PRIO_DISTURBANCE (3) | see multiplexer OpModDstudiOpMod | see multiplexer OpModDst Damper state | |||||
PRIO_LOCAL (8) | The OR module pools events which enable writing to the priority manual override (local) of the downstream BO object. | Open, if OpMod_udiPrVal = OPMOD_MAN_STP01 | |||||
PRIO_PROGRAM (15) | TRUE | If the plant step is udiPltStp >= PLTSTP_AC_DMP, the damper should open | |||||
MoveCtrlOpn | X | Function block, which monitors the 'open' end position of the damper | |||||
MoveCtrlCls | X | Function block, which monitors the 'closed' end position of the damper | |||||
AlmFnct | x | The AlmFnct function block records the event of the limit position switch monitoring. | |||||
Alm | x | BV object for displaying the damper fault in the MCL |
IO linking
Variables for linking with the terminals
Parameter | Type | optional | Process image |
BI_Damper_LimitSwitch_Open | BOOL | X | Input | Digital input - switch damper open - message - actuated/not actuated |
BI_Damper_LimitSwitch_Close | BOOL | X | Input | Digital input - switch damper closed - message - actuated/not actuated |
BI_Damper_LocalSwitch | BOOL | X | Input | Digital input - switch manual damper - message - manual/automatic |
BI_Feedback_Binary_Output | BOOL | X | Input | Digital input - damper switching command - feedback - on/off |
BO_Damper | BOOL |
| Output | Digital output - damper - switching command - on/off |
Version history
Version number | Comments |
1.0.1 | First release |