BAC_AC_OpMod_01
Functional description
The template BAC_AC_OpMod_01 prioritizes different events or commands of an air-conditioning plant, such as fire alarm, request of central switching or schedule and writes a resulting operation mode or resulting system status to the variable udiOpMod.
The devices and aggregates respond individually, depending on udiOpMod, so that the whole plant adjusts itself according to the current operation mode.
Sample: 1
The mixed-air system BAC_AC_MixAT_01 switches to a fresh air rate of 100%, if udiOpMod is in summer night cooling mode (udiOpMod = 11).
Sample: 2
The supply air and extract air fan switches on if forced ventilation is enabled. Controlled fans crank up to a speed of 100%.
Interface
System diagram
Block diagram
The following system states or operation modes are described via the variable : udiOpMod
udiOpMod | |||
1 | Off | Plant shutdown | |
2 | On | Plant startup | |
3 | Emergency | Plant shutdown | |
4 | Manual off | Plant shutdown | |
5 | Manual on | Plant startup | |
6 | Frost | Plant shutdown | |
7 | Smoke extraction program | Plant startup | |
8 | Smoke extraction supply | Plant supply air on | |
9 | Smoke extraction exhaust | Plant extract air on | |
10 | Fire | Plant shutdown | |
11 | Night cooling | Plant startup | |
12 | Cool down protection | Plant startup | |
13 | Overheating protection | Plant startup | |
14 | Alarm | Plant shutdown | |
15 | Forced ventilation | Plant startup | |
16 | Central switch-off | Plant shutdown |
bOn : BOOL;
bFrst : BOOL;
bAlmShutOff : BOOL;
bNgtCol : BOOL;
bColDwnPrtc : BOOL;
bOvrHtgPrtc : BOOL;
bFireDetc : BOOL;
bSmExttSuA : BOOL;
bSmExttExuA : BOOL;
bForcVent : BOOL;
bEmgOff : BOOL;
bCentSwiOff : BOOL;
bOn: Request from timer program
bFrst: Frost protection program active
bAlmShutOff: Collective fault message - shut down plant
bNgtCol: Request from summer night cooling program
bColDwnPrtc: Request from cooling protection program
bOvrHtgPrtc: Request from overheating protection program
bFireDetc: Fire alarm message from fire alarm center
bSmExttSuA: Additional flow requested by supply air section of the plant for smoke extraction.
bSmExttExhA: Smoke extraction with extract air section of the plant requested.
bForcVent: Forced ventilation request
bEmgOff: Emergency Stop
bCentSwiOff: Central shutdown
udiOpMod : UDINT;
udiOpMod: Output of the current plant operation mode.
VAR CONSTANT
PLT_NUM : BYTE := 1;
PLT_NUM: all alarms and events of all plant components within a controller are included in a global alarm and event list. The assignment of events and alarms to a plant is defined by the assignment of a PLT_NUM plant number.
The recording and processing of an alarm from an aggregate or a device takes place within the templates by means of the alarm function block FB_BA_Alarm.
The evaluation of the alarms of a plant, e.g. for the generation of a collective message or for plant shutdown in case of relevant faults, takes place within the template BAC_PltAlm_01 by means of the function block FB_BA_AlarmPlt.
The evaluation of different plant events within the templates of a plant, takes place within the template BAC_PltComnMsg_01 by means of the function block FB_BA_ComnMsg.
Important! The assignment and evaluation of the alarms and events of a plant can only be done correctly if all templates of a plant have the same plant number!
The plant number can be assigned in the Project Builder in the parameter menu for the templates or via a column in the Excel import.
Program description
Instance | Type | Task |
OpMod | The BACnet MV object serves as plant selector switch. The MV object can be used to switch the plant on or off, independent of the automatic programs. | |
OpModPrio | The function block logs all commands, prioritizes them and outputs the result at output udiVal. | |
OpModInd | The BACnet MV object indicates the current plant operation mode. |
Version history
Version number | Comments |
1.0.1 | First release |