FB_BA_Alarm
Alarm output function block with selectable alarm memory and internal acknowledgement.
The acknowledgement pulse is generated in FB_BA_AlarmPlt. It is internally passed to the collective alarm function blocks of a plant.
Inputs/outputs
bEvt : BOOL;
sMsgTxt : STRING;
byPrio : BYTE;
byPltId : BYTE;
bAckReq : BOOL;
bEvt: input for detecting the alarm
sMsgTxt: input field for message text (configurable via Project Builder or Excel import)
byPrio: defines the action that is to be triggered when the alarm occurs in relation to the control of the respective plant.
byPrio = 0 = no message = ALM_PRIO_EMPTY
byPrio = 1 = various messages = ALM_PRIO_NOTE
byPrio = 2 = warning = ALM_PRIO_WARNING
byPrio = 3 = alarm without shutdown = ALM_PRIO_ALARM
byPrio = 4 = alarm with shutdown = ALM_PRIO_CRITICAL , sets the output bCriticalAlm of the function block FB_BA_AlarmPlt.
byPltId: number of the corresponding plant. Important: All templates of plant must be assigned to the same plant number in the PLC!
bAckReq:TRUE = requires acknowledgement. Is the alarm requires acknowledgement, it is not removed from the alarm list until the plant operator acknowledges the alarm.
bQ : BOOL;
eState : E_BA_AlmSta;
bAckFlg : BOOL;
bQ: Alarm output
eState: Enumerator status of the alarm messages
bAckFlg: When an acknowledgement is triggered, this output is active for one cycle. The pulse can be used to acknowledge faults. The acknowledgement pulse is generated in FB_BA_AlarmPlt. It is internally passed to the collective alarm function blocks of a plant.
Development environment | Target system | required library | required supplement |
TwinCAT 2.11 R3/x64 | PC/CX | TcBA library from V1.0.0 | TS8040 | TwinCAT Building Automation from V1.0.0 |