BAC_AC_MixAT_01
Application
The call template BAC_AC_MixAT_01 is used to control and regulate a mixed air system.
The template BAC_AC_MixAT_01 is a call template.
Within the template the following subtemplates are called and linked with each other.
- MixAT_PID: supply air temperature controller
- DmpMixA: mixed air damper
- DmpOuA: outside air damper
- DmpExhA: exhaust air damper
Interface
Plant diagram 01
Plant diagram 02
Block diagram
rSuAT : REAL;
rSp : REAL;
udiPltStp : UDINT;
udiOpMod : UDINT;
rExtAT : REAL;
bWthTLmtCrit : BOOL;
rSuAT: Measured value of the supply air temperature
rSp: Set value for the supply air temperature
udiPltStp: Plant start sequence steps. The plant steps are generated in the system start programBAC_AC_StartT_01.
udiOpMod: Plant operation mode. The plant operation mode is determined in the mode selection programBAC_AC_OpMod_01.
rExtAT: Measured value outlet air temperature.
bWthTLmtCrit: Signal from system start program. Starting in recirculated-air mode via start-up ramp.
bAvail : BOOL;
bAvail: This output indicates that a mixed-air damper system is present. This variable notifies the system start program that prerinsing of the preheater is skipped, see BAC_AC_StartT_01.
On startup of the ventilation system, the ramp function in the template MixAT_PID replaces prerinsing of the air heater.
Program description
Instance | Type | Task | |||||||
PID | Subtemplate including PID sequence controller for supply air temperature control. | ||||||||
DmpMixA | Subtemplate recirculating air damper | ||||||||
DmpOuA | Subtemplate outside air damper | ||||||||
DmpExhA | Subtemplate exhaust air damper | ||||||||
Inv | Inversion of the control signal of the outside air damper for controlling the mixed air damper. | ||||||||
OpModPgm | The multiplexer defines the control value for the dampers in the program priority (automatic operation) via the plant operation mode udiOpMod | ||||||||
udiOpMod | Value |
OPMOD_AC_MANON | Manual on | Pgm_rY | Pgm_rY is a variable, which relays the result of the MIN selection of the mixed air damper controller and the ramp function to the dampers. | ||||||
OPMOD_AC_AC_ON | Automatic mode on | Pgm_rY | Pgm_rY is a variable, which relays the result of the MIN selection of the mixed air damper controller and the ramp function to the dampers. | ||||||
OPMOD_AC_NGTCOL | Night cooling | 100 |
OPMOD_AC_COLDWNPRTC | Cooling protection | 0 |
OPMOD_AC_OVRHTGPRTC | Overheating protection | 0 |
OpModSftyMix | The multiplexer defines the safety priority for the recirculating air damper via the plant operation mode udiOpMod | ||||||||
udiOpMod | Value | ||||||||
OPMOD_AC_SMEXTTPRG | Smoke extraction program | 0 | |||||||
OPMOD_AC_SMEXTTSUA | Smoke extraction supply air | 0 | |||||||
OPMOD_AC_SMEXTTEXHA | Smoke extraction exhaust air | 0 | |||||||
OPMOD_AC_FIRE | Fire | 0 | |||||||
OpModDistMix | The multiplexer defines the fault priority for the recirculating air damper via the plant operation mode udiOpMod | ||||||||
OPMOD_AC_FORCVENT | Forced ventilation | 0 | |||||||
OPMOD_AC_EMERG | emergency | 0 | |||||||
OPMOD_AC_FRST | Frost | 100 | |||||||
OPMOD_AC_CENTSWIOFF | Central shutdown | 0 | |||||||
OPMOD_AC_ALM | Fault/alarm | 100 | |||||||
OpModSftyOuA | The multiplexer defines the safety priority for the outside air damper via the plant operation mode udiOpMod | ||||||||
OPMOD_AC_SMEXTTPRG | Smoke extraction program | 100 | |||||||
OPMOD_AC_SMEXTTSUA | Smoke extraction supply air | 100 | |||||||
OpModDistOuA | The multiplexer defines the fault priority for the outside air damper via the plant operation mode udiOpMod | ||||||||
OPMOD_AC_FORCVENT | Forced ventilation | 100 | |||||||
OPMOD_AC_FRST | Frost | 0 | |||||||
OPMOD_AC_ALM | Fault/alarm | 0 | |||||||
OpModSftyExhA | The multiplexer defines the safety priority for the exhaust air damper via the plant operation mode udiOpMod | ||||||||
OPMOD_AC_SMEXTTEXHA | Smoke extraction exhaust air | 100 | |||||||
OpModDistExhA | The multiplexer defines the fault priority for the exhaust air damper via the plant operation mode udiOpMod | ||||||||
Version history
Version number | Comments |
1.0.1 | First release |