BAC_Uni_Dmp_01_xx
Functional description
The template BAC_Uni_Dmp_01_xx is used for controlling an analog damper drive. It basically consists of an AO object including a trend object, an MV object for manual control, and the associated AV object for entering the position. The template is complemented through optional BACnet objects, see table with version overview.
![]() | The two output variables rPrVal / bSync are only used for synchronization of controllers if the template used contains feedback of the damper position Fdb. |
Versions
The template BAC_Uni_Dmp_01_xx is available in different versions.
The damper versions are identified by means of a key. The identification key is derived from the table below.
Options | Feedback | Mechanical priority operation position feedback | mechanical priority operation position feedback hand switch |
Instance | Fdb | FdbOut | LocSwi |
Data point type | AI | AI | BI |
| 4 | 2 | 1 |
BAC_Uni_Dmp_01_00 | 0 | 0 | 0 |
BAC_Uni_Dmp_01_01 | 0 | 0 | 1 |
BAC_Uni_Dmp_01_03 | 0 | 1 | 1 |
BAC_Uni_Dmp_01_04 | 1 | 0 | 0 |
BAC_Uni_Dmp_01_05 | 1 | 0 | 1 |
BAC_Uni_Dmp_01_07 | 1 | 1 | 1 |
Interface
Block diagram version BAC_Uni_Dmp_01_05
rValPgm : REAL;
bEnSfty : BOOL;
bValSfty : BOOL;
bEnDst : BOOL;
bValDst : BOOL;
rValPgm: Analog value program priority
bEnSfty: Safety priority enable
rValSfty: Analog value safety priority
bEnDst: Enable fault priority
rValDst: Analog value fault priority
rPrVal : REAL;
bSync : BOOL;
rPrVal : Current position of the damper drive.
The output variable rPrVal is only active if the template used contains feedback of the damper position Fdb .
bSync: Output of a pulse to synchronise the controller associated with the damper during reset from manual to automatic operation to the current damper position.
The output variable bSync is only active if the template used contains feedback of the damper position Fdb .
VAR CONSTANT
PLT_NUM : BYTE := 1;
PLT_NUM: all alarms and events of all plant components within a controller are included in a global alarm and event list. The assignment of events and alarms to a plant is defined by the assignment of a PLT_NUM plant number.
The recording and processing of an alarm from an aggregate or a device takes place within the templates by means of the alarm function block FB_BA_Alarm.
The evaluation of the alarms of a plant, e.g. for the generation of a collective message or for plant shutdown in case of relevant faults, takes place within the template BAC_PltAlm_01 by means of the function block FB_BA_AlarmPlt.
The evaluation of different plant events within the templates of a plant, takes place within the template BAC_PltComnMsg_01 by means of the function block FB_BA_ComnMsg.
Important! The assignment and evaluation of the alarms and events of a plant can only be done correctly if all templates of a plant have the same plant number!
The plant number can be assigned in the Project Builder in the parameter menu for the templates or via a column in the Excel import.
Program description
Instance | Type | optional | Task | |||
OpMod |
| MV object for manual control of the damper drive via the MCL or a local operator display | ||||
ManPos |
| AV object for entering the damper position with manual override | ||||
FdbMonitHys | X | AV object for entering the hysteresis for the function monitoring of the control valve via the position feedback | ||||
FdbOut | X | AI object for logging the mechanical priority operation position feedback potentiometer | ||||
Fdb | X | AI object for logging the position feedback from the damper position | ||||
FdbMonitTiDly | X | AV object for entering the response delay of the function monitoring via position feedback. | ||||
LocSwi | X | BI object signals mechanical priority operation position feedback hand switch | ||||
AO |
| AO object for controlling the control valve. | ||||
Priority: | Enable | Value | Comment | |||
PRIO_SAFETY (1) | Input bEnSfty | Input rValSfty |
PRIO_DISTURBANCE (3) | Input bEnDst | Input rValDst |
PRIO_LOCAL (8) | OpMod_udiPrVal = OPMOD_MAN | ManPos_rPrVal | In manual mode, value of AV object ManPos | |||
PRIO_PROGRAM (15) | TRUE | AblkFnct_bQ or rValPgm | Value of input rValPgm or 100% of blocking protection | |||
| EQ |
| TRUE if the active priority is PRIO_PROGRAM (15). Can be used for synchronizing the controller on return to automatic mode | |||
FdbMonitFnct | X | Function monitoring of the damper drive through comparison of the control output and the position feedback. | ||||
AlmFdbMonit | X | Logging and further processing of an error from the position feedback monitoring | ||||
FdbMonit | X | Reports position feedback error to the MCL | ||||
TLogAO |
| Logs the present value of the AO object | ||||
IO linking
Variables for linking with the terminals
Parameter | Type | optional | Process image |
AI_Damper_Feedback | INT | X | Input | Damper - measured value - return value position |
AI_Feeback_Position_Poti | INT | X | Input | Damper potentiometer H-A - measured value |
BI_Damper_LocalSwitch | BOOL | X | Input | Damper switch H-A - message - operation mode |
AO_Damper_Position_Value | INT |
| Output | Analog output - damper - control value position |
Version history
Version number | Comments |
1.0.1 | First release |