FB_BA_ComnMsg
Formation of collective messages
Functional description
The function blocks FB_BA_ComnMsg and FB_BA_ComnMsgTermt are used to form collective messages at the plant level and the controller level. The information of the BACnet objects is transferred to the function blocks ST_BA_ComnMsg in the structure ST_BA_ComnMsg. The variables stOut are used to transfer the collective plant messages to the function block FB_BA_ComnMsgTermt. All messages of the BACnet objects of a BACnet controller are consolidated here.
Error handling:
In the first cycle after a controller restart, each BACnet object reserves a field in a one-dimensional array within the message structure ST_BA_ComnMsg. The size of the array is defined with the global constant gBA_cMaxArrComnMsg. The default for this constant is 256. If more than 256 BACnet objects are connected to an instance of FB_BA_ComnMsg, it has to be increased. The transfer of messages to FB_BA_ComnMsgTermt is set to 64 within the structure ST_BA_ComnMsgTermt. For a higher number the constant gBA_cMaxArrComnMsgTermt has to be increased.
Inputs/outputs
stIn : ST_BA_ComnMsg;
stTermt : ST_BA_ComnMsgTermt;
stIn: data structure for connecting the BACnet objects at the plant level
stTermt: data structure for transferring collective messages from the plant level to function block FB_BA_ComnMsgTermt.
iId : INT;
bInAlm : BOOL;
bFlt : BOOL;
bOvrrd : BOOL;
bOoServ : BOOL;
bHiLmt : BOOL;
bLoLmt : BOOL;
udiHiActvPrio : UDINT;
arrActvPrio : ARRAY [1..16] OF BOOL;
iMaxNumOfEntry : INT;
iNumOfEntry : INT;
dwObjId : DWORD;
eObjType : E_BACnetObjectType;
bErr : BOOL;
udiErrId : UDINT;
udiErrArg : UDINT;
iId: ID of the last information telegram (stTermt.arrData[iId]) sent to FB_BA_ComnMsgTermt
bInAlm: the last sending BACnet object is in alarm status.
bFlt: the last sending BACnet object is in fault status.
bOvrrd: in the last sending BACnet object, the local mechanical priority operation is enabled.
bOoServ: the last sending BACnet object is "out of service".
bHiLmt: in the last sending BACnet object the Hi limit is exceeded.
bLoLmt: in the last sending BACnet object the Lo limit is undershot.
udiHiActvPrio: indicates the highest written priority of all BACnet objects.
arrActvPrio: the array provides an overview of the active priorities of all connected BACnet objects.
iMaxNumOfEntry: indicates how many BACnet objects can be connected to the function block.
iNumOfEntry: indicates how many BACnet objects are connected to the function block.
dwObjId: ID of the object that last entered the error state.
eObjType: object type of the object that last entered the error state.
bErr: this output is switched to TRUE if the parameters entered are erroneous.
udiErrId / udiErrArg: contains the error number and the error argument. See error codes.
Development environment | Target system | required library | required supplement |
TwinCAT 2.11 R3/x64 | PC/CX | TcBA library from V1.0.0 | TS8040 | TwinCAT Building Automation from V1.0.0 |