BAC_AC_ErcPl_01
Application
The template BAC_AC_ErcPl_01 is used for control and anti-icing of an energy recovery unit with plate heat exchanger.
Within the call template the following subtemplates are called and linked with each other:
- ErcSuA_PID: supply air temperature control
- ErcExhA_PID: minimum limitation of exhaust air temperature
- ErcIcPrt: anti-icing of the heat exchanger by means of a differential pressure switch
- ErcDmp: control of a bypass damper system
The exhaust air minimum limiter ErcExhA_PID and the frost protection program ErcIcPrt limit the control value of the supply air temperature controller ErcSuA_PID of the energy recovery unit via the minimum value option, in order to prevent icing up of the heat exchanger.
Interface
Plant diagram 01
Plant diagram 02
The output of the control signal for energy recovery output control refers to damper Dmp, not damper ByDmp. (see diagram). During commissioning of the air-conditioning plant, ensure that damper Dmp is operated with direct direction of action and damper ByDmp with inverted direction of action.
Block diagram
rSuAT : REAL;
rSpErc : REAL;
udiPltStp : UDINT;
udiOpMod : UDINT;
bDeHum : BOOL;
rExhAT : REAL;
rExtAT : REAL;
rSuAT: Measured value supply air temperature
rSpErc: Set value supply air temperature
udiPltStp: Plant start sequence steps. The plant steps are generated in the system start program BAC_AC_StartT_01.
udiOpMod: Plant operation mode. The plant operation mode is determined in the mode selection program BAC_AC_OpMod_01.
bDeHum: Status message dehumidification mode. Disabling of energy recovery in heating mode (outside temperature > outlet air temperature) .
rExhAT: Measured value exhaust air temperature
rExtAT: Measured value outlet air temperature
bActn : BOOL;
bActn: control direction of the supply air temperature control SuA_PID. The control direction of the energy recovery is required by various setpoint programs or cascade controllers for determining setpoint for the supply air temperature of the energy recovery unit, e.g. BAC_AC_SpSuAT_02, BAC_AC_CasCtrlT_02.
Program description
Instance | Type | Task |
SuA_PID | Sub template supply air temperature control. The temperature control is analog via PID sequence controller | |
ExhA_PID | Sub template exhaust air temperature control. The control is used for anti-icing and serves as prevention, before the ramp function IcPrt becomes active. | |
IcPrt | Sub template anti-icing via differential pressure switch | |
Dmp | Sub template for controlling an analog damper | |
| MIN, MIN | MIN selection of the control signals for supply air temperature control SuA_PID,exhaust air temperature control ExhA_PID and the frost protection ramp function |
Version history
Version number | Comments |
1.0.1 | First release |