BAC_ErcIcPrt_01
Functional description
The template is used to protect an energy recovery unit from icing up.
If the differential pressure switch DiffPrssExhSwi is triggered, a ramp function is activated, which issues an analog limit signal.
The limitation of the energy recovery results in thawing through the warm exhaust air flow.
System diagram
Block diagram
rY : REAL;
rY: Ramp signal output. If the differential pressure switch is not triggered, 100% is output at rY
VAR CONSTANT
PLT_NUM : BYTE := 1;
PLT_NUM: all alarms and events of all plant components within a controller are included in a global alarm and event list. The assignment of events and alarms to a plant is defined by the assignment of a PLT_NUM plant number.
The recording and processing of an alarm from an aggregate or a device takes place within the templates by means of the alarm function block FB_BA_Alarm.
The evaluation of the alarms of a plant, e.g. for the generation of a collective message or for plant shutdown in case of relevant faults, takes place within the template BAC_PltAlm_01 by means of the function block FB_BA_AlarmPlt.
The evaluation of different plant events within the templates of a plant, takes place within the template BAC_PltComnMsg_01 by means of the function block FB_BA_ComnMsg.
Important! The assignment and evaluation of the alarms and events of a plant can only be done correctly if all templates of a plant have the same plant number!
The plant number can be assigned in the Project Builder in the parameter menu for the templates or via a column in the Excel import.
Program description
Instance | Type | Task |
DiffPrssExhSwi | BI object differential pressure switch via the heat exchanger on the exhaust air side | |
RampTi | AV object for input of the ramp signal rise time | |
RampFnct | Ramp function, which generates a ramp signal that increases from 0%, if the differential pressure monitor was triggered. | |
RampVal | The AV object indicates the ramp signal. | |
rtrigRamp | R_TRIG | Specifies the starting value 0% for the ramp function for one cycle, if the differential pressure switch was triggered. |
IO linking
Variables for linking with the terminals
Parameter | Type | optional | Process image |
BI_Differential_Pressure_Switch | BOOL |
| Input | Digital input - message - differential pressure switch |
Version history
Version number | Comments |
1.0.1 | First release |