BAC_AC_PreHtr_01
Application
The call template BAC_AC_PreHtr_01 is used to control a hot-water air heater.
The main tasks of the template are:
- Control of the supply air temperature
- Control of the return temperature
- Frost monitoring air side with frost protection thermostat FrstThermostat
- Frost monitoring air side with analog frost protection sensor FrstT
- Frost monitoring water side with return temperature sensor RetWtrT
- Enable the heater pump
- Control and monitoring of the heater valve
Interface
Plant diagram 01
Plant diagram 02
Block diagram
rSuAT : REAL;
rSpHtg : REAL;
bDeHum : BOOL;
udiPltStp : UDINT;
udiOpMod : UDINT;
bWthTLmttCrit : BOOL;
bRst : BOOL;
rSuAT: Measured value of the supply air temperature
rSpHtg: Set value for the supply air temperature
bDeHum: Status message dehumidification mode
If dehumidification is active, the supply air temperature controller SuA_PID is disabled and therefore removed from the sequence control.
udiPltStp: Plant start sequence steps. The plant steps are generated in the system start program BAC_AC_StartT_01.
udiOpMod: Plant operation mode. The plant operation mode is determined in the mode selection programBAC_AC_OpMod_01.
bWthTLmtCrit: Status message weather temperature critical. This information is generated in the system start program BAC_AC_StartT_01.
The following actions are triggered when the outside temperature falls below a critical value:
- Heater pump activation, forced pump operation
- Return temperature control enable BAC_AC_RetWtrCtrl_01
- During plant startup prerinsing mode is active, see BAC_AC_RetWtrCtrl_01
bRst: Acknowledge frost protection message.
bFrst : BOOL;
bPreriRdy : BOOL;
bFrst: Frost protection program output active.
bPreriRdy: Pre-rinsing process output complete.
Program description
Instance | Type | Task |
RetWtrT | Subtemplate AI object return temperature sensor | |
FrstT | Subtemplate AI object frost protection sensor air side | |
FrstThermostat | Subtemplate BI object frost protection thermostat | |
SuA_PID | Subtemplate loop object supply air temperature control | |
RetWtrCtrl | Subtemplate return temperature control of the hot water air heater | |
FrstPrt | Subtemplate frost protection program | |
Vlv | Subtemplate control valve | |
Pu | Subtemplate pump | |
| MAX | MAX selection of the control signals for supply air temperature control SuA_PID and return temperature control RetWtrCtrl |
| OR | Collects frost events and passes them to the frost protection program.
Version history
Version number | Comments |
1.0.1 | First release |