BAC_AC_RetWtrCtrl_01
Application
The call template BAC_AC_RetWtrCtrl_01 is used for controlling the return temperature of the hot-water air heater.
The main tasks of the template are:
- Control of the return temperature during the pre-rinsing process on plant startup.
- Control of the return temperature to a frost protection set value during plant operation and standstill.
Interface
Diagram
Block diagram
bEn : BOOL;
rX : REAL;
rSync : BOOL;
bSync : UDINT;
udiPltStp : UDINT;
bEn: Return temperature control enable.
rX: Measured value of the return temperature
rSync: Synchronization value for the controller PID
bSync: Input for synchronization of the controller PID
udiPltStp: Steps during startup of the air-conditioning plant. See also BAC_AC_StartT_01
AR_OUTPUT
rY : REAL;
bPreriRdy : BOOL;
rY: Control value output
bPreriRdy: Pre-rinsing process message complete
VAR CONSTANT
PLT_NUM : BYTE := 1;
PLT_NUM: all alarms and events of all plant components within a controller are included in a global alarm and event list. The assignment of events and alarms to a plant is defined by the assignment of a PLT_NUM plant number.
The recording and processing of an alarm from an aggregate or a device takes place within the templates by means of the alarm function block FB_BA_Alarm.
The evaluation of the alarms of a plant, e.g. for the generation of a collective message or for plant shutdown in case of relevant faults, takes place within the template BAC_PltAlm_01 by means of the function block FB_BA_AlarmPlt.
The evaluation of different plant events within the templates of a plant, takes place within the template BAC_PltComnMsg_01 by means of the function block FB_BA_ComnMsg.
Important! The assignment and evaluation of the alarms and events of a plant can only be done correctly if all templates of a plant have the same plant number!
The plant number can be assigned in the Project Builder in the parameter menu for the templates or via a column in the Excel import.
Program description
Instance | Type | Task |
SpPreriScaleX1 | AV object for input of the setpoint for prerinsing scaling point X1 | |
SpPreriScaleX2 | AV object for input of the setpoint for prerinsing scaling point X2 | |
SpPreriScaleY1 | AV object for input of the setpoint for prerinsing scaling point Y1 | |
SpPreriScaleY2 | AV object for input of the setpoint for prerinsing scaling point Y2 | |
SpRetWtrT | AV object for input of the setpoint for the return temperature water | |
SpPreriScale | Function block for calculating the prerinsing temperature depending on the outside temperature for return temperature control during plant startup. | |
HysPreri | When the air-conditioning plant starts up at low outside temperatures, the heating coil is pre-rinsed with warm water. Only then are the dampers opened and the fans switched on. When the prerinsing temperature SpPreriScale_lrY has been reached, the function block HysPreri switches the variable bPreriRdy to TRUE. This tells the plant start program BAC_AC_StartT_01 that the prerinsing process is complete. | |
| SUB | The value of the subtraction is the lower switching point of the two-point switch HysPreri. |
| OR | Outputs the prerinsing status through HysPreri or bEn. |
X | AV object for displaying the return temperature of the hot water air heater. | |
W | AV object for displaying the setpoint of the return temperature controller. | |
| >=, <=, AND, SEL | The value of this networks determines the setpoint for the return temperature control of the hot water air heater PID. |
En | The BV object is used to display and activate the controller enable in the MCL or in a local operator display. | |
PID | Loop object Return temperature control of the hot water air heater. | |
Y | AV object for displaying the control value of the return temperature control. |
Version history
Version number | Comments |
1.0.1 | First release |