BAC_AC_SeqT_01
Functional description
The template BAC_AC_SeqT_01 is responsible for starting the supply air temperature sequence control of an air-conditioning plant.
On startup of the air-conditioning plant the system determines whether to start with the heating, cooling or heat recovery sequence. The start sequence is selected depending on the plant operation mode and the outside temperature.
Only one element of the sequence can be in control. When the output of a controlling sequence element reaches Y Min or Y Max, the control is transferred to the next sequence controller that is ready for switch-on.
Interface
System diagram
Block diagram
Order of the sequences
The order of the control sequence is specified by the globally defined variables. If necessary, the sequence order can be adjusted slightly.
For example if energy recovery is to take place upstream of the mixed air system.
Globally defined sequence numbers of the sequence controllers:
1 | Sequenznummer Nacherhitzer//Sequence number reheater | |
2 | Sequenznummer Vorerhitzer//Sequence number preheater | |
3 | Sequenznummer Mischluft//Sequence number mixed air | |
4 | Sequenznummer Energierückgewinnung//Sequence number energy recovery | |
5 | Sequenznummer Kühler//Sequence number cooler | |
6 | kein Sequenzregler aktiv//no sequence controller active |
udiOpMod : UDINT;
udiPltStp : UDINT;
rSuAT : REAL;
udiOpMod: Plant operation mode. See also BAC_AC_OpMod_01
udiPltStp: Steps during startup of the air-conditioning plant. See also BAC_AC_StartT_01
rSuAT: Measured value supply air temperature
bSumLmt : BOOL;
bWinLmt : BOOL;
bSumLmt: Summer mode
bWinLmt: Winter mode
VAR CONSTANT
PLT_NUM : BYTE := 1;
PLT_NUM: all alarms and events of all plant components within a controller are included in a global alarm and event list. The assignment of events and alarms to a plant is defined by the assignment of a PLT_NUM plant number.
The recording and processing of an alarm from an aggregate or a device takes place within the templates by means of the alarm function block FB_BA_Alarm.
The evaluation of the alarms of a plant, e.g. for the generation of a collective message or for plant shutdown in case of relevant faults, takes place within the template BAC_PltAlm_01 by means of the function block FB_BA_AlarmPlt.
The evaluation of different plant events within the templates of a plant, takes place within the template BAC_PltComnMsg_01 by means of the function block FB_BA_ComnMsg.
Important! The assignment and evaluation of the alarms and events of a plant can only be done correctly if all templates of a plant have the same plant number!
Within a ventilation system with sequence controller the plant number indicates which field from the global data structure g_stSeqLinkT[PLT_NUM] is used as link between the individual sequence controllers and the corresponding control function blockFB_BA_SeqLink.
The plant number can be assigned in the Project Builder in the parameter menu for the templates or via a column in the Excel import.
Program description
Instance | Type | Task |
WthTLmtSum | AV object for input of an outside temperature value from which the air-conditioning plant starts in the cooling sequence. | |
WthTLmtWin | AV object for input of an outside temperature value from which the air-conditioning plant starts in the heating sequence. | |
SttSeqT | The priority switch is used to select the start sequence. | |
SeqLinkT | The function block SeqLinkT is the core of the template BAC_AC_SeqT_01. The sequence linker is linked with all supply air controllers of the sequence via the global data structure g_stSeqLinkT[PLT_NUM] . It is the central control element, and responsible for switching between the sequence controllers and starting of the control sequence. | |
CurSeqT | The MV object indicates the currently active sequence controller. |
Version history
Version number | Comments |
1.0.1 | First release |