FB_BA_AHU_1st_10
FB_BA_AHU_1st_10 1:
Template of an air conditioning system.
The main components of the template are:
FB_BA_AHU_1st_10 2:
FB_BA_AHU_1st_10 3:
The initialization of the template takes place within the method FB_Init.
Block diagram
FB_BA_AHU_1st_10 4:
Plant diagram
FB_BA_AHU_1st_10 5:
Switch-on sequence of the aggregates of the plant
Within PlantCmd, a step sequence controller sequentially controls the switching on and off of the aggregates one after the other. When switching from aggregate to aggregate, predefined delay times and feedback from the aggregates are taken into account.
The order of the aggregates is determined by the ordinal number of the individual elements of the bidirectional array arrAggregate.
FB_BA_AHU_1st_10 6:
Step
Stages of plant start-up
Aggregate
Function blocks
00
E_BA_AC_PlantStep01.eOff
Plant Off
01
E_BA_AC_PlantStep01.eErc
Energy recovery
Erc
02
E_BA_AC_PlantStep01.ePreRinse
Prerinsing of the hot water air heater
PreHtr
03
E_BA_AC_PlantStep01.eDamperOuA
Outside air damper
OuADmp
04
E_BA_AC_PlantStep01.eFanSupplyAir
Supply air fan
SuAFan
05
E_BA_AC_PlantStep01.eDamperExhA
Exhaust air damper
ExhADmp
06
E_BA_AC_PlantStep01.eFanExtractAir
Extract air fan
ExtAFan
07
E_BA_AC_PlantStep01.eCooler
Cold water air cooler
Col
08
E_BA_AC_PlantStep01.eOn
Room supply air cascade, plant On
TCasCtrl
If the plant has reached step 08 E_BA_AC_PlantStep01.eOn, the supply air temperature sequence control TSeqLink is enabled when the cascade control TCasCtrl is switched on.
FB_BA_AHU_1st_10 7:
Starting up the plant in cold weather
When the system is switched on in cold weather, the step sequence control of the PlantCmd command includes the plant step PreRinse of the preheater E_BA_AC_PlantStep01.ePreRinse. In this step, the return temperature control of the hot water air heater is activated. This procedure is intended to prevent the freezing of the hot water air heater during the plant start-up.
Fault shutdown
The plant switches off at:
FB_BA_AHU_1st_10 8:
In the event of a frost alarm, the PreHtr hot water air heater remains in the frost protection position even when the plant is switched off!
The following table lists the event-capable objects of the template that can trigger relevant PlantLock faults. The parameterization of the lock priority of these events can be found in FB_init.
Function block
eEnPlantLock
Function block
bPrioHigh
bPrioMedium
TSuA.MV
E_BA_LockPriority.eMedium
PlantLock
x
FiltOuAMonit.DstMainAlarm
x
OuADmp.MonitOpen.Dst
x
SuAFan.Dst
x
SuAFan.ThOvrld
x
SuAFan.MntnSwi
x
SuADiffPrssMonit.Dst
x
ExhADmp.MonitOpen.Dst
x
ExtAFan.Dst
x
ExtAFan.ThOvrld
x
ExtAFan.MntnSwi
x
ExtADiffPrssMonit.Dst
x
PreHtr.TRt.MV
x
PreHtr.TFrost.MV
x
PreHtr.FrostThermostat.Input
x
PreHtr.Pu.Dst
x
Temperature control
In this plant template a simple room air supply air cascade is realized as control strategy.
The setpoints for the plant are generated in the templates SpTRm / TCasCtrl and forwarded to the sequence controllers within the templates PreHtr, Col and Erc.
FB_BA_AHU_1st_10 9:
Sequence control
The number of sequence controllers in the control sequence varies and depends on the number of aggregates in the ventilation system. The PID sequence controllers, which contribute to increasing the supply air temperature, are arranged on the left of the control sequence. The controllers of the aggregates that cool down the supply air temperature are located on the right.
Several heating or cooling aggregates can be integrated into the control sequence.
Only one PID controller is active at any one time in the sequence control. All others remain at the value of their maximum or minimum control value.
FB_BA_AHU_1st_10 10:
The sequence control TSeqLink is enabled when bOn is received from the cascade control TCasCtrl.
The start sequence controller with which the plant starts up is determined depending on the weather temperature Site.stGeneralSettings.fTWth or the operation mode OpMod.
The stTSeqLink data structure is used to transmit the plant enable and the number of the start controller to the sequence controllers of the PreHtr air heater, Col air cooler and Erc energy recovery unit.
The ventilation system in the sequence diagram is equipped with an air heater, an energy recovery unit and an air cooler.
All aggregates are integrated into a sequence controller for continuous control of the supply air temperature TSuA at very low outdoor temperatures in winter through to high outdoor temperatures in summer.
The sequence on the left starts with the control range of the PreHtr air heater. At low outside temperatures, the output of the air heater is increased until the supply air temperature TSuA has reached its setpoint.
If the outside temperature TOuA rises, the sequence controller TSuACtrl of the PreHtr air heater reduces its actuating variable until it reaches the lower limit of its control range.
If the setpoint of the supply air temperature TCasCtrl is still not reached, the sequence controller TSuACtrl of the air heater PreHtr switches to the sequence controller TSuACtrl of the energy recovery Erc.
The behavior of the energy recovery Erc depends on the ratio of the weather temperature Site.stGeneralSettings.fTWth and the extract air temperature TExtA.
If the weather temperature Site.stGeneralSettings.fTWth is lower than the extract air temperature TExtA, energy recovery recovers heat energy from the extract air and transfers it to the outside air. The red characteristic curve is then activated in the control sequence.
The control direction of the sequence controller TSuACtrl is therefore indirect (heating mode).
In summer, the extract air temperature is often lower than the weather temperature. The energy flow of the energy recovery Erc is then inverted. The heat from the outside air is transferred to the exhaust air TExhA and the supply air temperature is reduced as a result. In this operating case, the sequence follows the blue characteristic curve. The control direction of the sequence controller TSuACtrl is therefore direct (cooling mode).
At high outside temperatures, if the recovery capacity of the Erc is not sufficient to cool the outside air OuA down far enough, the sequence controller TSuACtrl of the energy recovery Erc switches on to the sequence controller TSuACtrl of the cooler Col. This increases the capacity of the cooler until the setpoint of the supply air temperature is reached.
Filter monitoring
The outside and extract air filters are monitored via the function blocks FiltOuAMonit and FiltExtAMonit with the analog differential pressure sensors DiffPrssOuAFilt / DiffPrssExtAFilt. The filter monitors are enabled when bOn is received from the cascade control TCasCtrl.
Night cooling
Night cooling can be controlled via the function block SumNgtCol.
FUNCTION_BLOCK FB_BA_AHU_1st_10 EXTENDS FB_BA_View
VAR_INPUT CONSTANT
  TOuA                    : FB_BA_SensorAnalog;
  TExhA                   : FB_BA_SensorAnalog;
  TSuA                    : FB_BA_SensorAnalog;
  TExtA                   : FB_BA_SensorAnalog;
  TRm                     : FB_BA_SensorAnalog;
  DiffPrssOuAFilt         : FB_BA_SensorAnalog;
  FiltOuAMonit            : FB_BA_Hys_21;
  DiffPrssExtAFilt        : FB_BA_SensorAnalog;
  FiltExtAMonit           : FB_BA_Hys_21;
  OuADmp                  : FB_BA_AC_Dmp2P;
  SuAPrss                 : FB_BA_SensorAnalog;
  SuADiffPrss             : FB_BA_SensorAnalog;
  SuAFan                  : FB_BA_AC_FanCtl;
  SuADiffPrssMonit        : FB_BA_FdbAnalog;
  ExhADmp                 : FB_BA_AC_Dmp2P;
  ExtAPrss                : FB_BA_SensorAnalog;
  ExtADiffPrss            : FB_BA_SensorAnalog;
  ExtAFan                 : FB_BA_AC_FanCtl;
  ExtADiffPrssMonit       : FB_BA_FdbAnalog;
  PreHtr                  : FB_BA_AC_PreHtr;
  Erc                     : FB_BA_AC_ErcPl_02;
  Col                     : FB_BA_AC_ColT_02;
  SpTRm                   : FB_BA_Scale_04_Y2_3;
  TCasCtrl                : FB_BA_AC_TCasCtrl_01;
  SumNgtCol               : FB_BA_AC_SumNgtCol;
  OpMod                   : FB_BA_AC_OpMod1St;
  PlantLock               : FB_BA_PlantLock;
  PlantCmd                : FB_BA_AC_PlantCmd_AHU_1st_10;
  TSeqLink                : FB_BA_AC_SeqT;
  stTSeqLink              : ST_BA_SeqLink;
  arrAggregate            : ARRAY [1..BA_Param.nMaxAggregate] OF ST_BA_Aggregate;
FB_BA_AHU_1st_10 11: VAR_INPUT CONSTANT
Type
TOuA
FB_BA_SensorAnalog
Represents the outside air temperature
TExhA
FB_BA_SensorAnalog
Represents the exhaust air temperature
TSuA
FB_BA_SensorAnalog
Represents the supply air temperature
TExtA
FB_BA_SensorAnalog
Represents the extract air temperature
TRm
FB_BA_SensorAnalog
Represents the room temperature
DiffPrssOuAFilt
FB_BA_SensorAnalog
Analog differential pressure via the outside air filter
FiltOuAMonit
FB_BA_Hys_21
Analog monitoring of the outside air filter. The filter monitoring uses the analog differential pressure DiffPrssOuAFilt and can trigger both a pre-alarm and a main alarm.
DiffPrssExtAFilt
FB_BA_SensorAnalog
Analog differential pressure via the extract air filter
FiltExtAMonit
FB_BA_Hys_21
Analog monitoring of the extract air filter. Filter monitoring uses the analog differential pressure FiltExtAMonit and can trigger both a pre-alarm and a main alarm.
OuADmp
FB_BA_AC_Dmp2P
Activation of the outside air damper with a spring return actuator and end position monitor.
SuAPrss
FB_BA_SensorAnalog
Supply air pressure
SuADiffPrss
FB_BA_SensorAnalog
Differential pressure via the supply air fan
SuAFan
FB_BA_AC_FanCtl
Activation and control of the speed-controlled supply air fan.
SuADiffPrssMonit
FB_BA_FdbAnalog
Analog differential pressure monitoring via the supply air fan.
Differential pressure monitoring uses the SuADiffPrss analog differential pressure sensor and can trigger a plant shutdown alarm.
ExhADmp
FB_BA_AC_Dmp2P
Control of the exhaust air damper with a spring return actuator and end position monitor.
ExtAPrss
FB_BA_SensorAnalog
Extract air pressure.
The extract air pressure is the controlled variable of the pressure controller of the extract air fan ExtAFan.
ExtADiffPrss
FB_BA_SensorAnalog
Differential pressure via the extract air fan
ExtAFan
FB_BA_AC_FanCtl
Control and regulation of the speed-controlled extract air fan.
ExtADiffPrssMonit
FB_BA_FdbAnalog
Analog differential pressure monitoring via the extract air fan.
Differential pressure monitoring uses the analog differential pressure sensor ExtADiffPrss and can trigger a plant shutdown alarm.
PreHtr
FB_BA_AC_PreHtr
Activation and control of a hot water air heater.
The function block is regarded as an aggregate and is part of the temperature sequence control of this plant due to its implemented sequence controller.
Erc
FB_BA_AC_ErcPl_02
Activation and control of a plate heat exchanger for the energy recovery of a ventilation system.
The function block is considered as an aggregate and is part of the temperature sequence control of this plant due to its implemented sequence controller.
Col
FB_BA_AC_ColT_02
Activation and control of a temperature-controlled cold water air cooler.
SpTRm
FB_BA_Scale_04_Y2_3
Setpoint program for supply air temperature control with a supply air temperature setpoint, including summer/winter compensation via a characteristic curve.
TCasCtrl
Room temperature control by means of room-supply air cascade. It consists of a master controller for setpoint calculation for heating, cooling and energy recovery.
SumNgtCol
FB_BA_AC_SumNgtCol
Night cooling control
OpMod
FB_BA_AC_OpMod1St
The function block is used to switch on the plant. It represents the choice of plant operation mode, a timer program and a plant selector switch.
PlantLock
FB_BA_PlantLock
When the function block is called, the relevant faults of the event-enabled objects are collected and output at this and lower levels of the plant. These relevant faults trigger the operation mode Fault E_BA_AC_OpMod01.eAlarm in the operation mode program OpMod. As a result, the air conditioning system is shut down.
A list of the faults that shut down the plant can be found under Fault shutdowns.
PlantCmd
The function block represents the plant command of the aggregates and functions of this air conditioning system. The integrated step sequence controller fixes the order in which the individual aggregates of the plant are switched on or off sequentially one after the other.
TSeqLink
FB_BA_AC_SeqT
Represents the start and control of the supply air temperature sequence control.
stTSeqLink
ST_BA_SeqLink
Data and command structure between the individual sequence controllers of the temperature control sequence PreHtr, Col, Erc and the supply air temperature sequence control TSeqLink.
arrAggregates
ST_BA_Aggregate
The array contains a bidirectional data and command structure for each aggregate.
When the step sequence controller is switched up or down, the switching command determined for each aggregate is transferred via the bidirectional communication structure arrAggregate. Feedback from the aggregates for switching the step sequence control up or down is transmitted to the plant control unit via the communication structure.