FB_BA_AC_TCasCtrl_01

FB_BA_AC_TCasCtrl_01 1:

The template is used for room temperature control by means of room-supply air cascade.

It consists of a master controller for calculating the supply air temperature setpoint for the aggregates heater, cooler and energy recovery.

The supply air temperature sequence control is enabled with the variable bOn by evaluating the receive block of the step sequence control Aggregate.

Principle diagram01

FB_BA_AC_TCasCtrl_01 2:

Principle diagram02

FB_BA_AC_TCasCtrl_01 3:
FB_BA_AC_TCasCtrl_01 4:

The initialization of the template takes place within the method FB_Init.

Block diagram

FB_BA_AC_TCasCtrl_01 5:

Syntax

FUNCTION_BLOCK FB_BA_AC_TCasCtrl_01 EXTENDS FB_BA_View
VAR_INPUT
  fSpTRm        : REAL;
  fTRm          : REAL;
END_VAR
VAR_OUTPUT
  fSpHtg        : REAL;
  fSpCol        : REAL;
  fSpErc        : REAL;
  fMax          : REAL;
  fMin          : REAL;
  bOn           : BOOL;
END_VAR
VAR_IN_OUT
  stAggregate   : ST_BA_Aggregate;
END_VAR
VAR_INPUT CONSTANT
  Sp            : FB_BA_AV_Op;
  Ctrl          : FB_BA_Loop;
  Aggregate     : FB_BA_Aggregate;
END_VAR
VAR
  PrioSwiVal    : FB_BA_PrioSwi_UDI04;
  MuxCmd        : FB_BA_MMUX_B04;
  MuxSp         : FB_BA_MMUX_R04;
END_VAR

FB_BA_AC_TCasCtrl_01 6: Inputs CONSTANT

Name

Type

Description

fSpTRm

REAL

Input variable for the room temperature setpoint.

fTRm

REAL

Input variable to which the room temperature is applied. The room temperature is the control value of the PID master controller Ctrl. If no room temperature is available, the outlet air temperature of a ventilation system can be used as control value.

FB_BA_AC_TCasCtrl_01 7: Outputs

Name

Type

Description

fSpHtg

REAL

Calculated setpoint of the supply air temperature for the heater.

fSpCol

REAL

Calculated setpoint of the supply air temperature for the cooler.

fSpErc

REAL

Calculated setpoint of the supply air temperature. for energy recovery.

fMax

REAL

Upper value of the controller output limitation.

fMin

REAL

Lower value of the controller output limitation.

bOn

BOOL

The output shows the resulting result of the multiplexer MuxCmd. This is further processed within the ventilation system and is used to enable the supply air temperature sequence control.

FB_BA_AC_TCasCtrl_01 8: Inputs/outputs

Name

Type

Description

stAggregate

ST_BA_Aggregate

Bidirectional aggregate structure via which the enables and switching values are transmitted to the evaluation function block of the step sequence control Aggregate. The aggregate structure transmits the recorded feedback signals up and down to the central plant control.

FB_BA_AC_TCasCtrl_01 9: Inputs CONSTANT

Name

Type

Description

Sp

FB_BA_AV_Op

Analog value object for displaying the supply air temperature setpoint.

Ctrl

FB_BA_Loop

The LOOP object serves as a master controller for a room temperature control by means of a room-supply air cascade. It provides the supply air temperature setpoint.

Aggregates

FB_BA_Aggregate

The aggregate function block represents a receive block of a step sequence controller.

Within the function block, the aggregate structure stAggregate is evaluated and integrated into the template using the inputs and outputs.

Variables

Name

Type

Description

PrioSwiVal

FB_BA_PrioSwi_UDI04

The priority switch uses the command structure stCmd to determine the modulation command for the multiplexer MuxCmd.

MuxCmd

FB_BA_MMUX_B04

The multiplexer determines the current switching command from the modulation command of the priority switch PrioSwiVal. The resulting output is sent to the output bOn.

The multiplexer defines the enabling conditions of the PID master controller Ctrl.

MuxSp

FB_BA_MMUX_R04

The multiplexer defines the supply air temperature setpoint depending on the priority switch PrioSwiVal.