FB_BA_AC_PlantCmd_AHU_1st_10
FB_BA_AC_PlantCmd_AHU_1st_10 1:
The template represents the plant command of an air conditioning system without humidification and dehumidification.
The function block PlantControl is the core of the plant command system. It serves as a higher-level plant control unit for the connected aggregates.
The corresponding switch-on or switch-off commands and their priority are determined for each aggregate according to the specified plant operation mode eOpMode and the information in the control matrix of the PlantControl unit.
The bidirectional communication to the aggregates of the air conditioning system takes place via the array arrAggregate, see Principle diagram plant.
The parameterization of the control matrix is done in the methods below this template.
FB_BA_AC_PlantCmd_AHU_1st_10 2:
The initialization of the template takes place within the method FB_Init.
Block diagram
FB_BA_AC_PlantCmd_AHU_1st_10 3:
FB_BA_AC_PlantCmd_AHU_1st_10 4:
FUNCTION_BLOCK FB_BA_AC_PlantCmd_AHU_1st_10 EXTENDS FB_BA_View
  eOpMode               : E_BA_AC_OpMod01;
  ePltStp               : E_BA_AC_PlantStep01;
  bStepCtrlUp           : BOOL;
  bStepCtrlDown         : BOOL;
  arrAggregate          : ARRAY [1..MAX(1,BA_Param.nMaxAggregate)] OF ST_BA_Aggregate;
VAR_INPUT CONSTANT
  DmpDlyCls             : FB_BA_AV_Op;
  SuAFanDlyOn           : FB_BA_AV_Op;
  ExtAFanDlyOn          : FB_BA_AV_Op;
  TempCtrlDlyOn         : FB_BA_AV_Op;
  PltStp                : FB_BA_MV_Op;
  PlantControl          : FB_BA_PlantControl;
VAR_INPUT CONSTANT PERSISTENT
  bInit                 : BOOL := TRUE;
  MMuxStart             : FB_BA_MMUX_B16;
  MMuxProfile           : FB_BA_MMUX_UDI16;
  MMuxPltStp            : FB_BA_MMUX_UDI16;
FB_BA_AC_PlantCmd_AHU_1st_10 5: Inputs
Type
eOpMode
E_BA_AC_OpMod01
Input of the current operation mode eOpMode, see template FB_BA_AC_OpMod1St.
FB_BA_AC_PlantCmd_AHU_1st_10 6: Outputs
Type
ePltStp
E_BA_AC_PlantStep01
Output of the current plant step of the air conditioning system.
bStepCtrlUp
Indicates that the order of the step sequence control is in the rising state.
bStepCtrlDown
Indicates that the order of the step sequence control is in the falling state.
FB_BA_AC_PlantCmd_AHU_1st_10 7: Inputs/outputs
Type
arrAggregates
The array contains a bidirectional data and command structure for each aggregate.
When the step sequence control is switched up or down, the switching command determined for each aggregate is transferred via the bidirectional communication structure arrAggregate. Feedback from the aggregates for switching the step sequence control up or down is transmitted to the PlantControl via the communication structure.
FB_BA_AC_PlantCmd_AHU_1st_10 8: Inputs CONSTANT
Type
DmpDlyCls
FB_BA_AV_Op
AV object for entering the value to delay the closing of the dampers during shutdown of the air conditioning plant, to take into account the overrun time of the fans during plant shutdown.
SuAFanDlyOn
FB_BA_AV_Op
AV object for entering a value for the start-up delay of the supply air fan when the air conditioning plant is switched on.
ExtAFanDlyOn
FB_BA_AV_Op
AV object for entering a value for the start-up delay of the extract air fan when the air conditioning plant is switched on.
TempCtrlDlyOn
FB_BA_AV_Op
AV object for entering a value for delayed temperature control enable.
PltStp
FB_BA_MV_Op
The MV object shows the current step of the plant's step sequence control.
PlantControl
FB_BA_PlantControl
The function block represents the higher-level plant control of a step sequence control of aggregates. The function block ensures that the individual aggregates of a plant are switched on or off sequentially one after the other in a certain order.
FB_BA_AC_PlantCmd_AHU_1st_10 9: Inputs CONSTANT PERSISTENT
Type
bInit
The variable is used to call the initialization methods for the control matrix in the CallInit method.
After starting the controller, the variable is set to FALSE after a PLC cycle and this state is saved persistently.
Variables
Type
MMuxStart
FB_BA_MMUX_B16
The multiplexer uses the plant operation mode eOpMode to define whether the air conditioning system is started or stopped.
MMuxProfile
FB_BA_MMUX_UDI16
The multiplexer uses the plant operation mode eOpMode to define the control profile of the PlantControl.
MMuxPltStp
FB_BA_MMUX_UDI16
The multiplexer evaluates the steps of the step sequence control and transfers them to the MV object PltStp for display at management level.
FB_BA_AC_PlantCmd_AHU_1st_10 10: Methods
Definition location
CallInit
Local
Calling the initialization methods for parameterization of the control matrix of the plant control unit.
ProfileDescription
Local
Used to initialize the parameter array arrProfileDescription of the plant control unit.
ProfileParameter0x
Local
Initialization of a part of the multidimensional profile parameter array arrProfileParameter of the control unit.
StepDescription
Local
Used to initialize the parameter array arrStepDescription of the plant control unit.