FB_BA_Scale_04_Y2_3
FB_BA_Scale_04_Y2_3 1:
The template is a setpoint program for an extract air/supply air cascade with only one room temperature setpoint, including summer and winter compensation.
Setpoint program for supply air temperature control with a supply air temperature setpoint, including summer/winter compensation via a characteristic curve.
The supply air temperature setpoint is determined by the function block Scale depending on the outside temperature.
FB_BA_Scale_04_Y2_3 2:
FB_BA_Scale_04_Y2_3 3:
The initialization of the template takes place within the method FB_Init.
Block diagram
FB_BA_Scale_04_Y2_3 4:
FUNCTION_BLOCK FB_BA_Scale_04 EXTENDS FB_BA_View
  fTWth    : REAL;
  fY       : REAL;
VAR_INPUT CONSTANT
  X1       : FB_BA_AV_Op;
  X2       : FB_BA_AV_Op;
  X3       : FB_BA_AV_Op;
  X4       : FB_BA_AV_Op;
  Y1       : FB_BA_AV_Op;
  Y2_3     : FB_BA_AV_Op;
  Y4       : FB_BA_AV_Op;
  Y        : FB_BA_AV_Op;
  Scale    : FB_BA_Chrct04;
FB_BA_Scale_04_Y2_3 5: Inputs
Type
fTWth
REAL
Current value of the outside temperature.
FB_BA_Scale_04_Y2_3 6: Outputs
Type
fY
REAL
Calculated setpoint for the room temperature.
FB_BA_Scale_04_Y2_3 7: Inputs CONSTANT
Type
X1
FB_BA_AV_Op
The AV object is used to specify the value for interpolation point X1.
X2
FB_BA_AV_Op
The AV object is used to specify the value for interpolation point X2.
X3
FB_BA_AV_Op
The AV object is used to specify the value for interpolation point X3.
X4
FB_BA_AV_Op
The AV object is used to specify the value for interpolation point X4.
Y1
FB_BA_AV_Op
The AV object is used to specify the value for interpolation point Y1.
Y2_3
FB_BA_AV_Op
The AV object is used to specify the value for the interpolation points Y2/Y3.
Y4
FB_BA_AV_Op
The AV object is used to specify the value for interpolation point Y4.
Y
FB_BA_AV_Op
Output of the calculated, simple room temperature setpoint. It is output at output fY.
Variables
Type
Scale
FB_BA_Chrct04
The function block represents a linear interpolation with four interpolation points and can be used to generate a characteristic curve. The function block calculates the setpoint curve for the current room temperature, depending on the outside temperature.