FB_BA_AC_SeqT
The template represents the start and control of the supply air temperature sequence control of an air conditioning (HVAC) system.
![]() | The initialization of the template takes place within the method FB_Init. |
Start behavior of the sequence
On startup of the air-conditioning plant the system determines whether to start with the heating, cooling or heat recovery sequence. The start sequence is selected depending on the plant operation mode eOpMode and the outside temperature fTWth. The result of the network at the input nNumStartCtrl of the function block SeqLink determines the start controller of the control sequence.
If the sequence controller specified at nNumStartCtrl is not ready for operation, the parameter enum eNoStartCtrlFound of the function block SeqLink is used to define the procedure for finding a new start controller. This ensures that the sequence always starts.
Control of the sequence control
Only one element of the sequence can be controlling. If a regulating sequence controller reaches its maximum or minimum value (Ymax,Ymin), the next controller in the sequence is switched to depending on the control direction.
Switching to another sequence controller can be delayed by specifying the time nSwiOverTi of the function block SeqLink.
The order of the temperature control sequences is specified by the globally defined enumeration variable E_BA_SeqNumber_T.
Block diagram
Principle diagram plant
FUNCTION_BLOCK FB_BA_AC_SeqT EXTENDS FB_BA_View
bEn : BOOL;
eOpMode : E_BA_AC_OpMod01;
fTWth : REAL;
bSumLmt : BOOL;
bWinLmt : BOOL;
nActvSeqCtrl : UDINT;
stTSeqLink : ST_BA_SeqLink;
VAR_INPUT CONSTANT
WthTLmtSum : FB_BA_AV_Op;
WthTLmtWin : FB_BA_AV_Op;
SeqLink : FB_BA_SequenceLinkBase;
ActvSeqCtrl : FB_BA_MV_Op;
WthTLmtWinHys : FB_BA_Swi2P;
WthTLmtSumHys : FB_BA_Swi2P;
StartSeq : FB_BA_PrioSwi_UDI08;
Name | Type | Description |
bEn |
BOOL |
Activation of the supply air temperature sequence control. |
eOpMode |
The plant operation mode is used for the selection of the start sequence controller. | |
fTWth |
REAL |
Input for the weather temperature. |
Outputs
bSumLmt | BOOL | The output variable indicates that the ventilation system starts with the cooling sequence. |
bWinLmt | BOOL | The output variable indicates that the ventilation system starts with the heating sequence. |
nActvSeqCtrl | UDINT | The output variable shows the number of the active sequence controller. |
Inputs/outputs
stTSeqLink |
Data and command structure between the individual sequence controllers FB_BA_SeqCtrl of the temperature control sequence (preheater, energy recovery, cooler) and the control block SeqLink. |
Inputs CONSTANT
WthTLmtSum | AV object for input of an outside temperature limit value from which the air-conditioning plant starts in the heating sequence. | |
WthTLmtWin | AV object for input of an outside temperature limit value from which the air-conditioning plant starts in the cooling sequence | |
SeqLink | The function block SeqLinkH is the core of the template FB_BA_AC_SeqT. The sequence linker is connected to the supply air controllers of the sequence via the data structure stTSeqLink. It is the central control element, and responsible for switching between the sequence controllers and starting of the control sequence. | |
ActvSeqCtrl | The MV object indicates the currently active sequence controller. |
Variables
WthTLmtWinHys | FB_BA_Swi2P | Two-position switch which generates the binary switching signal for bWinLmt based on the weather temperature fTWth and the winter weather temperature limit value WthTLmtWin. |
WthTLmtSumHys | FB_BA_Swi2P | Two-position switch which generates the binary switching signal for bWinLmt based on the weather temperature fTWth and the limit value weather temperature summer WthTLmtSum. |
StartSeq | The priority switch is used to select the start sequence. Prio 1: bEN01 In the overheating protection E_BA_AC_OpMod01.eOverHeatingProtection, the cooling sequence (E_BA_AC_SeqNumber.eCooler) is always started. Prio 2: bEN02 In the cool-down protection mode E_BA_AC_OpMod01.eCoolDownProtection, the heating sequence (E_BA_AC_SeqNumber.ePreHeater) is always started. Prio 4: bEN04 The upstream function block WthTLmtWinHys checks whether the actual outside temperature is below the critical value of AV object WthTLmtSum. If this is the case, the air-conditioning system starts with the sequence controller of the preheater (E_BA_AC_SeqNumber.ePreHeater). Prio 5: bEN05 The upstream function block WthTLmtSumHys checks whether the actual outside temperature is above the value of AV object WthTLmtSum. If this is the case, the air conditioning system starts with the sequence controller of the cooler (E_BA_AC_SeqNumber.eCooler). Prio 8: bEN08 In the transitional periods between winter and summer, the inputs of StartSeq.bEn04 and StartSeq.bEn05 are FALSE on account of the weather. In this case, priority 8 applies to the priority switch, meaning that the air-conditioning system is started in the energy recovery sequence (E_BA_AC_SeqNumber.eEnergyRecovery). |