FB_BA_SequenceLinkBase
FB_BA_SequenceLinkBase 1:
The FB_BA_SequenceLinkBase function block represents the higher-level connection of a sequence control.
Data exchange sequence control
The data exchange between the sequence controllers FB_BA_SeqCtrl and the FB_BA_SequenceLinkBase takes place via the stSeqLink structure.
FB_BA_SequenceLinkBase 2:
Start behavior of the sequence
A TRUE signal at bEn input enables the entire sequence control. The function block will initially activate the sequence controller that is known at nNumStartCtrl. All other sequence controller base their output value on the ranking of the active controller.
If the sequence controller specified at nNumStartCtrl is not ready for operation, the enum eNoStartCtrlFound defines the procedure to find a new start controller. This ensures that the sequence always starts.
Switching in the sequence
If a sequence controller reaches its maximum or minimum value, the system switches to the next controller in the sequence depending on the control direction, provided that the actual value falls below or exceeds the setpoint of the next controller.
4 cases are distinguished:
Switching to another sequence controller can be delayed by specifying the time nSwiOverTi.
Operational readiness of the sequence controllers
If a controller loses its operational readiness in the sequence (missing enable bEn), it is no longer available for the entire sequence.
If this is not the previously active controller, a temperature change may occur, depending on which control value this controller has output, which is compensated by the controller sequence, if possible.
However, if it is the active sequence controller, the enumeration eNoEnableSeqCtrl defines the procedure to find a new, active sequence controller.
If a sequence controller obtains its operational readiness in the running process, the controller is added to the sequence. Depending on the control direction E_BA_Action and its own sequence number nMyNum it will be placed in the controller sequence and output its minimum or maximum value. The resulting temperature change is compensated by the controller sequence, if possible.
Error detection
The error messages listed below are detected by FB_BA_SequenceLinkBase.
The x in the text messages stands for a numerical specification of a sequence controller.
The error messages are output in the "Error list" window in the Tc3 development environment. This can be activated under the menu item View.
Output of the error texts via the property StateText.
The enumeration eState additionally displays the messages.
FB_BA_SequenceLinkBase 3:
Globaler Parameter Tc3_BA2.BA_Param.nMaxSeqCtrl < 1
This message is the only one that disables sequence control.
German
English
Der nächste Sequenzsollwert ist kleiner als sein Vorgänger: x
Next sequence setpoint is smaller than its predecessor: x
Global parameter Tc3_BA2.BA_Param.nMaxSeqCtrl < 1
Mehrfache Wirkrichtung "eActn" in der Sequenzsteuerung
Multiple direction of action "eActn" of the sequence controller
Startsequenzregler ist nicht freigegeben: nNumStartCtrl = x
Start sequence controller is not enabled: nNumStartCtrl = x
Kein Sequenzregler ist betriebsbereit
No sequence controller is operational
Sequenznummer mehrfach vergeben: x
Sequence number assigned multiple times: x
FUNCTION_BLOCK FB_BA_SequenceLinkBase
  bEn                                     : BOOL;
  nNumStartCtrl                           : UDINT;
  {attribute 'parameterUnit':= 's'}
  nSwiOverTi                              : UDINT(0..1800);
  bSeqCtrlOperational                     : BOOL;
  nActvSeqCtrl                            : UDINT;
  fActvSeqCtrl_Y                          : REAL;
  fActvSeqCtrl_X                          : REAL;
  fActvSeqCtrl_W                          : REAL;
  bActvSeqCtrlIsMaxLimit                  : BOOL;
  bActvSeqCtrlIsMinLimit                  : BOOL;
  bErr                                    : BOOL;
  eState                                  : E_BA_StateSeqLink;
  nRemTiSwiOvrTi                          : UDINT;
  stSeqLink                               : ST_BA_SeqLink;
VAR_INPUT CONSTANT
  fHys                                    : REAL := 0.2;
  eNoStartCtrlFound                       : E_BA_NoStartCtrlFound := E_BA_NoStartCtrlFound.eLastActionReverse;
  eNoEnableSeqCtrl                        : E_BA_NoEnableSeqCtrl := E_BA_NoEnableSeqCtrl.eNextAction;
FB_BA_SequenceLinkBase 4: Inputs
Type
bEn
Sequence control is activated when the function block is enabled. However, the sequence controllers must first be enabled.
nNumStartCtrl
UDINT
Ordinal number of the sequence controller, which should be the start controller when the sequence is activated.
An internal limitation allows only values from 1 - BA_Param.nMaxSeqCtrl.
nSwiOverTi
UDINT
Switching to another sequence controller can be delayed by the time specification.
An internal limitation only allows values from 0 - 1800 seconds.
FB_BA_SequenceLinkBase 5: Outputs
Type
bSeqCtrlOperational
The sequence control is ready to operate or is in operation.
nActvSeqCtrl
UDINT
The output variable shows the number of the active sequence controller.
fActvSeqCtrl_Y
REAL
Control value of the active sequence controller.
fActvSeqCtrl_X
REAL
Actual value of the active sequence controller.
fActvSeqCtrl_W
REAL
Setpoint of the active sequence controller.
The upper output limit of the active sequence controller has been reached.
If it has not yet been advanced to the next sequence controller, bActvSeqCtrlIsMaxLimit is not set to FALSE until fActvSeqCtrl_Y has fallen below (fActvSeqCtrl_Y - fHys).
The lower output limit of the active sequence controller has been reached.
If it has not yet been advanced to the next sequence controller, bActvSeqCtrlIsMinLimit is not set to FALSE until fActvSeqCtrl_Y has risen above (fActvSeqCtrl_Y + fHys).
bErr
Indicates that an error has been detected.
More detailed information is provided by the property StateText. In addition, the enum eState displays further information.
Further explanations on error analysis can be found at Error detection.
eState
E_BA_StateSeqLink
The enumeration shows the state of the FB_BA_SequenceLinkBase and the sequence control.
nRemTiSwiOvrTi
UDINT
Countdown of switching to the next sequence controller [s].
FB_BA_SequenceLinkBase 6: / FB_BA_SequenceLinkBase 7: Inputs Outputs
Type
stSeqLink
ST_BA_SeqLink
Data and command structure between the individual sequence controllers FB_BA_SeqCtrl and the function block FB_BA_SequenceLinkBase.
FB_BA_SequenceLinkBase 8: Inputs CONSTANT
Type
fHys
REAL
This value sets a hysteresis around the upper and lower output limit bActvSeqCtrlIsMaxLimit / bActvSeqCtrlIsMinLimit of the active sequence controller.
An internal limitation only allows values from 0 - 2.
eNoStartCtrlFound
If during the running process the active sequence controller loses its operational readiness, then the enumeration defines the procedure to find a new, active sequence controller.
eNoEnableSeqCtrl
If the start controller at the input nNumStartCtrl is not available or enabled, the enumeration defines the procedure to find a new start controller.
FB_BA_SequenceLinkBase 9: Properties
Type
Access
FirstActvSeqCtrl
UDINT
Get
The property shows the number of the first sequence controller ready for operation.
FirstActvSeqCtrlWithActionDirect
UDINT
Get
The property shows the number of the first sequence controller ready for operation with the control direction E_BA_Action.eDirect.
LastActvSeqCtrl
UDINT
Get
The property shows the number of the last sequence controller ready for operation.
LastActvSeqCtrlWithActionReverse
UDINT
Get
The property shows the number of the last sequence controller ready for operation with the control direction E_BA_Action.eReverse.
NextActionActvSeqCtrl
UDINT
Get
Depending on the control direction of the active sequence controller nActvSeqCtrl the next sequence controller ready for operation is displayed here.
Cooling/Direct control direction: next sequence controller ready for operation with the Cooling/Direct control direction (after 5 would come 6 or higher). If none is found, then E_BA_NoEnableSeqCtrl.eLastSeqNum is implemented.
Heating/reverse control direction: previous operational sequence controller with heating/reverse control direction (after 5 would come 4 or lower). If none is found, then E_BA_NoEnableSeqCtrl.eFirstSeqNum is implemented.
NextActvSeqCtrl
UDINT
Get
The property shows the number of the next sequence controller ready for operation after the last active one (after 5 would come 6 or higher).
PreviousActvSeqCtrl
UDINT
Get
The property shows the number of the previous sequence controller ready for operation after the last active one (after 5 would come 4 or lower).
ActvSeqCtrl
UDINT
Get
The property shows the number of the active sequence controller, see nActvSeqCtrl.
ActvSeqCtrl_ControlValue
REAL
Get
The property shows the control value of the active sequence controller, see fActvSeqCtrl_Y.
ActvSeqCtrl_IsMaxLimit
Get
The property indicates that the upper output limit of the active sequence controller has been reached, see bActvSeqCtrlIsMaxLimit.
ActvSeqCtrl_IsMinLimit
Get
The property indicates that the lower output limit of the active sequence controller has been reached, see bActvSeqCtrlIsMinLimit.
ErrorParamMaxSeqCtrl
T_MaxString
Get
The property displays the following text in case of error: "Global parameter Tc3_BA2.BA_Param.nMaxSeqCtrl < 1", see BA_Param.nMaxSeqCtrl.
The global parameter must be adjusted in any case, because due to the wrong parameterization the sequence stops.
ErrorStartSeqCtrlNotOperable
T_MaxString
Get
The property displays the following text in case of error: "Start sequence controller is not enabled: nNumStartCtrl = x".
A check of the start sequence controller, which was specified with the input variable nNumStartCtrl, is required.
MultiDirectionActionSeqCtrl
T_MaxString
Get
The property displays the following text in case of error: Multiple direction of action "eActn" of the sequence controller: x.
Multiple direction of action of the sequence controller. It always looks from the sequence controller with the smallest number to the next largest one. It is possible to change the direction of action.
NextSeqSpIsSmaller
T_MaxString
Get
The property displays the following text in case of error: "Next sequence setpoint is smaller than its predecessor: x".
A check of the setpoints of the sequence controllers according to ascending order is required.
NoSeqCtrlIsOperational
T_MaxString
Get
The property displays the following text in case of an error: "No sequence controller is operational".
A check of the operational readiness of the sequence controllers is required.
SeqNumMulti
T_MaxString
Get
The property displays the following text in case of error: "Sequence number assigned multiple times: x".
A check of the displayed sequence number is necessary because it has been assigned several times in the sequence.
Development environment
Required PLC library
TwinCAT from v3.1.4024.56
Tc3_XBA from v5.6.1.0