IDN 3015 (P-0-3015) Hardware Limit Switch Consequence
This parameter define the consequence off the Hardware Limit Switch, if the corresponding digital inputs ( IDN 3002 and/or IDN 3003 ) are set to the limit switches.
If the hardware limit switch consequence is set to 0, then the Limit switch consequence is a warning. Else if the IDN P3015 is set to 1, then the switch consequence is a fault and the drive ramp down with setting the following fault bits, in IDN 11 bit 15 and in IDN 129 the bit 2.
After the reset class 1 diagnostic command ( IDN 99 ) the drive could enable again and move back in the valid range. During the procedure drive controlled homing ( IDN 148 ), the hardware limit switch could use in the normal way (refer to IDN 3027 .
If the hardware limit switch consequence is set to 0, then the Limit switch consequence is a warning. Else if the IDN IDN 3015 is set to 1, then the switch consequence is a fault and the drive ramp down with setting the following fault bits, in IDN 11 bit 15 and in IDN 129 the bit 2.
Data Length:
2 bytes
Non-Volatile:
Yes
Data Type:
Unsigned decimal
Write Access:
CP2, CP3, CP4
Minimum:
0
Run-Up Check:
Maximum:
1
Cyclic Transfer:
Default:
0
Serial Equiv:
SERCSET (Bit 0)
Units:
Version:
5.04
IDN Type:
VE
ADS Index Group (hex.):
0x8BC7