IDN 11 (S-0-0011) Class 1 Diagnostic (C1D)
The current fault status of the drive. When a fault occurs, the drive decelerates to a stop and is disabled.
The C1D status bit (AT bit 13) is set, and the corresponding fault bits are set within IDN 11. All faults are latched within IDN 11 and are reset through the „Procedure: Reset Class 1 Diagnostic“ ( IDN 99 ). IDN 99 performs a cold start automatically when required. Those faults which require a cold start are noted in the table below. The error messages which appear on the front panel of the drive are also shown below.
Data Length:
2 bytes
Non-Volatile:
No
Data Type:
Binary
Write Access:
Read-only
Minimum:
Run-Up Check:
Maximum:
Cyclic Transfer:
Default:
0
Serial Equiv:
ERRCODE
Units:
Version:
5.04
IDN Type:
MT
ADS Index Group (hex.):
0x000B
Definition:
Bit
Coldstart
LED Error
LSB 0
Overload fault ( IDN 114 ).
no
F15
1
Amplifier over temperature fault ( IDN 203 ).
no
F01
2
Motor over temperature fault.
yes
F06
3
Cooling system fault ( IDN 205 ).
no
F13
4
Control voltage fault ((15V).
yes
F07
5
Feedback loss fault.
yes
F04
6
Commutation fault. Set to 0.
yes
F25
7
Over current fault.
yes
F14
8
Over voltage fault.
no
F02
9
Under voltage fault.
no
F05
10
Power supply phase fault.
no
F12, F19
11
Excessive position deviation ( IDN 159 ).
no
F03
12
Communication interface fault ( IDN 14 ).
no
F29
13
Software limit switch fault ( IDN 49 and 50).
no
F24
14
Reserved. Set to 0.
MSB 15
Manufacturer defined fault ( IDN 129 ).
IDN 129