IDN 129 (S-0-0129) Manufacturer Class 1 Diagnostic (MC1D)
Lists the status of the latched manufacturer defined drive faults. When a manufacturer defined fault occurs, the drive decelerates to a stop and disables.
The C1D status bit (AT status bit 13) is set, IDN 11 bit 15 is set, and the corresponding manufacturer-defined fault bit is set within IDN 129.
All manufacturer defined faults are latched within IDN 129 and are reset through the „Reset Class 1 Diagnostic“ procedure ( IDN 99 ). IDN 99 performs a cold start automatically when required. Those faults which require a cold start are noted in the table below. The error messages which appear on the front panel of the drive are also shown below.
Data Length:
2 bytes
Non-Volatile:
No
Data Type:
Binary
Write Access:
Read-only
Minimum:
Run-Up Check:
Maximum:
Cyclic Transfer:
Default:
0
Serial Equiv:
ERRCODE
Units:
Version:
5.04
IDN Type:
MT:FS
ADS Index Group (hex.):
0x0081
Definition:
Bit
Cold start
LED Error
LSB 0
Reserved
1
Non-volatile memory check-sum fault
yes
F09, F10
2
Warning fault (actual warning is mask to a fault)
no
F24
3
Motor brake fault
yes
F11
4
Supply voltage not present
no
F16
5
A/D converter fault
yes
F17
6
Regeneration fault
yes
F18
7
System fault
yes
F32
8
Reserved
9
Motor over speed fault
no
F08
10
Excessive position command difference
No
F28
11
Non-permissible software-enable (no hardware-enable; no SERCOS control)
No
F29
12 – 15
Reserved