MP_VRU_Process
This function block is suitable for VAV actuators VRU-D3-BAC, VRU-M1-BAC and VRU-M1R-BAC (max. 8 slaves). For more information please visit www.belimo.com.
MP_Address is used to specify the MP-Bus device with which the function block is to communicate. bStart activates communication with the MP-Bus device. bBusy indicates that the function block is active. If bStart remains TRUE, the device is addressed cyclically with a period specified by the time in TMPolling. The time should be set longer than 1 s. bError is used to indicate an error in communication with the actuator. The type of the error can be read with iErrorId.
MP_Address : USINT := 1;
bStart : BOOL;
strDataKL6771 : DataKL6771;
TMpolling : TIME := t#10s;
rSetpoint : LREAL;
nOverrideControl : E_MP_VRU_OverrideControl;
nCommand : E_MP_VRU_Command;
nDataRead : BYTE;
MP_Address | USINT | MP-Bus address of the slave. |
bStart | BOOL | A positive edge starts the function block. If this remains continuously TRUE, the function block will be activated cyclically with a period specified by the time in TMPolling. |
strDataKL6771 | The data structure with which the KL6771() function block must be linked. | |
TMpolling | TIME | The time for which the function block should address the actuator. Default 10 s, minimum time 1 s. |
rSetpoint | LREAL | Setpoint in % (0...100). |
nOverrideControl | Setpoint override | |
nCommand | Command for service and test functions of the actuator. | |
nDataRead | BYTE | 0xFF - read all data; bit 0 - read relative position; bit 1 - read absolute position; bit 2 - read relative volume flow rate; bit 3 - read absolute volume flow rate; bit 4 - read value sensor 1; bit 5 - read analog setpoint; bit 6 - read relative differential pressure; bit 7 - read absolute differential pressure |
Outputs
iErrorId : MP_Error;
strMP_Serial_Number : MP_Serial_Number;
st_MP_VRU_ServiceInfo : St_MP_VRU_ServiceInfo;
rSetpoint_Read : LREAL;
nOverrideControl_Read : E_MP_VRU_OverrideControl;
nCommand_Read : E_MP_VRU_Command;
rRelativePosition : LREAL;
rAbsolutePosition : LREAL;
rRelativeVolumeticFlow : LREAL;
rAbslouteVolumeticFlow : LREAL;
rSensor1Value : LREAL;
rSetpointAnalog : LREAL;
rRelativeDeltaPressure : LREAL;
rAbsoluteDeltaPressure : LREAL;
bBusy | BOOL | This bit is set for as long as the function block is active. |
bError | BOOL | This output goes TRUE as soon as an error occurs. This error is described via the iErrorId variable. |
iErrorId | This output outputs an error code in the event of an error. bError goes TRUE at the same time. | |
strMP_Serial_Number | Structure for the serial number. | |
st_MP_VRU_ServiceInfo | Malfunction and service information | |
rSetpoint_Read | LREAL | Setpoint |
nOverrideControl_Read | Override | |
nCommand_Read | Command | |
rRelativePosition | LREAL | Relative position in %. Value -1 means data disabled (see VAR_INPUT nDataRead). |
rAbsolutePosition | LREAL | Absolute position in °. Value -1 means data disabled (see VAR_INPUT nDataRead). |
rRelativeVolumeticFlow | LREAL | Relative volume flow rate in %. Value -1 means data disabled (see VAR_INPUT nDataRead). |
rAbslouteVolumeticFlow | LREAL | Absolute volume flow rate in m³/h. Value of -1 means data disabled (see VAR_INPUT nDataRead). |
rSensor1Value | LREAL | Value of sensor 1 in mV/Ohm. Value -1 means data disabled (see VAR_INPUT nDataRead). |
rSetpointAnalog | LREAL | Analog setpoint in %. Value -1 means data disabled (see VAR_INPUT nDataRead). |
rRelativeDeltaPressure | LREAL | Relative differential pressure %. Value -1 means data disabled (see VAR_INPUT nDataRead). |
rAbsoluteDeltaPressure | LREAL | Absolute differential pressure in Pa. Value -1 means data disabled (see VAR_INPUT nDataRead). |
Development environment | PLC library to include |
TwinCAT from v3.1.4024.22 | Tc2_MPBus from 3.4.13.0 |