EPI3188-0022
Index 0000 direct parameters 1
Index (hex)  | Name  | Meaning  | Data type  | Flags  | Default  |
0000:01  | Reserved  | -  | UINT8  | RO  | 0  |
0000:02  | Master Cycle Time  | IO-Link specific  | UINT8  | RO  | 0  |
0000:03  | Min Cycle Time  | IO-Link specific  | UINT8  | RO  | 0  |
0000:04  | M-Sequence Capability  | IO-Link specific  | UINT8  | RO  | 0  |
0000:05  | IO-Link Version ID  | IO-Link specific  | UINT8  | RO  | 0  |
0000:06  | Process Data Input Length  | IO-Link specific  | UINT8  | RO  | 0  |
0000:07  | Process Data Output Length  | IO-Link specific  | UINT8  | RO  | 0  |
0000:08  | Vendor ID  | Vendor ID 1  | UINT8  | RO  | 0  |
0000:09  | Vendor ID  | Vendor ID 2  | UINT8  | RO  | 0  |
0000:0A  | Device ID  | Device ID 1  | UINT8  | RO  | 0  |
0000:0B  | Device ID  | Device ID 2  | UINT8  | RO  | 0  |
0000:0C  | Device ID  | Device ID 3  | UINT8  | RO  | 0  |
0000:0D  | Reserved  | -  | UINT8  | RO  | 0  |
0000:0E  | Reserved  | -  | UINT8  | RO  | 0  |
0000:0F  | Reserved  | -  | UINT8  | RO  | 0  |
0000:10  | System Command  | IO-Link specific  |
  | RO  | 0  |
Index 0001 direct parameters 2
0001:01  | Device Specific Parameter 1  | IO-Link specific  | UINT8  | RW  | 0  |
0001:02  | Device Specific Parameter 2  | IO-Link specific  | UINT8  | RW  | 0  |
0001:03  | Device Specific Parameter 3  | IO-Link specific  | UINT8  | RW  | 0  |
0001:04  | Device Specific Parameter 4  | IO-Link specific  | UINT8  | RW  | 0  |
0001:05  | Device Specific Parameter 5  | IO-Link specific  | UINT8  | RW  | 0  |
0001:06  | Device Specific Parameter 6  | IO-Link specific  | UINT8  | RW  | 0  |
0001:07  | Device Specific Parameter 7  | IO-Link specific  | UINT8  | RW  | 0  |
0001:08  | Device Specific Parameter 8  | IO-Link specific  | UINT8  | RW  | 0  |
0001:09  | Device Specific Parameter 9  | IO-Link specific  | UINT8  | RW  | 0  |
0001:0A  | Device Specific Parameter 10  | IO-Link specific  | UINT8  | RW  | 0  |
0001:0B  | Device Specific Parameter 11  | IO-Link specific  | UINT8  | RW  | 0  |
0001:0C  | Device Specific Parameter 12  | IO-Link specific  | UINT8  | RW  | 0  |
0001:0D  | Device Specific Parameter 13  | IO-Link specific  | UINT8  | RW  | 0  |
0001:0E  | Device Specific Parameter 14  | IO-Link specific  | UINT8  | RW  | 0  |
0001:0F  | Device Specific Parameter 15  | IO-Link specific  | UINT8  | RW  | 0  |
0001:10  | Device Specific Parameter 16  | IO-Link specific  | UINT8  | RW  | 0  |
Index 0002 standard command
0002  | Standard Command  | IO-Link specific  | UINT8  | RW  | 0  |
Index 000C Device Access Locks
000C:01  | Parameter (write) Access Lock  | 0: Write access for the parameters is enabled. 1: Write access for the parameters is disabled.  | BOOL  | RW  | FALSE  |
000C:02  | Data Storage Lock  | 0: The data storage function is enabled. 1: The data storage function is disabled.  | BOOL  | RW  | FALSE  |
000C:03  | Local Parameterization Lock  | 0: Local parameterization is enabled. 1: Local parameterization is disabled.  | BOOL  | RW  | FALSE  |
000C:04  | Local User Interface Lock  | 0: The local user interface is enabled. 1: The local user interface is disabled.  | BOOL  | RW  | FALSE  |
Index 0010 vendor name
0010  | Vendor Name  | Vendor name  | String  | R  | Beckhoff Automation GmbH & Co. KG  |
Index 0011 vendor text
0011  | Vendor Text  | Vendor-specific text  | String  | R  | www.beckhoff.com  |
Index 0012 Product Name
0012  | Product Name  | Product designation  | String  | R  | EPI3188-0022  |
Index 0013 Product ID
0013  | Product ID  | Product designation  | String  | R  | EPI3188-0022  |
Index 0014 Product Text
0014  | Product Text  | Product description  | String  | R  | 8 Analog Input Module  |
Index 0015 serial number
0015  | Serial Number  | Serial number  | String  | R  | 00000000  |
Index 0016 Hardware version
0016  | Hardware version  | Hardware version  | String  | R  | 00  |
Index 0017 firmware version
0017  | Firmware version  | Firmware version  | String  | R  | 00  |
Index 0018 application-specific tag
0018:00  | Application Specific Tag  | Application-specific description  | String  | RW  | ********************** **********  |
Index 0050 IO status
0050:01  | State  | Indicates the status of the IO board. The IO board is working properly if state = 8dec. and status code = 0 Other values indicate an error on the IO board.  | UINT16  | RO  | 0x0000 (0dec)  |
0050:02  | Status code  | UINT16  | RO  | 0x0000 (0dec)  |
Index 0800 AI Settings Ch1
Index (hex)  | Name  | Description  | Data type  | Flags  | Default  |
0800:01  | Enable user scale  | Enabling the user scaling.  | BOOL  | RW  | 0  |
0800:02  | Presentation  | Select the data format of the measured values.  | UINT3  | RW  | 0 ("Signed")  |
0800:06  | Enable filter  | Enabling the digital filter.  | BOOL  | RW  | 0  |
0800:07  | Enable limit 1  | Enabling the limit value monitoring for the limit value "Limit 1".  | BOOL  | RW  | 0  |
0800:08  | Enable limit 2  | Enabling the limit value monitoring for the limit value "Limit 2"  | BOOL  | RW  | 0  |
0800:0A  | Enable user calibration  | Enabling the user calibration.  | BOOL  | RW  | 0  |
0800:0B  | Enable vendor calibration  | Enabling the vendor calibration.  | BOOL  | RW  | 1  |
0800:0E  | Swap limit bits  | Invert comparison operation of the limit value monitoring.  | BOOL  | RW  | 0  |
0800:11  | User scale offset  | Offset value for the user scaling.  | INT16  | RW  | 0  |
0800:12  | User scale gain  | Gain value for the user scaling.  | INT32  | RW  | 65536dec  |
0800:13  | Limit 1  | Limit value "Limit 1" for the limit value monitoring.  | INT16  | RW  | 0  |
0800:14  | Limit 2  | Limit value "Limit 2" for the limit value monitoring.  | INT16  | RW  | 0  |
0800:15  | Filter settings  | Select the type of digital filter.  | INT16  | RW  | 2 ("IIR1")  |
0800:17  | User calibration offset  | Offset value for the user calibration.  | INT16  | RW  | 0  |
0800:18  | User calibration gain  | Gain value for the user calibration.  | INT16  | RW  | 16384dec  |
Index 080D AI Advanced Settings Ch.1
080D:11  | Input Type  | Set the measuring range.  | UINT16  | RW  | 2 ("U ±10 V")  |
080D:12  | Scaler  | Select the nominal or technical measuring range.  | UINT16  | RW  | 0 ("Extended Range")  |
080D:17  | Low Range Error  | The Status bit "Error" is set if the measured value is smaller than this parameter.  | INT32  | RW  | 1048568dec  |
080D:18  | High Range Error  | The Status bit "Error" is set if the measured value is smaller than this parameter.  | INT32  | RW  | 32767dec  |
Index 0810 AI Settings Ch2
0810:01  | Enable user scale  | Enabling the user scaling.  | BOOL  | RW  | 0  |
0810:02  | Presentation  | Select the data format of the measured values.  | UINT3  | RW  | 0 ("Signed")  |
0810:06  | Enable filter  | Enabling the digital filter.  | BOOL  | RW  | 0  |
0810:07  | Enable limit 1  | Enabling the limit value monitoring for the limit value "Limit 1".  | BOOL  | RW  | 0  |
0810:08  | Enable limit 2  | Enabling the limit value monitoring for the limit value "Limit 2"  | BOOL  | RW  | 0  |
0810:0A  | Enable user calibration  | Enabling the user calibration.  | BOOL  | RW  | 0  |
0810:0B  | Enable vendor calibration  | Enabling the vendor calibration.  | BOOL  | RW  | 1  |
0810:0E  | Swap limit bits  | Invert comparison operation of the limit value monitoring.  | BOOL  | RW  | 0  |
0810:11  | User scale offset  | Offset value for the user scaling.  | INT16  | RW  | 0  |
0810:12  | User scale gain  | Gain value for the user scaling.  | INT32  | RW  | 65536dec  |
0810:13  | Limit 1  | Limit value "Limit 1" for the limit value monitoring.  | INT16  | RW  | 0  |
0810:14  | Limit 2  | Limit value "Limit 2" for the limit value monitoring.  | INT16  | RW  | 0  |
0810:15  | Filter settings  | Select the type of digital filter.  | INT16  | RW  | 2 ("IIR1")  |
0810:17  | User calibration offset  | Offset value for the user calibration.  | INT16  | RW  | 0  |
0810:18  | User calibration gain  | Gain value for the user calibration.  | INT16  | RW  | 16384dec  |
Index 081D AI Advanced Settings Ch.2
081D:11  | Input Type  | Set the measuring range.  | UINT16  | RW  | 2 ("U ±10 V")  |
081D:12  | Scaler  | Select the nominal or technical measuring range.  | UINT16  | RW  | 0 ("Extended Range")  |
081D:17  | Low Range Error  | The Status bit "Error" is set if the measured value is smaller than this parameter.  | INT32  | RW  | 1048568dec
081D:18  | High Range Error  | The Status bit "Error" is set if the measured value is smaller than this parameter.  | INT32  | RW  | 32767dec  |
Index 0820 AI Settings Ch3
0820:01  | Enable user scale  | Enabling the user scaling.  | BOOL  | RW  | 0  |
0820:02  | Presentation  | Select the data format of the measured values.  | UINT3  | RW  | 0 ("Signed")  |
0820:06  | Enable filter  | Enabling the digital filter.  | BOOL  | RW  | 0  |
0820:07  | Enable limit 1  | Enabling the limit value monitoring for the limit value "Limit 1".  | BOOL  | RW  | 0  |
0820:08  | Enable limit 2  | Enabling the limit value monitoring for the limit value "Limit 2"  | BOOL  | RW  | 0  |
0820:0A  | Enable user calibration  | Enabling the user calibration.  | BOOL  | RW  | 0  |
0820:0B  | Enable vendor calibration  | Enabling the vendor calibration.  | BOOL  | RW  | 1  |
0820:0E  | Swap limit bits  | Invert comparison operation of the limit value monitoring.  | BOOL  | RW  | 0  |
0820:11  | User scale offset  | Offset value for the user scaling.  | INT16  | RW  | 0  |
0820:12  | User scale gain  | Gain value for the user scaling.  | INT32  | RW  | 65536dec  |
0820:13  | Limit 1  | Limit value "Limit 1" for the limit value monitoring.  | INT16  | RW  | 0  |
0820:14  | Limit 2  | Limit value "Limit 2" for the limit value monitoring.  | INT16  | RW  | 0  |
0820:15  | Filter settings  | Select the type of digital filter.  | INT16  | RW  | 2 ("IIR1")  |
0820:17  | User calibration offset  | Offset value for the user calibration.  | INT16  | RW  | 0  |
0820:18  | User calibration gain  | Gain value for the user calibration.  | INT16  | RW  | 16384dec  |
Index 082D AI Advanced Settings Ch.3
082D:11  | Input Type  | Set the measuring range.  | UINT16  | RW  | 2 ("U ±10 V")  |
082D:12  | Scaler  | Select the nominal or technical measuring range.  | UINT16  | RW  | 0 ("Extended Range")  |
082D:17  | Low Range Error  | The Status bit "Error" is set if the measured value is smaller than this parameter.  | INT32  | RW  | 1048568dec
082D:18  | High Range Error  | The Status bit "Error" is set if the measured value is smaller than this parameter.  | INT32  | RW  | 32767dec  |
Index 0830 AI Settings Ch4
0830:01  | Enable user scale  | Enabling the user scaling.  | BOOL  | RW  | 0  |
0830:02  | Presentation  | Select the data format of the measured values.  | UINT3  | RW  | 0 ("Signed")  |
0830:06  | Enable filter  | Enabling the digital filter.  | BOOL  | RW  | 0  |
0830:07  | Enable limit 1  | Enabling the limit value monitoring for the limit value "Limit 1".  | BOOL  | RW  | 0  |
0830:08  | Enable limit 2  | Enabling the limit value monitoring for the limit value "Limit 2"  | BOOL  | RW  | 0  |
0830:0A  | Enable user calibration  | Enabling the user calibration.  | BOOL  | RW  | 0  |
0830:0B  | Enable vendor calibration  | Enabling the vendor calibration.  | BOOL  | RW  | 1  |
0830:0E  | Swap limit bits  | Invert comparison operation of the limit value monitoring.  | BOOL  | RW  | 0  |
0830:11  | User scale offset  | Offset value for the user scaling.  | INT16  | RW  | 0  |
0830:12  | User scale gain  | Gain value for the user scaling.  | INT32  | RW  | 65536dec  |
0830:13  | Limit 1  | Limit value "Limit 1" for the limit value monitoring.  | INT16  | RW  | 0  |
0830:14  | Limit 2  | Limit value "Limit 2" for the limit value monitoring.  | INT16  | RW  | 0  |
0830:15  | Filter settings  | Select the type of digital filter.  | INT16  | RW  | 2 ("IIR1")  |
0830:17  | User calibration offset  | Offset value for the user calibration.  | INT16  | RW  | 0  |
0830:18  | User calibration gain  | Gain value for the user calibration.  | INT16  | RW  | 16384dec  |
Index 083D AI Advanced Settings Ch.4
083D:11  | Input Type  | Set the measuring range.  | UINT16  | RW  | 2 ("U ±10 V")  |
083D:12  | Scaler  | Select the nominal or technical measuring range.  | UINT16  | RW  | 0 ("Extended Range")  |
083D:17  | Low Range Error  | The Status bit "Error" is set if the measured value is smaller than this parameter.  | INT32  | RW  | 1048568dec
083D:18  | High Range Error  | The Status bit "Error" is set if the measured value is smaller than this parameter.  | INT32  | RW  | 32767dec  |
Index 0840 AI Settings Ch5
0840:01  | Enable user scale  | Enabling the user scaling.  | BOOL  | RW  | 0  |
0840:02  | Presentation  | Select the data format of the measured values.  | UINT3  | RW  | 0 ("Signed")  |
0840:06  | Enable filter  | Enabling the digital filter.  | BOOL  | RW  | 0  |
0840:07  | Enable limit 1  | Enabling the limit value monitoring for the limit value "Limit 1".  | BOOL  | RW  | 0  |
0840:08  | Enable limit 2  | Enabling the limit value monitoring for the limit value "Limit 2"  | BOOL  | RW  | 0  |
0840:0A  | Enable user calibration  | Enabling the user calibration.  | BOOL  | RW  | 0  |
0840:0B  | Enable vendor calibration  | Enabling the vendor calibration.  | BOOL  | RW  | 1  |
0840:0E  | Swap limit bits  | Invert comparison operation of the limit value monitoring.  | BOOL  | RW  | 0  |
0840:11  | User scale offset  | Offset value for the user scaling.  | INT16  | RW  | 0  |
0840:12  | User scale gain  | Gain value for the user scaling.  | INT32  | RW  | 65536dec  |
0840:13  | Limit 1  | Limit value "Limit 1" for the limit value monitoring.  | INT16  | RW  | 0  |
0840:14  | Limit 2  | Limit value "Limit 2" for the limit value monitoring.  | INT16  | RW  | 0  |
0840:15  | Filter settings  | Select the type of digital filter.  | INT16  | RW  | 2 ("IIR1")  |
0840:17  | User calibration offset  | Offset value for the user calibration.  | INT16  | RW  | 0  |
0840:18  | User calibration gain  | Gain value for the user calibration.  | INT16  | RW  | 16384dec  |
Index 084D AI Advanced Settings Ch.5
084D:11  | Input Type  | Set the measuring range.  | UINT16  | RW  | 2 ("U ±10 V")  |
084D:12  | Scaler  | Select the nominal or technical measuring range.  | UINT16  | RW  | 0 ("Extended Range")  |
084D:17  | Low Range Error  | The Status bit "Error" is set if the measured value is smaller than this parameter.  | INT32  | RW  | 1048568dec
084D:18  | High Range Error  | The Status bit "Error" is set if the measured value is smaller than this parameter.  | INT32  | RW  | 32767dec  |
Index 0850 AI Settings Ch6
0850:01  | Enable user scale  | Enabling the user scaling.  | BOOL  | RW  | 0  |
0850:02  | Presentation  | Select the data format of the measured values.  | UINT3  | RW  | 0 ("Signed")  |
0850:06  | Enable filter  | Enabling the digital filter.  | BOOL  | RW  | 0  |
0850:07  | Enable limit 1  | Enabling the limit value monitoring for the limit value "Limit 1".  | BOOL  | RW  | 0  |
0850:08  | Enable limit 2  | Enabling the limit value monitoring for the limit value "Limit 2"  | BOOL  | RW  | 0  |
0850:0A  | Enable user calibration  | Enabling the user calibration.  | BOOL  | RW  | 0  |
0850:0B  | Enable vendor calibration  | Enabling the vendor calibration.  | BOOL  | RW  | 1  |
0850:0E  | Swap limit bits  | Invert comparison operation of the limit value monitoring.  | BOOL  | RW  | 0  |
0850:11  | User scale offset  | Offset value for the user scaling.  | INT16  | RW  | 0  |
0850:12  | User scale gain  | Gain value for the user scaling.  | INT32  | RW  | 65536dec  |
0850:13  | Limit 1  | Limit value "Limit 1" for the limit value monitoring.  | INT16  | RW  | 0  |
0850:14  | Limit 2  | Limit value "Limit 2" for the limit value monitoring.  | INT16  | RW  | 0  |
0850:15  | Filter settings  | Select the type of digital filter.  | INT16  | RW  | 2 ("IIR1")  |
0850:17  | User calibration offset  | Offset value for the user calibration.  | INT16  | RW  | 0  |
0850:18  | User calibration gain  | Gain value for the user calibration.  | INT16  | RW  | 16384dec  |
Index 085D AI Advanced Settings Ch.6
085D:11  | Input Type  | Set the measuring range.  | UINT16  | RW  | 2 ("U ±10 V")  |
085D:12  | Scaler  | Select the nominal or technical measuring range.  | UINT16  | RW  | 0 ("Extended Range")  |
085D:17  | Low Range Error  | The Status bit "Error" is set if the measured value is smaller than this parameter.  | INT32  | RW  | 1048568dec
085D:18  | High Range Error  | The Status bit "Error" is set if the measured value is smaller than this parameter.  | INT32  | RW  | 32767dec  |
Index 0860 AI Settings Ch7
0860:01  | Enable user scale  | Enabling the user scaling.  | BOOL  | RW  | 0  |
0860:02  | Presentation  | Select the data format of the measured values.  | UINT3  | RW  | 0 ("Signed")  |
0860:06  | Enable filter  | Enabling the digital filter.  | BOOL  | RW  | 0  |
0860:07  | Enable limit 1  | Enabling the limit value monitoring for the limit value "Limit 1".  | BOOL  | RW  | 0  |
0860:08  | Enable limit 2  | Enabling the limit value monitoring for the limit value "Limit 2"  | BOOL  | RW  | 0  |
0860:0A  | Enable user calibration  | Enabling the user calibration.  | BOOL  | RW  | 0  |
0860:0B  | Enable vendor calibration  | Enabling the vendor calibration.  | BOOL  | RW  | 1  |
0860:0E  | Swap limit bits  | Invert comparison operation of the limit value monitoring.  | BOOL  | RW  | 0  |
0860:11  | User scale offset  | Offset value for the user scaling.  | INT16  | RW  | 0  |
0860:12  | User scale gain  | Gain value for the user scaling.  | INT32  | RW  | 65536dec  |
0860:13  | Limit 1  | Limit value "Limit 1" for the limit value monitoring.  | INT16  | RW  | 0  |
0860:14  | Limit 2  | Limit value "Limit 2" for the limit value monitoring.  | INT16  | RW  | 0  |
0860:15  | Filter settings  | Select the type of digital filter.  | INT16  | RW  | 2 ("IIR1")  |
0860:17  | User calibration offset  | Offset value for the user calibration.  | INT16  | RW  | 0  |
0860:18  | User calibration gain  | Gain value for the user calibration.  | INT16  | RW  | 16384dec  |
Index 086D AI Advanced Settings Ch.7
086D:11  | Input Type  | Set the measuring range.  | UINT16  | RW  | 2 ("U ±10 V")  |
086D:12  | Scaler  | Select the nominal or technical measuring range.  | UINT16  | RW  | 0 ("Extended Range")  |
086D:17  | Low Range Error  | The Status bit "Error" is set if the measured value is smaller than this parameter.  | INT32  | RW  | 1048568dec
086D:18  | High Range Error  | The Status bit "Error" is set if the measured value is smaller than this parameter.  | INT32  | RW  | 32767dec  |
Index 0870 AI Settings Ch8
0870:01  | Enable user scale  | Enabling the user scaling.  | BOOL  | RW  | 0  |
0870:02  | Presentation  | Select the data format of the measured values.  | UINT3  | RW  | 0 ("Signed")  |
0870:06  | Enable filter  | Enabling the digital filter.  | BOOL  | RW  | 0  |
0870:07  | Enable limit 1  | Enabling the limit value monitoring for the limit value "Limit 1".  | BOOL  | RW  | 0  |
0870:08  | Enable limit 2  | Enabling the limit value monitoring for the limit value "Limit 2"  | BOOL  | RW  | 0  |
0870:0A  | Enable user calibration  | Enabling the user calibration.  | BOOL  | RW  | 0  |
0870:0B  | Enable vendor calibration  | Enabling the vendor calibration.  | BOOL  | RW  | 1  |
0870:0E  | Swap limit bits  | Invert comparison operation of the limit value monitoring.  | BOOL  | RW  | 0  |
0870:11  | User scale offset  | Offset value for the user scaling.  | INT16  | RW  | 0  |
0870:12  | User scale gain  | Gain value for the user scaling.  | INT32  | RW  | 65536dec  |
0870:13  | Limit 1  | Limit value "Limit 1" for the limit value monitoring.  | INT16  | RW  | 0  |
0870:14  | Limit 2  | Limit value "Limit 2" for the limit value monitoring.  | INT16  | RW  | 0  |
0870:15  | Filter settings  | Select the type of digital filter.  | INT16  | RW  | 2 ("IIR1")  |
0870:17  | User calibration offset  | Offset value for the user calibration.  | INT16  | RW  | 0  |
0870:18  | User calibration gain  | Gain value for the user calibration.  | INT16  | RW  | 16384dec  |
Index 087D AI Advanced Settings Ch.8
087D:11  | Input Type  | Set the measuring range.  | UINT16  | RW  | 2 ("U ±10 V")  |
087D:12  | Scaler  | Select the nominal or technical measuring range.  | UINT16  | RW  | 0 ("Extended Range")  |
087D:17  | Low Range Error  | The Status bit "Error" is set if the measured value is smaller than this parameter.  | INT32  | RW  | 1048568dec
087D:18  | High Range Error  | The Status bit "Error" is set if the measured value is smaller than this parameter.  | INT32  | RW  | 32767dec  |
Index 0A00 ADC raw value
0A00:01  | ADC raw value  | ADC raw value of channel 1.  | INT16  | RO  | 0  |
Index 0A10 ADC raw value
0A10:01  | ADC raw value  | ADC raw value of channel 2.  | INT16  | RO  | 0  |
Index 0A30 ADC raw value
0A20:01  | ADC raw value  | ADC raw value of channel 3.  | INT16  | RO  | 0  |
0A30:01  | ADC raw value  | ADC raw value of channel 4.  | INT16  | RO  | 0  |
Index 0A40 ADC raw value
0A40:01  | ADC raw value  | ADC raw value of channel 5.  | INT16  | RO  | 0  |
Index 0A50 ADC raw value
0A50:01  | ADC raw value  | ADC raw value of channel 6.  | INT16  | RO  | 0  |
Index 0A60 ADC raw value
0A60:01  | ADC raw value  | ADC raw value of channel 7.  | INT16  | RO  | 0  |
Index 0A70 ADC raw value
0A70:01  | ADC raw value  | ADC raw value of channel 8.  | INT16  | RO  | 0  |
Index 0AFA Diagnose
0AFA:01  | Overtemperature  | Overheating of the IO-Link module  | BOOL  | RO  | -  |
0AFA:02  | Short detected  | Short circuit on the IO-Link C/Q data line.  | BOOL  | RO  | -  |
0AFA:03  | L+ low  | The supply voltage L+ is too low (L+ < 18 V).  | BOOL  | RO  | -  |
0AFA:04  | 2L+ low 1)  | The supply voltage P24 is too low (P24 < 18 V).  | BOOL  | RO  | -  |
0AFA:05  | 2L+ stat 1)  | The supply voltage P24 is not available (P24 < 8 V).  | BOOL  | RO  | -  |
0AFA:06  | reserved  | -  | BOOL  | RO  | -  |
0AFA:07  | reserved  | -  | BOOL  | RO  | -  |
0AFA:08  | reserved  | -  | BOOL  | RO  | -  |
0AFA:09  | reserved  | -  | BOOL  | RO  | -  |
0AFA:0A  | reserved  | -  | BOOL  | RO  | -  |
0AFA:0B  | reserved  | -  | BOOL  | RO  | -  |
0AFA:0C  | reserved  | -  | BOOL  | RO  | -  |
0AFA:0D  | reserved  | -  | BOOL  | RO  | -  |
0AFA:0E  | reserved  | -  | BOOL  | RO  | -  |
0AFA:0F  | reserved  | -  | BOOL  | RO  | -  |
0AFA:10  | reserved  | -  | BOOL  | RO  | -  |
1) "2L+" was the original designation for "P24" in the IO-Link specification.