Configuration data
Index 8000 ENC Settings 0 Ch.1
Index (hex)  | Name  | Meaning  | Data type  | Flags  | Default  |
8000:0  | ENC Settings 0 Ch.1  | Maximum subindex  | UINT8  | RO  | 0x23 (35dec)  |
8000:01  | The counter is reset via the C input.  | BOOLEAN  | RW  | 0x00 (0dec)  | |
8000:02  | Enable extern reset  | A counter reset is triggered via the external latch input (24 V)  | BOOLEAN  | RW  | 0x00 (0dec)  |
8000:04  | 0: Disable gate  | BIT2  | RW  | 0x01 (1dec)  | |
8000:06  | 0: 4-fold (quadruple evaluation)  | BIT2  | RW  | 0x00 (0dec)  | |
8000:08  | 0: Enables input filter (inputs A, /A, B, /B, C, /C only) If a filter is enabled, a signal edge must be present for at least 2.4 µs in order to be counted as an increment.  | BOOLEAN  | RW  | 0x01 (1dec)  | |
8000:0A  | When enabled, the terminal interpolates microincrements between the integer encoder increments in DC mode.  | BOOLEAN  | RW  | 0x00 (0dec)  | |
8000:0B  | Error detection A  | A wire break or short circuit on track A is indicated in index 0x6000:07 and as process data. Diagnostics is only possible, if the associated input is wired differentially.  | BOOLEAN  | RW  | 0x01 (1dec)  |
8000:0C  | Error detection B  | A wire break or short circuit on track B is indicated in index 0x6000:07 and as process data. Diagnostics is only possible, if the associated input is wired differentially.  | BOOLEAN  | RW  | 0x01 (1dec)  |
8000:0D  | Error detection C  | A wire break or short circuit on track C is indicated in index 0x6000:07 and as process data. Diagnostics is only possible, if the associated input is wired differentially.  | BOOLEAN  | RW  | 0x00 (0dec)  |
8000:0E  | Activates reversion of rotation  | BOOLEAN  | RW  | 0x00 (0dec)  | |
8000:10  | Extern reset polarity  | 0: Fall (with the falling edge the counter is set to zero)  | BIT1  | RW  | 0x01 (1dec)  |
8000:11  | This is the minimum time over which the frequency is determined; The frequency is calculated from the number of increments (changes of position value) in the “frequency window” time interval. The determined frequency is output in index 0x6000:13 and as process data. The frequency calculation is carried out locally without distributed clocks function.  | UINT16  | RW  | 0x2710 (10000dec)  | |
8000:13  | Scaling of the frequency measurement (must be divided by this value to obtain the unit in Hz): 100: "0.01 Hz" (default)  | UINT32  | RW  | 0x00000064 (100dec)  | |
8000:14  | Period scaling  | Resolution of the period value in the process data: 10: "10 ns" Period duration value is multiple of 10 ns   | UINT32  | RW  | 0x0000000A (10dec)  |
8000:17  | Waiting time [ms] for frequency measurement If no full period is detected within the Frequency window, another frequency window is started to record a full period. This happens until the maximum frequency wait time has elapsed. At least double the period value of the minimum frequency to be measured should be entered here. t >= 2* (1 / fmin)  | UINT16  | RW  | 0x53E2 (21474dec)  | |
8000:1D  | Frequency numerator,  | UINT32  | RW  | 0x00000001 (1dec)  | |
8000:1E  | Frequency denominator,  | UINT32  | RW  | 0x00000001 (1dec)  | |
8000:21  | Activation of plausibility check  | BOOLEAN  | RW  | 0x00 (0dec)  | |
8000:22  | FALSE: TRUE:  | BOOLEAN  | RW  | 0x00 (0dec)  | |
8000:23  | FALSE: TRUE:  | BOOLEAN  | RW  | 0x00 (0dec)  |
Index 8001 ENC Settings 1 Ch.1
8001:0  | ENC Settings 1 Ch.1  | Maximum subindex  | UINT8  | RO  | 0x23 (35dec)  |
8001:17  | Setting the encoder supply 50dec: 5.0 V (default) Refer to the Note on setting the encoder supply  | UINT32  | RW  | 0x00000032 (50dec)  | |
8001:19  | Filter settings: 10dec: 10 kHz  | UINT32  | RW  | 0x00001388 (5000dec)  | |
8001:1A  | Specifies the value for the upper counter limit.  | UINT32  | RW  | 0xFFFFFFFF (-1dec)  | |
8001:1B  | Specifies the value for the lower counter limit.  | UINT32  | RW  | 0x00000000 (0dec)  | |
8001:1C  | Enter the hysteresis in number of increments. A value greater than 0 must be selected. If the counter value exceeds the value, the bit in index 0x60n2:13 "Direction inversion detected" is set in the next PLC cycle.  | UINT8  | RW  | 0x0A (10dec)  | |
8001:1D  | 0: Encoder RS422 (diff. Input)  | UINT32  | RW  | 0x00000000 (0dec)  | |
8001:1E  | Input of the switching characteristics for output 1 0: TRUE=Push, FALSE=Pull  | UINT8  | RW  | 0x00 (0dec)  | |
8001:1F  | Input of the switching characteristics for output 2 0: TRUE=Push, FALSE=Pull  | UINT8  | RW  | 0x00 (0dec)  | |
8001:20  | Input of the reference value for the switching value of output 1: 0: Counter value  | UINT8  | RW  | 0x00 (0dec)  | |
8001:21  | Input of the reference value for the switching value of output 2: 0: Counter value  | UINT8  | RW  | 0x00 (0dec)  | |
8001:22  | Setting the response time for short‑circuit/overload diagnostics at output 1 0: Disable  | UINT8  | RW  | 0x02 (2dec)  | |
8001:23  | Setting the response time for short‑circuit/overload diagnostics at output 2 0: Disable  | UINT8  | RW  | 0x02 (2dec)  |
Index 80n0 DIG Safe State Active Ch.n
(n = 2 for Ch.1; n = 3 for Ch.2)
80n0:0  | DIG Safe State Active Ch.n  | Maximum subindex  | UINT8  | RO  | 0x01 (1dec)  |
80n0:01  | Active  | Enabling of the output state defined in index 0x80n1:01 in case of a bus error 0: Output keeps the current state. 1: Output is switched to the state defined in index 0x80n1.  | BOOLEAN  | RW  | 0x01 (1dec)  |
Index 80n1 DIG Safe State Value Ch.n
80n1:0  | DIG Safe State Value Ch.n  | Maximum subindex  | UINT8  | RO  | 0x01 (1dec)  |
80n1:01  | Value  | Defines the state of the output in case of a bus error: 0: Output off  | BOOLEAN  | RW  | 0x00 (0dec)  |