FB_BA_AC_ColT_01
FB_BA_AC_ColT_01 1:
The template represents the open-loop and closed-loop control of a cold water air cooler without dehumidification control.
The main tasks of the template are:
Principle diagram 01
The diagram shows the intended use of the template with the plant elements involved.
FB_BA_AC_ColT_01 2:
Principle diagram 02
The diagram shows the integration of the template within a plant.
FB_BA_AC_ColT_01 3:
FB_BA_AC_ColT_01 4:
The initialization of the template takes place within the method FB_Init.
Block diagram
FB_BA_AC_ColT_01 5:
FUNCTION_BLOCK FB_BA_AC_ColT_01 EXTENDS FB_BA_View
  fSpTSuA           : REAL;
  fTSuA             : REAL;
  bSyncTSuACtrl     : BOOL;
  fSyncTSuACtrl     : REAL;
  bCmd              : BOOL;
  fPresentValue     : REAL;
  bActiveSeqCtrl    : BOOL;
  stTSeqLink        : ST_BA_SeqLink;
  stAggregate       : ST_BA_Aggregate;
VAR_INPUT CONSTANT PERSISTENT
  {attribute 'parameterCategory' := 'Behaviour'}
  fHysPuOn          : REAL := 5.0;
  fHysPuOff         : REAL := 1.0;
VAR_INPUT CONSTANT
  TFl               : FB_BA_SensorAnalog;
  TRt               : FB_BA_SensorAnalog;
  TSuACtrl          : FB_BA_AC_ColTSuACtrl;
  Vlv               : FB_BA_Vlv;
  Pu                : FB_BA_Pu1st;
  PlantLock         : FB_BA_PlantLock;
  Aggregate         : FB_BA_Aggregate;
  bPrioSfty         : BOOL;
  bPrioCrit         : BOOL;
  PrioSwiVal        : FB_BA_PrioSwi_B04;
  HysPu             : FB_BA_Swi2P;
FB_BA_AC_ColT_01 6: Inputs
Type
fSpTSuA
REAL
Setpoint of the supply air temperature.
fTSuA
REAL
Measured value of the supply air temperature.
bSyncTSuACtrl
Input for synchronization of the supply air sequence controller in the TSuACtrl function block.
fSyncTSuACtrl
REAL
Synchronization value for the supply air sequence controller in the TSuACtrl function block.
FB_BA_AC_ColT_01 7: Outputs
Type
bCmd
Current switching status of the single-stage pump.
fPresentValue
REAL
Current value of the cooler valve.
bActiveSeqCtrl
Indicates that the sequence controller of the cooler is the active one in the sequence control.
FB_BA_AC_ColT_01 8: Inputs/outputs
Type
stSeqLink
ST_BA_SeqLink
The data and command structure is the link between the supply air temperature sequence controller Ctrl and the supply air temperature sequence controller TSeqLink of an air conditioning system.
stAggregate
ST_BA_Aggregate
Bidirectional aggregate structure via which the enables and switching values are transmitted to the evaluation function block of the step sequence control Aggregate. The aggregate structure transmits the recorded feedback signals up and down to the central plant control.
FB_BA_AC_ColT_01 9: Inputs CONSTANT PERSISTENT
Type
fHysPuOn
REAL
Upper switching point of the hysteresis to switch on the pump.
fHysPuOff
REAL
Lower switching point of the hysteresis to switch off the pump.
FB_BA_AC_ColT_01 10: Inputs CONSTANT
Type
TFl
FB_BA_SensorAnalog
The function block represents the flow temperature sensor.
TRt
FB_BA_SensorAnalog
The function block represents the return temperature sensor.
TSuACtrl
The function block represents the supply air temperature control of the cooler and is part of the temperature sequence control of an air conditioning system.
The control signal is forwarded to the valve Vlv.
Vlv
FB_BA_Vlv
The function block represents the valve.
Pu
FB_BA_Pu1st
The function block represents the cooler pump.
PlantLock
FB_BA_PlantLock
When the function block is called, the relevant faults of the event-enabled objects are collected and output at this and lower levels of the template.
These relevant faults cause specific switching actions via the variables bPrioSfty and bPrioCrit in the template.
The parameterization of the lock priority of the event-enabled objects can be found in the FB_init of this template.
Aggregates
FB_BA_Aggregate
The aggregate function block represents a receive block of a step sequence controller.
Within the function block, the aggregate structure stAggregate is evaluated and integrated into the template using the inputs and outputs.
Variables
Type
bPrioSfty
The variable is an evaluation of the "Safety" lock priority of the event-enabled objects in the project structure and causes targeted switching actions in the template when a relevant fault is triggered.
bPrioCrit
The variable is an evaluation of the "Critical" lock priority of the event-enabled objects in the project structure and causes targeted switching actions in the template when a relevant fault is triggered.
PrioSwiVal
FB_BA_PrioSwi_B04
The priority switch PrioSwiVal determines the switching conditions and enables for the supply air temperature control TSuACtrl using the aggregate function block Aggregate and the global variable list Priority.
HysPu
FB_BA_Swi2P
The two-position switch HysPu switches the pump Pu on and off depending on the valve position fPresentValue and the switching points of the hysteresis fHysPuOn/fHysPuOff.