Register description R0 - R31
R0: Actual position (low-order word)
Contains the low-order word of the actual position.
If the latch function is enabled (RP0.R52.2 = 1bin), this register must be read first. In doing so, registers R0 and R1 are cached. Both registers are enabled again during subsequent read of register R1.
R1: Actual position (high-order word)
Contains the high-order word of the actual position.
R2: Setting of the target position or position (low-order word)
Here you can specify the low-order word for the required position (maximum: 65535).
R3: Setting of the target position or position (high-order word)
Here you can specify the high-order word for the required position (maximum: 65535).
R4: Register page selection register
This register is used for specifying which register page is shown in registers R32 to R63 of the KL2531/KL2541:
- 0x0000: Register page 0 - further terminal parameters (default)
- 0x0001: Register page 1 - current values of the user current table
- 0x0002: Register page 2 - user position table
R5: Latch value (high-order word)
Contains the high-order word of the latch value.
The low-order word of the latch value can only be read in process data mode by setting CW.5.
R6: Temperature register
The internal temperature of the terminal can be read, in °C, through register R6. The terminal sets bit SB.5 as a warning if the temperature exceeds the threshold of 80 °C. SB5 is automatically reset when the temperatures drops below 60 °C.
R7: Command register
Standard commands
To execute a standard command, the user code word 0x1235 must be entered in register R31.
Command 0x7000: Restore Factory Settings | |
Register page 0 (further parameters):
R50: 2047 |
Register page 1 (current table): Register page 2 (position table): Register page 3 (velocity and acceleration table): |
| Command 0x8000: Software Reset |
WARNINGDuring a software reset, the motor is switched current-free, i.e. the rotor axis can rotate freely. Ensure that your system state permits this and that hazards for persons or machinery have been ruled out!
Special commands
To execute a special command, no code word must be entered in register R31.
| Command 0x0500: start multiple motion command 'forward' |
Command 0x0510: start multiple motion command 'backward' |
Command 0x0520: start referencing |
| Command 0x0530: start self-adjustment |
Command 0x0540: stopping or resetting special functions |
R8: Terminal type
The terminal identifier is contained in register R8:
KL2531: 0x09E3 (2531dec)
KL2541: 0x09ED (2541dec)
R9: Firmware version
Register R9 contains the ASCII coding of the terminal's firmware version, e.g. 0x3141 = '1A'. The '0x31' corresponds here to the ASCII character '1', while the '0x41' represents the ASCII character 'A'.
This value cannot be changed.
R16: Hardware version number
Register R16 contains the hardware version of the terminal.
R31: Code word register
- If you write values into the user registers without first entering the user code word (0x1235) into the code word register, the terminal will not accept the supplied data.
- If you write values into the user registers and have previously entered the user code word (0x1235) in the code word register, these values are written into the RAM registers and in the EEPROM registers and are therefore retained if the terminal is restarted.
- Registers R37, R38, R39, R40, R47, R48, R49, R50 and R58 can be written without user code. The new values are only stored in the RAM.
The code word is reset if the terminal is restarted.