ELM350x - Technical data
Technical data
ELM3502-00x0
ELM3504-00x0
Analog inputs
2-channel (differential)
4-channel (differential)
Time relation between channels
Simultaneous conversion of all channels in the terminal, synchronous conversion between terminals, if Distributed clocks is used
ADC conversion method
ΔΣ (delta-sigma) with internal sampling rate
8 Msps
5.12 Msps
Input filter cut-off frequency hardware
see explanations within chapter
ELM features/firmware filter concept)
Before AD converter:
hardware low-pass -3 dB @ 30 kHz
Type Butterworth 3rd order
Within ADC after conversion:
Low-pass filter
-3 dB @ 5.3 kHz, rise time 150 µs
Low-pass filter
-3 dB @ 2.6 kHz, rise time 300 µs
Type sinc3/average filter
The rise time/settling time/delay caused by the filtering will be considered within the distributed clocks timestamp.
Resolution
24 bit (including sign)
Connection technology
2/3/4/5/6-wire
Sampling rate (per channel, simultaneous)
50 µs/20 ksps
100 µs/10 ksps
Free down sampling by firmware via decimation factor
Oversampling
1…100 can be selected
Supported EtherCAT cycle time
(dependent on operation mode)
Distributed clocks: min. 100 µs, max. 10 ms
FrameTriggered/Synchronous: min. 200 µs, max. 100 ms
FreeRun: not yet supported
Connection diagnosis
Wire break/short circuit
Internal analog ground AGND
Existing by external connection to -Uv
Overvoltage protection of the inputs related to -Uv (internal ground)
Value to follow
Internal power supply
Via E-bus
Current consumption E-bus
typ. 450 mA
typ. 720 mA *)
Current consumption via power contacts
Thermal power loss
typ. 3 W
Dielectric strength – destruction limit
max. permitted short-term/continuous voltage between the contact points ±I1, ±I2, +Uv, and -Uv: unsupplied ±40 V, supplied ±36 V
Note: -Uv corresponds to the internal AGND
Recommended operating voltage range for compliance with specification **)
- maximum permissible differential voltage during normal operation between +I1/-I1 and +I2/-I2: see the respective nominal measuring range (see Figure **: U1 + U2)
- maximum allowable differential voltage during normal operation at +I1 or -I1 relative to -Uv: typically ±10 V (see Figure **: Ucm + U1 or Ucm – U2)
Note: Ucm must not exceed this value
- max. permitted voltage during specified normal operation at +I2 relative to -Uv: 1 …5 V (see figure **: Ucm + U1)
- maximum allowable voltage during normal operation at -I2 relative to -Uv: typically 0 V (see Figure **: Ucm – U2, to be understood as single-ended)
- Note: -Uv corresponds to the internal AGND
- Note: U1 = U2 for the purposes of these explanations
*) 650 mA when operated with 4 x 350 Ω quarter bridges or 1000 Ω at 5 V
**) Explanations of potential:
ELM350x - Technical data 1:
Common data
ELM3502-00x0
ELM3504-00x0
Distributed Clocks
Yes, with Oversampling n = 1…100, accuracy << 1 μs
Special features
Extended Range 107 %, freely configurable numeric filters, TrueRMS, integrator/differentiator, non-linear scaling, PeakHold
Functional diagnosis 1)
Yes
Electrical isolation channel/channel 2)
no
Electrical isolation channel/E-Bus 2)
Functional insulation, 707 V DC (type test)
Electrical isolation channel/SGND 2)
Configuration
via the EtherCAT Master, e.g. TwinCAT
Note to cable length
Signal cable lengths to the sensor / encoder over 3 m must be shielded, the shield design must be in line with the state of the art and be effective. For larger cable lengths > 30 m, a suitable surge protection should be provided if appropriate interference could affect the signal cable.
1) see chapters Self-test and self-test report and Connection test/switchable connection diagnosis
2) see notes to potential groups within chapter Power supply, potential groups
Basic mechanical properties
ELM3502-00x0
ELM3504-00x0
Connection type
6-pin. PushIn spring-loaded technology, service plug
Dimensions (W x H x D)
See chapter Housing
Mounting
on 35 mm rail conforms to EN 60715
Note Mounting
Plug partly not within scope of delivery, see chapter
Notes on connection technology
Weight
Approx. 350 g
Permissible ambient temperature range during operation
-25…+60 °C
0…+55 °C
Permissible ambient temperature range during storage
-40…+85 °C
-25…+85 °C
Environmental data
ELM3502-00x0
ELM3504-00x0
Permissible operating altitude range
0 up to 2000 m (derating at higher altitudes on request)
Relative humidity
max. 95%, no condensation
Protection class
IP 20
Installation position
Variable
Normative data
ELM3502-00x0
ELM3504-00x0
Vibration-/shock resistance
Conforms to EN 60068-2-6 / EN 60068-2-27
EMC-resistance / emission
Conforms to EN 61000-6-2 / EN 61000-6-4
Approvals/ markings *)
CE, UKCA, cULus_60, EAC
CE, UKCA, cULus_55, EAC
EMC notes
In case of the "PushIn" connector, ESD air discharges conforming to EN 61000-6-4 into the connectors or to the lines connected there can lead to measurement deviations up to ±FSV within the respective channel or to other channels by crosstalk.
Peak voltages (surge) conforming to EN 61000-6-2 that are applied to the cable shield can lead to measurement deviations up to ±FSV.