MP_SR_actuator_Process
This function block is suitable for SR actuators. For more information please visit www.belimo.com.
MP_Address is used to specify the MP-Bus device with which the function block is to communicate. bStart activates communication with the MP-Bus device. bBusy indicates that the function block is active. If bStart remains TRUE, the device is addressed cyclically with a period specified by the time in TMPolling. The time should be set longer than 1 second. bError is used to indicate an error in communication with the actuator. The type of the error can be read with iErrorId.
![]() | Restrictions This function is called only if the corresponding “Configuration” function block is not executed. |
MP_Address : USINT := 1;
bStart : BOOL;
strDataKL6771 : DataKL6771;
TMpolling : TIME := t#10s;
rSetpointRel_Write : LREAL;
nOverrideControl_Write : E_MP_SR_OverrideControl;
MP_Address | USINT | MP-Bus address of the slave. |
bStart | BOOL | A positive edge starts the function block. If this remains continuously TRUE, the function block will be activated cyclically with a period specified by the time in TMPolling. |
strDataKL6771 | The data structure with which the KL6771() function block must be linked. | |
TMpolling | TIME | The time for which the function block should address the actuator. Default 10 s, minimum time 1 s. |
rSetpointRel_Write | LREAL | Setpoint in % (0…100). |
nOverrideControl_Write | Override the setpoint with defined values. |
Outputs
iErrorId : MP_Error;
strMP_Serial_Number : MP_Serial_Number;
rSetpointRel : LREAL;
rPositionRel : LREAL;
rPositionAbs : LREAL;
nOverrideControl : E_MP_SR_OverrideControl;
bBusy | BOOL | This bit is set for as long as the function block is active. |
bError | BOOL | This output goes TRUE as soon as an error occurs. This error is described via the iErrorId variable. |
iErrorId | This output outputs an error code in the event of an error. bError goes TRUE at the same time. | |
strMP_Serial_Number | Structure for the serial number. | |
rSetpointRel | LREAL | Setpoint in % (0…100). |
rPositionRel | LREAL | Relative position with respect to the nominal range, in % (0…100). |
rPositionAbs | LREAL | Absolute position refers to the actual position within the mechanical range. Rotation in ° (0…95) or linear in mm (0…600). |
nOverrideControl | Setpoint override. |
Development environment | PLC library to include |
TwinCAT from v3.1.4024.77 | Tc2_MPBus from 3.8.1.0 |