MP_EPIV_R6_V4_Process
MP_EPIV_R6_V4_Process 1:
This function block is suitable for 6-way EPIV V4 DN 15…25 EP..R6 + BAC-HHx. For more information please visit www.belimo.com.
MP_Address is used to specify the MP-Bus device with which the function block is to communicate. bStart activates communication with the MP-Bus device. bBusy indicates that the function block is active. If bStart remains TRUE, the device is addressed cyclically with a period specified by the time in TMPolling. The time should be set longer than 1 second. bError is used to indicate an error in communication with the actuator. The type of the error can be read with iErrorId.
MP_EPIV_R6_V4_Process 2: Inputs
  MP_Address          : USINT := 1;
  bStart              : BOOL;
  strDataKL6771       : DataKL6771;
  TMpolling           : TIME := t#10s;
  rSetpoint           : LREAL;
  nCommand            : E_MP_EV_V4_Command;
  nOverrideControl    : E_MPBus_Override_6wayMPIV_V4;
  rSetpointSeq1_Write : LREAL;
  rSetpointSeq2_Write : LREAL;
  nDataRead           : WORD := 16#FFFF;
Type
MP_Address
USINT
MP-Bus address of the slave.
bStart
A positive edge starts the function block. If this remains continuously TRUE, the function block will be activated cyclically with a period specified by the time in TMPolling.
strDataKL6771
DataKL6771
The data structure with which the KL6771() function block must be linked.
TMpolling
TIME
The time for which the function block should address the actuator. Default 10 s, minimum time 1 s.
rSetpoint
LREAL
Setpoint in % (0...100).
nCommand
E_MP_EV_V4_Command
Command for service and test functions of the actuator.
nOverrideControl
Override the setpoint with defined values.
rSetpointSeq1_Write
LREAL
Setpoint for Sequence 1 in % (0…100).
rSetpointSeq2_Write
LREAL
Setpoint for Sequence 2 in % (0…100).
nDataRead
WORD
0xFFFF - Read all data
Bit 0 – Read relative position
Bit 1 – Read absolute position
Bit 2 – Read value sensor 1
Bit 3 – Read analog setpoint
Bit 4 – Read relative flow rate
Bit 5 – Read absolute flow rate
Bit 6 – Read glycol concentration
Bit 7 – Read Temperature1 remote
Bit 8 – Read Temperature2 integrated
Bit 9 – Read temperature delta
Bit 10 – Read relative power
Bit 11 – Read absolute cooling power
Bit 12 – Read absolute heating power
Bit 13 - Total volume
Bit 14 – Read cooling energy
Bit 15 – Read heating energy
MP_EPIV_R6_V4_Process 3: Outputs
  bBusy                            : BOOL;
  bError                           : BOOL;
  iErrorId                         : MP_Error;
  nOverrideControl_Read            : E_MPBus_Override_6wayMPIV;
  rSetpoint_Read                   : LREAL;
  rRelativePos_Read                : LREAL;
  rAbsolutePos_Read                : LREAL;
  rRelativeFlow_Read               : LREAL;
  bErrorStateFlowSensorErr         : BOOL;
  bErrorStateActuator_can_not_move : BOOL;
  st_StateEV                       : st_StateEV;
  rAbsoluteFlow_UnitSel            : LREAL;
Type
bBusy
This bit is set for as long as the function block is active.
This output goes TRUE as soon as an error occurs. This error is described via the iErrorId variable.
iErrorId
MP_ERROR
This output outputs an error code in the event of an error. bError goes TRUE at the same time.
strMP_Serial_Number
MP_Serial_Number
Structure for the serial number.
rSetpoint_Read
LREAL
Setpoint in % (0…100).
rRelativePosition
LREAL
Relative position in % (0…100).
rAbsolutePosition
LREAL
Absolute position in ° (0…96).
Override mode.
nSensor1Value
DINT
Sensor 1 value in mV/ohm (0…65535). A value of -1 means that the data is disabled.
rSetpointAnalog
LREAL
Analog setpoint in % (0…100). A value of -1 means that the data is disabled.
rRelativeVolumetricFlow
LREAL
Relative volume flow rate in % (0…100). A value of -1 means that the data is disabled.
rAbsoluteVolumetricFlow
LREAL
Absolute volume flow rate in l/s (0…100). A value of -1 means that the data is disabled.
rAbsoluteVolumetricFlowSelUnit
LREAL
Absolute volumetric flow in selected unit.
rGlycolConcentration
LREAL
Glycol concentration in % (0…100). A value of -1 means that the data is disabled.
rTemperature
LREAL
Temperature1 in °C (-20…+150). A value of -273 means that the data is disabled.
rSetpointSeq1
LREAL
rSetpointSeq2
LREAL
rAccumulatedVolume
LREAL
Total volume in m³ (0…214748.36).
st_ErrorState
ST_MP_EPIV_HealthState
Device status.
nCondensationProtectionStatus
E_MP_CondensationProtectStatus
Condensation protection status.
rRelativeHumidity
LREAL
Relative humidity in % (0–100) for EP0..R6+BAC+HHM and in V for EP0..R6+BAC.
Development environment
PLC library to include
TwinCAT from v3.1.4024.77
Tc2_MPBus from 3.8.1.0