MP_EPIV_R6_V4_Process
This function block is suitable for 6-way EPIV V4 DN 15…25 EP..R6 + BAC-HHx. For more information please visit www.belimo.com.
MP_Address is used to specify the MP-Bus device with which the function block is to communicate. bStart activates communication with the MP-Bus device. bBusy indicates that the function block is active. If bStart remains TRUE, the device is addressed cyclically with a period specified by the time in TMPolling. The time should be set longer than 1 second. bError is used to indicate an error in communication with the actuator. The type of the error can be read with iErrorId.
MP_Address : USINT := 1;
bStart : BOOL;
strDataKL6771 : DataKL6771;
TMpolling : TIME := t#10s;
rSetpoint : LREAL;
nCommand : E_MP_EV_V4_Command;
nOverrideControl : E_MPBus_Override_6wayMPIV_V4;
rSetpointSeq1_Write : LREAL;
rSetpointSeq2_Write : LREAL;
nDataRead : WORD := 16#FFFF;
MP_Address | USINT | MP-Bus address of the slave. |
bStart | BOOL | A positive edge starts the function block. If this remains continuously TRUE, the function block will be activated cyclically with a period specified by the time in TMPolling. |
strDataKL6771 | The data structure with which the KL6771() function block must be linked. | |
TMpolling | TIME | The time for which the function block should address the actuator. Default 10 s, minimum time 1 s. |
rSetpoint | LREAL | Setpoint in % (0...100). |
nCommand | Command for service and test functions of the actuator. | |
nOverrideControl | Override the setpoint with defined values. | |
rSetpointSeq1_Write | LREAL | Setpoint for Sequence 1 in % (0…100). |
rSetpointSeq2_Write | LREAL | Setpoint for Sequence 2 in % (0…100). |
nDataRead | WORD | 0xFFFF - Read all data |
Outputs
iErrorId : MP_Error;
nOverrideControl_Read : E_MPBus_Override_6wayMPIV;
rSetpoint_Read : LREAL;
rRelativePos_Read : LREAL;
rAbsolutePos_Read : LREAL;
rRelativeFlow_Read : LREAL;
bErrorStateFlowSensorErr : BOOL;
bErrorStateActuator_can_not_move : BOOL;
st_StateEV : st_StateEV;
rAbsoluteFlow_UnitSel : LREAL;
bBusy | BOOL | This bit is set for as long as the function block is active. |
bError | BOOL | This output goes TRUE as soon as an error occurs. This error is described via the iErrorId variable. |
iErrorId | This output outputs an error code in the event of an error. bError goes TRUE at the same time. | |
strMP_Serial_Number | Structure for the serial number. | |
rSetpoint_Read | LREAL | Setpoint in % (0…100). |
rRelativePosition | LREAL | Relative position in % (0…100). |
rAbsolutePosition | LREAL | Absolute position in ° (0…96). |
nOverrideControl_Read | Override mode. | |
nSensor1Value | DINT | Sensor 1 value in mV/ohm (0…65535). A value of -1 means that the data is disabled. |
rSetpointAnalog | LREAL | Analog setpoint in % (0…100). A value of -1 means that the data is disabled. |
rRelativeVolumetricFlow | LREAL | Relative volume flow rate in % (0…100). A value of -1 means that the data is disabled. |
rAbsoluteVolumetricFlow | LREAL | Absolute volume flow rate in l/s (0…100). A value of -1 means that the data is disabled. |
rAbsoluteVolumetricFlowSelUnit | LREAL | Absolute volumetric flow in selected unit. |
rGlycolConcentration | LREAL | Glycol concentration in % (0…100). A value of -1 means that the data is disabled. |
rTemperature | LREAL | Temperature1 in °C (-20…+150). A value of -273 means that the data is disabled. |
rSetpointSeq1 | LREAL | Setpoint for Sequence 1 in % (0…100). |
rSetpointSeq2 | LREAL | Setpoint for Sequence 2 in % (0…100). |
rAccumulatedVolume | LREAL | Total volume in m³ (0…214748.36). |
st_ErrorState | Device status. | |
nCondensationProtectionStatus | Condensation protection status. | |
rRelativeHumidity | LREAL | Relative humidity in % (0–100) for EP0..R6+BAC+HHM and in V for EP0..R6+BAC. |
Development environment | PLC library to include |
TwinCAT from v3.1.4024.77 | Tc2_MPBus from 3.8.1.0 |