MP_EnergyValveV4_Configuration
This function block is used to configure the Energy Valve actuators EV..R2+.. with firmware 4.0.0 or higher. For more information please visit www.belimo.com.
MP_Address is used to specify the MP-Bus device with which the function block is to communicate. bStart activates communication with the MP-Bus device. bBusy indicates that the function block is active. bError is used to indicate an error in communication with the actuator. The type of the error can be read with iErrorId.
MP_Address : USINT := 1;
bStart : BOOL;
bRead_Write : BOOL;
strDataKL6771 : DataKL6771;
rVmax_Write : LREAL := 100;
rVmin_Write : LREAL;
bSetpointSource_Write : BOOL := TRUE;
nSensor1Type_Write : E_MP_EV_V4_Sensor1Type;
nControlMode_Write : E_MP_EV_V4_ControlMode := 1;
rBusFailPosition_Write : LREAL;
nCommunicationWatchdog_Write : UINT;
rPmax_Write : LREAL := 100;
nDeltaTLimitation_Write : E_MP_EV_V4_DeltaTLimitation;
rSetpointDeltaT_Write : LREAL := 1.0;
rSetpointAbsFlowDeltaT_Write : LREAL;
bSelectMeterRegister_Write : BOOL;
MP_Address | USINT | MP-Bus address of the slave. |
bStart | BOOL | A positive edge starts the function block. |
bRead_Write | BOOL | If FALSE then READ only; if TRUE then READ and WRITE. |
strDataKL6771 | The data structure with which the KL6771() function block must be linked. | |
rVmax_Write | LREAL | Max. setpoint in % (25...100). Standard 100 %. Refers to Vnom and is taken into account when control mode = flow control. |
rVmin_Write | LREAL | Min. setpoint in % (0...Vmax). Vmin must be smaller than Vmax. |
bSetpointSource_Write | BOOL | TRUE = bus; FALSE = analog. |
nSensor1Type_Write | Sensor 1 Type | |
nControlMode_Write | Control mode | |
rBusFailPosition_Write | LREAL | Not functional. |
nCommunicationWatchdog_Write | UINT | Communication monitoring in s (0...3600). Not functional (reserved for future extensions). |
rPmax_Write | LREAL | Max. setpoint in % (5...100). Standard 100 %. Refers to Pnom and is taken into account if control mode = power control. |
nDeltaTLimitation_Write | Determines whether the device responds to a low delta T. | |
rSetpointDeltaT_Write | LREAL | Setpoint Delta T in K (0...60). Standard 1.0K. Is taken into account if the delta T limitation is active (not disabled). |
rSetpointAbsFlowDeltaT_Write | LREAL | Setpoint Abs flow Delta T in l/s (0...100,000). Considered when Delta T limitation is set to "Delta T Manager scaled". |
bSelectMeterRegister_Write | BOOL | FALSE = certified meter; TRUE = lifetime meter. |
Outputs
iErrorId : MP_Error;
st_MalfunctionService : St_MP_EV_V4_MalfunctionServiceInfo;
nControlMode : E_MP_EV_V4_ControlMode;
rBusFailPosition : LREAL;
nCommunicationWatchdog : UINT;
bSetpointSource : BOOL;
nSensor1Type : E_MP_EV_V4_Sensor1Type;
rVmin : LREAL;
rVmax : LREAL;
rVnom : LREAL;
rPnom : LREAL;
rPmax : LREAL;
nDeltaTLimitation : E_MP_EV_V4_DeltaTLimitation;
nDeltaTManagerStatus : E_MP_EV_V4_DeltaTManagerStatus;
rSetpointDeltaT : LREAL;
rSetpointAbsFlowDeltaT : LREAL;
arSerialNumber : ARRAY[0..1] OF DWORD;
bSelectMeterRegister : BOOL;
bBusy | BOOL | This bit is set for as long as the function block is active. |
bError | BOOL | This output goes TRUE as soon as an error occurs. This error is described via the iErrorId variable. |
iErrorId | This output outputs an error code in the event of an error. bError goes TRUE at the same time. | |
st_MalfunctionService | Malfunction and service information | |
nControlMode | Control mode | |
rBusFailPosition | LREAL | Not functional. |
nCommunicationWatchdog | UINT | Communication monitoring in sec (0...3600). Not functional (reserved for future extensions). |
bSetpointSource | BOOL | TRUE = bus; FALSE = analog |
nSensor1Type | Sensor 1 Type | |
rVmin
| LREAL | Min. setpoint in % (0...Vmax). Refers to Vnom and is taken into account when control mode = flow control. |
rVmax | LREAL | Max. setpoint in % (25...100). Refers to Vnom and is taken into account when control mode = flow control. |
rVnom | LREAL | Nominal volume flow in l/s (0...100) |
rPnom |
LREAL |
Nominal output in kW (0...21.5). |
rPmax |
LREAL |
Max. setpoint in % (5...100). Refers to Pnom and is taken into account if control mode = power control. |
nDeltaTLimitation |
Indicates whether the device responds to a low delta T. | |
nDeltaTManagerStatus |
Indicates the status of the Delta T Manager. | |
rSetpointDeltaT |
LREAL |
Setpoint Delta T in K (0...60). Is taken into account if delta T limitation is active (not disabled). |
rSetpointAbsFlowDeltaT |
LREAL |
Setpoint Abs flow Delta T in l/s (0...100.000). Considered when Delta T limitation is set to "Delta T Manager scaled". |
arSerialNumber | ARRAY OF DWORD | Serial number of the device. |
bSelectMeterRegister | BOOL | FALSE = certified meter; TRUE = lifetime meter. |
Development environment | PLC library to include |
TwinCAT from v3.1.4024.26 | Tc2_MPBus from 3.4.14.0 |
