MP_EnergyValveV4_Configuration
MP_EnergyValveV4_Configuration 1:
This function block is used to configure the Energy Valve actuators EV..R2+.. with firmware 4.0.0 or higher. For more information please visit www.belimo.com.
MP_Address is used to specify the MP-Bus device with which the function block is to communicate. bStart activates communication with the MP-Bus device. bBusy indicates that the function block is active. bError is used to indicate an error in communication with the actuator. The type of the error can be read with iErrorId.
MP_EnergyValveV4_Configuration 2: Inputs
  MP_Address                   : USINT := 1;
  bStart                       : BOOL;
  bRead_Write                  : BOOL;
  strDataKL6771                : DataKL6771;
  rVmax_Write                  : LREAL := 100;
  rVmin_Write                  : LREAL;
  bSetpointSource_Write        : BOOL := TRUE;
  nSensor1Type_Write           : E_MP_EV_V4_Sensor1Type;
  nControlMode_Write           : E_MP_EV_V4_ControlMode := 1;
  rBusFailPosition_Write       : LREAL;
  nCommunicationWatchdog_Write : UINT;
  rPmax_Write                  : LREAL := 100;
  nDeltaTLimitation_Write      : E_MP_EV_V4_DeltaTLimitation;
  rSetpointDeltaT_Write        : LREAL := 1.0;
  rSetpointAbsFlowDeltaT_Write : LREAL;
  bSelectMeterRegister_Write   : BOOL;
Type
MP_Address
USINT
MP-Bus address of the slave.
bStart
A positive edge starts the function block.
bRead_Write
If FALSE then READ only; if TRUE then READ and WRITE.
strDataKL6771
DataKL6771
The data structure with which the KL6771() function block must be linked.
rVmax_Write
LREAL
Max. setpoint in % (25…100). Standard 100%. Refers to Vnom and is taken into account when control mode = flow control.
rVmin_Write
LREAL
Min. setpoint in % (0…Vmax). Vmin must be smaller than Vmax.
TRUE = bus; FALSE = analog
nSensor1Type_Write
Sensor 1 Type
nControlMode_Write
Control mode.
LREAL
Not functional.
UINT
Communication monitoring in s (0…3600). Not functional (reserved for future extensions).
rPmax_Write
LREAL
Max. setpoint in % (5…100). Standard 100%. Refers to Pnom and is taken into account if control mode = power control.
Determines whether the device responds to a low delta T.
LREAL
Setpoint delta T in K (0…60). Standard 1.0K. Is taken into account if the delta T limitation is active (not disabled).
LREAL
Setpoint absolute flow delta T in l/s (0…100,000). Considered when Delta T limitation is set to “Delta T Manager scaled”.
FALSE = certified meter; TRUE = lifetime meter.
MP_EnergyValveV4_Configuration 3: Outputs
  bBusy                  : BOOL;
  bError                 : BOOL;
  iErrorId               : MP_Error;
  st_MalfunctionService  : St_MP_EV_V4_MalfunctionServiceInfo;
  nControlMode           : E_MP_EV_V4_ControlMode;
  rBusFailPosition       : LREAL;
  nCommunicationWatchdog : UINT;
  bSetpointSource        : BOOL;
  nSensor1Type           : E_MP_EV_V4_Sensor1Type;
  rVmin                  : LREAL;
  rVmax                  : LREAL;
  rVnom                  : LREAL;
  rPnom                  : LREAL;
  rPmax                  : LREAL;
  nDeltaTLimitation      : E_MP_EV_V4_DeltaTLimitation;
  nDeltaTManagerStatus   : E_MP_EV_V4_DeltaTManagerStatus;
  rSetpointDeltaT        : LREAL;
  rSetpointAbsFlowDeltaT : LREAL;
  arSerialNumber         : ARRAY[0..1] OF DWORD;
  bSelectMeterRegister   : BOOL;
Type
bBusy
This bit is set for as long as the function block is active.
This output goes TRUE as soon as an error occurs. This error is described via the iErrorId variable.
iErrorId
MP_ERROR
This output outputs an error code in the event of an error. bError goes TRUE at the same time.
ST_MP_EV_V4_MalfunctionServiceInfo
Malfunction and service information
nControlMode
Control mode.
rBusFailPosition
LREAL
Not functional.
UINT
Communication monitoring in sec (0…3600). Not functional (reserved for future extensions).
bSetpointSource
nSensor1Type
Sensor 1 Type
rVmin
LREAL
Min. setpoint in % (0...Vmax). Refers to Vnom and is taken into account when control mode = flow control.
rVmax
LREAL
Max. setpoint in % (25...100). Refers to Vnom and is taken into account when control mode = flow control.
rVnom
LREAL
Nominal volume flow in l/s (0…100).
rPnom
LREAL
Nominal output in kW (0...21.5).
rPmax
LREAL
Max. setpoint in % (5...100). Refers to Pnom and is taken into account if control mode = power control.
nDeltaTLimitation
Indicates whether the device responds to a low delta T.
Indicates the status of the Delta T Manager.
rSetpointDeltaT
LREAL
Setpoint Delta T in K (0...60). Is taken into account if delta T limitation is active (not disabled).
LREAL
Setpoint Abs flow Delta T in l/s (0...100.000). Considered when Delta T limitation is set to "Delta T Manager scaled".
arSerialNumber
ARRAY OF DWORD
Serial number of the device.
Development environment
PLC library to include
TwinCAT from v3.1.4024.26
Tc2_MPBus from 3.4.14.0