FB_MBUS_General_Ext
FB_MBUS_General_Ext 1:
Some M-Bus devices send values distributed over several telegrams. The function block FB_MBUS_General_Ext can be used to read all telegrams from any M-Bus devices.
The variable arrTelegram[1..cMBUS_MaxTelegrams].arrData[1..cMBUS_MaxData] supplies a maximum of cMBUS_MaxData data from a maximum of cMBUS_MaxTelegrams telegrams. String values and vendor-specific information are not shown correctly.
The number of telegrams to be read can be changed with the constant cMBUS_MaxTelegrams.
The number of data per telegram to be read can be changed with the constant cMBUS_MaxData.
The function block FB_MBUS_General_Ext can only be executed together with the function block FB_MBUSKL6781().
FB_MBUS_General_Ext 2:
Further information
See Operating principle of the function block
FB_MBUS_General_Ext 3: Inputs
  usiAddress   : USINT;
  stSecAdr     : ST_MBUS_SecAdr;
  eBaudrate    : E_MBUS_Baudrate := eMBUS_Baud2400;
  bStart       : BOOL;
  bSND_NKE     : BOOL := TRUE;
  bReadInit    : BOOL := TRUE;
  tMinSendTime : TIME := t#2s;
  usiUnit      : USINT;
  bDisabled    : BOOL := FALSE;
Type
usiAddress
USINT
Primary address of the meter to be read with this function block.
stSecAdr
ST_MBUS_SecAdr
Secondary address of the meter to be read with this function block.
eBaudrate
E_MBUS_Baudrate
300, 600, 1200, 2400, 4800, 9600 baud
bStart
All meters are read once on the positive edge of this input.
bSND_NKE
TRUE initializes the meter for each read operation and sets the meter to the first telegram (SND_NKE).
bReadInit
If the PLC is restarted, the meter is read once.
tMinSendTime
TIME
Default t#2s. The meter is read again, once the time set here has elapsed. If t#0s the meter is not read and can be read manually with bStart.
usiUnit
USINT
Unit of the energy values to be output by the function block. 0=W(h) / 1=KW(h) / 2 =MW(h) / 3=GW(h).
bDisabled
TRUE = deselection of the function block
FB_MBUS_General_Ext 4: Inputs/outputs
  stCom : ST_MBUS_Communication;
Type
stCom
This structure is used to link the function block FB_MBUSKL6781() with the meter blocks.
FB_MBUS_General_Ext 5: Outputs
  bBusy          : BOOL;
  bReady         : BOOL;
  bError         : BOOL;
  eError         : E_MBUS_ERROR;
  dwIdNumber     : DWORD;
  byStatus       : BYTE;
  byGEN          : BYTE;
  byCounter      : BYTE;
  usiRecivedAdr  : USINT;
  eMedium        : E_MBUS_Medium;
  sMan           : STRING(3);
  arrTelegram    : ARRAY [1..cMBUS_MaxTelegrams] OF ST_MBus_Data2;
Type
bBusy
The bBusy output is TRUE as long as the meter is being read.
bReady
The bReady output is TRUE for one cycle, once meter reading is completed.
This output goes TRUE as soon as an error occurs. This error is described via the eError variable.
eError
E_MBUS_ERROR
This output outputs an error code in the event of an error. bError goes TRUE at the same time.
dwIdNumber
DWORD
Serial number of the meter (secondary address)
byStatus
BYTE
Device status
byGEN
BYTE
Software version of the device
byCounter
BYTE
Number of times the master has accessed data of the respective slave
usiRecivedAdr
USINT
Received primary address (0-250)
eMedium
E_MBUS_Medium
Medium
sMan
STRING
Manufacturer sign
arrTelegram
ARRAY OF ST_MBus_Data2
Maximum cMBUS_MaxTelegrams telegrams. The meaning of the values is explained in the M-Bus protocol for the device.
Development Environment
PLC library to include
TwinCAT from v3.1.4020.14
Tc2_MBus from 3.3.5.0