Control commands of an axis

Feed Enable, Axis

Description

Axis-specific Feed Enable

The Feed Enable must be set for all axes to be moved. If this is not the case, no path movement occurs.

Control commands of an axis 1:Data type

MCControlBoolUnit, see description Control Unit

Characteristics

SERCOS drives

In the case of SERCOS drives, the data item is derived from bit 13 of the control word.

Access

PLC reads Request + State and writes Command + Enable

ST path

pAC[axis_idx]^.addr^.McControlLr_Data.MCControlBoolUnit_ReleaseFeedhold

Commanded, requested, and return value

ST element

. X_Command

.X_Request

Data type

BOOL

Value range

[TRUE = Drive Enable,

Transition TRUE -> FALSE: The drive is shut down in compliance with the acceleration parameters.

FALSE = Drive HALT]

Return value

ST element

. X_State

Data type

BOOL

Value range

[TRUE = Drive Enable, FALSE = Drive HALT]

Redirection

ST element

. X_Enable

Feed Hold ON/OFF, axis

Description

Axis-specific Feed Hold

The axis-specific Feed Hold acts on an axis if this axis is currently not being traversed in the path network but in Manual mode or as an independent axis.

Otherwise, the global Feed Hold of the channel acts for it.

Control commands of an axis 2:Data type

MCControlBoolUnit, see description Control Unit

Access

PLC reads Request + State and writes Command + Enable

ST path

pAC[axis_idx]^.addr^.McControlIpo_Data. MCControlBoolUnit_Feedhold

Commanded, requested and return value

ST element

.X_Command

.X_Request

.X_State

Data type

BOOL

Value range

[TRUE = Feed Hold on, FALSE = Feed Hold off]

Redirection

ST element

. X_Enable

Feed Override, axis

Description

Axis-specific feed override

The axis-specific feed override allows to weight the axis velocity with an additional percentage factor. The axis-specific feed override acts on an axis if this axis is currently not being traversed in the path network but in Manual mode or as an independent axis.

Otherwise, the global override of the channel acts for it.

Control commands of an axis 3:Data type

MCControlUNS16Unit, see description Control Unit

Access

PLC reads Request + State and writes Command + Enable

ST path

pAC[axis_idx]^.addr^.McControlIpo_Data.MCControlUNS16Unit_Override

Commanded, requested, and return value

ST element

.D_Command

.D_Request

.D_State

Unit

0.1 %

Data type

UINT

Value range

[0, P-AXIS-00109]

P-AXIS-00109 is an axis-specific parameter. The default value is 1000. See [Axis Parameter].

Redirection

ST element

. X_Enable

Feed override valid, axis

Description

Axis-specific Feed Override valid

Control commands of an axis 4:Data type

MCControlBoolUnit, see description Control Unit

Access

PLC reads Request + State and writes Command + Enable

ST path

pAC[axis_idx]^.addr^.McControlIpo_Data.MCControlBoolUnit_OverrideValid

Commanded, requested and return value

ST element

.X_Command

.X_Request

.X_State

Data type

BOOL

Value range

[TRUE = Axis-specific Feed Override valid, FALSE]

Redirection

ST element

. X_Enable

Drive ON

Description

Drive ON

Control commands of an axis 5:Data type

MCControlBoolUnit, see description Control Unit

Characteristics

SERCOS drives

In the case of SERCOS drives, the data item is derived from bit 15 of the control word.

Access

PLC reads Request + State and writes Command + Enable

ST path

pAC[axis_idx]^.addr^.McControlLr_Data.MCControlBoolUnit_DriveOn

Commanded and requested value

ST element

.X_Command

.X_Request

Data type

BOOL

Value range

[TRUE = Drive ON,

Transition TRUE -> FALSE: The drive is shut down as best possible.

FALSE = Drive OFF]

Return value

ST element

. X_State

Data type

BOOL

Value range

[TRUE = Drive ON, FALSE = Drive OFF]

Redirection

ST element

. X_Enable

Controller Enable

Description

Controller Enable “axis-specific” torque connection.

Control commands of an axis 6:Data type

MCControlBoolUnit, see description Control Unit

Characteristics

SERCOS drives

In the case of SERCOS drives, the data item is derived from bit 14 of the control word.

Access

PLC reads Request + State and writes Command + Enable

ST path

pAC[axis_idx]^.addr^.McControlLr_Data.MCControlBoolUnit_TorquePermission

Commanded, requested, and return value

ST element

.X_Command

.X_Request

.X_State

Data type

BOOL

Value range

[TRUE = Torque connection, FALSE = Drive is idle]

Redirection

ST element

. X_Enable

The following diagram shows the combination of control units of the HLI and the SERCOS-Controlword respectively SERCOS-Statusword.

Control commands of an axis 7:
Fig.8: Figure 2-1: Combination control units and SERCOS Control- respectively Statusword

Reference cam

Description

Signal of a reference cam when homing.

Control commands of an axis 8:Data type

MCControlBoolUnit, see description Control Unit

Characteristics

Commanding this signal acts only if the characteristic parameter lr_hw[i].cam_direct_access = 0 is set in the axis machine data record of the relevant axis.

Using characteristic parameter lr_hw[i].cam_level in the axis machine data record can program the action of this command from high-active to low-active.

The action in the default case is described below.

Access

PLC reads Request + State and writes Command + Enable

ST path

pAC[axis_idx]^.addr^.McControlLr_Data.MCControlBoolUnit_ReferenceCam

Commanded, requested, and return value

ST element

.X_Command

.X_Request

.X_State

Data type

BOOL

Value range

[TRUE = Reference cam switched, FALSE = Reference cam not switched]

Redirection

ST element

. X_Enable

Reduced feed, axis

Description

If this signal is activated axis velocity is reduced, in case G00 or G01 is commanded, to the values defined in P-AXIS-00214 respectively P-AXIS-00155. See also [Axis Parameter].

Control commands of an axis 9:Data type

MCControlBoolUnit, see description Control Unit

Characteristics

Is the axis member of a channel (axes group), the limitations of the other axes that are part of the motion are considered. The path feed that takes effect in such a case is evaluated that no axis that is part of the actual motion exceeds their configured feed limit. In this case the behavior is identical to the command via the channel specific control unit.

Access

PLC reads Request + State and writes Command + Enable

ST path

pAC[axis_idx]^.addr^.McControlIpo_Data.MCControlBoolUnit_ReducedFeed

Commanded, requested, and return value

ST element

X_Command

.X_Request

.X_State

Data type

BOOL

Value range

[TRUE = Reduced feed active, FALSE = Reduced feed not active]

Redirection

ST element

. X_Enable

Reduced feed in zone 1, axis

Description

When this signal is activated and axis position is within the values defined in P-AXIS-00085 and P-AXIS-00093 axis velocity is reduced to the value defined in P-AXIS-00030. If necessary velocity is reduced after entering the zone. See also [Axis Parameter].

Control commands of an axis 10:Data type

MCControlBoolUnit, see description Control Unit

Characteristics

Is the axis member of a channel (axes group), the limitations of the other axes that are part of the motion and located within their configured zone, are considered.

Access

PLC reads Request + State and writes Command + Enable

ST path

pAC[axis_idx]^.addr^.McControlIpo_Data.MCControlBoolUnit_ReducedFeedZone

Commanded, requested, and return value

ST element

X_Command

.X_Request

.X_State

Data type

BOOL

Value range

[TRUE = Reduced feed in zone 1 active, FALSE = Reduced feed in zone 1 not active]

Redirection

ST element

. X_Enable

Reduced feed in zone 2, axis

Description

When this signal is activated and axis position is within the values defined in P-AXIS-00097 and P-AXIS-00105 path velocity is reduced to the value defined in P-AXIS-00030. If necessary velocity is reduced after entering the zone.

Control commands of an axis 11:Data type

MCControlBoolUnit, see description Control Unit

Characteristics

Is the axis member of a channel (axes group), the limitations of the other axes that are part of the motion and located within their configured zone, are considered.

Access

PLC reads Request + State and writes Command + Enable

ST path

pAC[axis_idx]^.addr^.McControlIpo_Data.MCControlBoolUnit_ReducedFeedZone2

Commanded, requested, and return value

ST element

X_Command

.X_Request

.X_State

Data type

BOOL

Value range

[TRUE = Reduced feed in zone 2 active, FALSE = Reduced feed in zone 2 not active]

Redirection

ST element

. X_Enable

Suppression of Read-In Enable

Description

Suppression of Read-In Enable

If the Read-In Enable is cancelled (setting NoEfg), the interpolator does not read any new advance-decoded NC forward-traverse information, i.e. the movement is stopped after the end of the current jobs in the interpolator.

Control commands of an axis 12:Data type

MCControlBoolUnit, see description Control Unit

Access

PLC reads Request + State and writes Command + Enable

ST path

pAC[axis_idx]^.addr^.McControlIpo_Data.MCControlBoolUnit_NoEfg

Commanded, requested, and return value

ST element

.X_Command

.X_Request

.X_State

Data type

BOOL

Value range

[TRUE = No Read-In Enable, FALSE = Read-In Enable]

Redirection

ST element

. X_Enable

Machining Simulation, Axis

Description

Activates and deactivates axis-specific machining simulation.

During machining simulation, all axis-specific technology commands of the NC program are no longer output to the PLC but are acknowledged internally.

Control commands of an axis 13:Data type

MCControlBoolUnit, see description Control Unit

Access

PLC reads Request + State and writes Command + Enable

ST path

pAC[axis_idx]^.addr^.McControlIpo_Data.MCControlBoolUnit_MachiningSimu

Commanded, requested, and return value

ST element

.X_Command

.X_Request

.X_State

Data type

BOOL

Value range

[TRUE = No Read-In Enable, FALSE = Read-In Enable]

Redirection

ST element

. X_Enable

Tracking Operation

Description

The axis is set to tracking operation (follow up), i.e. the control loop is opened. The command position implicitly is set to the actual position.

Control commands of an axis 14:Data type

MCControlBoolUnit, see description Control Unit

Characteristics

Because the command value takes over the position lag of the actual position, it is possible that any external force (e.g. weight of axis) slowly moves the axis (drift).

Access

PLC reads Request + State and writes Command + Enable

ST-path

pAC[axis_idx]^.addr^.McControlLr_Data.MCControlBoolUnit_FollowUp

Commanded, requested, and return values

ST element

.X_Command

.X_Request

.X_State

Data type

BOOL

Range

[TRUE = control loop open, FALSE]

Redirection

ST element

. X_Enable

Ignore minimal tool velocity

Description

If a value for minimal tool velocity is configured for a tool, NC-Kernel by default takes care, that this limit is not underrunned by commanding an override.

This control unit is used to avoid this behavior of the NC-Kernel and the override takes effect onto the axis as commanded.

Control commands of an axis 15: Data type

MCControlBoolUnit, see description Control Unit

Characteristics

Control unit only takes effect if the axis is a spindle.

Access

PLC reads Request + State and writes Command + Enable

ST-path

pAC[axis_idx]^.addr^.McControlIpo_Data.MCControlBoolUnit_IgnoreVbMinTool

Commanded, requested, and return values

ST element

.X_Command

.X_Request

.X_State

Data type

BOOL

Range

[TRUE = Ignore minimal tool velocity in case of override command, FALSE]

Redirection

ST element

. X_Enable

Driving out gantry difference

Description

If the axis is a gantry slave axis and master and slave are referenced the position difference between master and slave axis is driven out.

Control commands of an axis 16:Data type

MCControlBoolUnit, see description Control Unit

Characteristics

 

Access

PLC reads Request + State and writes Command + Enable

ST-path

pAC[axis_idx]^.addr^.McControlLr_Data.MCControlBoolUnit_GantryOn

Commanded, requested, and return values

ST element

.X_Command

.X_Request

.X_State

Data type

BOOL

Range

[TRUE = driving out gantry difference allowed, FALSE]

Redirection

ST element

. X_Enable

Overtake reference position

Description

Overtake reference position and mark axis as referenced on a rising edge of this control unit. Depending on the value of P-AXIS-00278 the axis position is set to the following values:

P-AXIS-00278

Reference position of the axis

ABSOLUT

Value of P-AXIS-00152

OFFSET

Encoder position of the drive + P-AXIS-00279

PLC

Value of control unit MCControlSGN32Unit
_ReferencePosition.

PLC_OFFSET

Encoderposition of the drive + Value of control unit refpos_position.

The variable X_State shows if the reference position was set manually and as a result the coordinate system has been shifted. The manual setting can be removed by a CNC-controlled homing (G74).

Also, for an axis with absolute measurement system the reference position can be set manually.

Control commands of an axis 17:Data type

MCControlBoolUnit, see description Control Unit

Characteristics

Edge detection. Functionality is active on rising edge on X_Command.

Access

PLC reads Request + State and writes Command + Enable

ST-path

pAC[axis_idx]^.addr^.McControlLr_Data. MCControlBoolUnit_SetReferencePosition

Commanded, requested, and return values

ST element

.X_Command

.X_Request

.X_State

Data type

BOOL

Range

[TRUE, FALSE]

Redirection

ST element

. X_Enable

Reference position to overtake

Description

If in the axis parameter list the value of P-AXIS-00278 is set to „PLC”‚ or to „PLC_OFFSET” the value of this control unit is used as reference position if the control unit MCControlSGN32_RefposPosition is used to trigger overtaking of the reference position.

P-AXIS-00278

Reference position of the axis

PLC

Value of this control unit.

PLC_OFFSET

Encoder position of the drive + Value of this control unit.

Control commands of an axis 18:Data type

MCControlSGN32Unit, see description Control Unit

Characteristics

 

Access

PLC reads Request + State and writes Command + Enable

ST-path

pAC[axis_idx]^.addr^.McControlLr_Data. MCControlSGN32UNIT
_ReferencePosition

Commanded, requested, and return values

ST element

.D_Command

.D_Request

.D_State

Data type

DINT

Dimension

0.1 um resp.10-4°

Range

[MIN_DINT, MAX_DINT]

Redirection

ST element

. X_Enable

Clear of homing state

Description

If axis has been homed by set of reference position of by G74, this state can be cleared again by usage of the actual control unit.

If axis has an absolute measurement system, the axis also is considered as „not homed“ afterwards (it can by homed again by standard G74).

E.g. by clearing the homing state the checking of software limit switches can by suppressed temporarily.

Any position offset activated by „set reference position“ is not cleared by the actual control unit.

The variable X_State displays if the axis is „not homed“ (inverse of homed).

Control commands of an axis 19:Data type

MCControlBoolUnit, see description Control Unit

Characteristics

Functionality is commanded by a rising edge at X_Command.

Access

PLC reads Request + State and writes Command + Enable

ST-path

pAC[axis_idx]^.addr^.McControlLr_Data.MCControlBoolUnit_ClearReferencePosition

Commanded, requested, and return values

ST element

.X_Command

.X_Request

. X_State

Data type

BOOL

Ramge

[TRUE, FALSE]

Redirection

ST element

. X_Enable

Definition of axis couplings

Description

With this control unit there can be defined axis couplings defined for the axis. It is possible to influence the movement of the axis additionally or exclusively by the movement of another axis. Further details can be taken from the documentation [Axis couplings via HLI].

Control commands of an axis 20:Data type

MCControlAxisCouplingUnit, s. Description Control Unit

Access

PLC reads State and writes Command + Enable

ST-path

pAC[axis_idx]^.addr^.McControlLr_Data.
MCControlAxisCouplingUnit_AxisCoupling

Commanded values

ST element

.AxisCouplingCommand

Information flow

PLC -> CNC

Data type

 

Access

PLC writes

Return value

ST element

.AxisCouplingState

Information flow

CNC -> PLC

Data type

 

Access

PLC reads

Redirection

ST element

. X_Enable

Axis couplings, state

Description

Displays the active axis couplings for this axis.

Information flow

CNC -> PLC

ST-Path

pAC[axis_idx]^.addr^.McControlLr_Data.
MCControlAxisCouplingUnit_AxisCoupling.AxisCouplingState

Data type

HLIAxisCouplingState

Access

PLC read

Elements of data type

Element

.desc[ ]

Data type

ARRAY [1 .. HLI_AxisCouplingMax] OF HLIAxisCouplingDesc

Access

PLC reads

 

 

Element

.X_Active

Data type

BOOL

Access

PLC reads

Axis couplings, command

Description

In this entry all coupling definitions for an axis is set up. The number of maximal possible coupling definitions is defined in the constant HLI_AxisCouplingMax. See also documentation [Axis couplings via HLI].

Information flow

PLC -> CNC

Data type

HLIAxisCouplingCommand

ST-Path

pAC[axis_idx]^.addr^.McControlLr_Data.
MCControlAxisCouplingUnit_AxisCoupling.AxisCouplingCommand

Access

PLC write

Elements of data type

Element

.desc[ ]

Data type

ARRAY [1 .. HLI_AxisCouplingMax] OF HLIAxisCouplingDesc

Access

PLC write

Element

X_Semaphor

Data type

BOOL

Access

Consumption data

The CNC overtakes the commanded values it the element is set to TRUE. After proccessing the commanded values, the CNC sets this element back to FALSE.

PLC sets element TRUE, if commanded values are ready to be overtaken by CNC. PLC may only change data of desc[..], if the value of the element is TRUE.

Definition of an axis coupling

Description

In this entry all coupling definitions for an axis is set up. See also documentation [Axis couplings via HLI].

Information flow

PLC -> CNC

Data type

HLIAxisCouplingDesc

ST-Path

pAC[axis_idx]^.addr^.McControlLr_Data.
MCControlAxisCouplingUnit_AxisCoupling.AxisCouplingCommand.desc[]idx

pAC[axis_idx]^.addr^.McControlLr_Data.
MCControlAxisCouplingUnit_AxisCoupling.AxisCouplingState.desc[idx

Access

Command for axis coupling: PLC writes

Status of axis coupling: PLC reads

Elements of data type

ST element

.CouplingMode

Data type

UINT

Value range

HLI_AXIS_COUPLING_INACTIVE = 0,

HLI_AXIS_COUPLING_ZERO = 1,

HLI_AXIS_COUPLING_DIRECT = 2,

HLI_AXIS_COUPLING_MIRROR = 3

HLI_AXIS_COUPLING_FRACT = 4

Description

  • HLI_AXIS_COUPLING_INACTIVE: Coupling is not acitve.
  • HLI_AXIS_COUPLING_ZERO: Coupling factor is zero, can be used to deactivate an axis.
  • HLI_AXIS_COUPLING_DIRECT: Coupling factor is 1.
  • HLI_AXIS_COUPLING_MIRROR: Coupling factor is –1
  • HLI_AXIS_COUPLING_FRACT: Coupling factor is a fraction, defined by .desc[idx].FractNumerator / .desc[idx].FractDenominator.

 

 

ST element

.AxisNumber

Data type

UINT

Description

Logical axis number of source axis. It the axis shall be moved with active coupling by a NC program a coupling command with the logical axis number of the axis itself and coupling mode HLI_AXIS_COUPLING_DIRECT must be defined.

 

 

ST element

.FractNumerator

Data type

INT

Value range

The permissible range is [-32768 .... 32767]. A value of zero has the same effect as coupling mode HLI_AXIS_COUPLING_INACTIVE.

Description

Numerator of coupling factor if coupling mode is set to HLI_AXIS_COUPLING_FRACT. For all other coupling modes this element is not used.

The maximal permissible value for the coupling factor desc[idx].FractNumerator / .desc[idx].FractDenominator is HLI_AXIS_COUPLING_FACT_MAX. Exceeding this value leads to error message P-ERR-70397.

 

 

ST element

.FractDenominator

Data type

INT

Value range

The permissible range is [-32768 .... 32767], zero excluded. A value of zero in this element leads to error message P-ERR-70396.

Description

Denominator of coupling factor if coupling mode is set to HLI_AXIS_COUPLING_FRACT. For all other coupling modes this element is not used.

The maxima permissible value for the coupling factor desc[idx].FractNumerator / .desc[idx].FractDenominator is HLI_AXIS_COUPLING_FACT_MAX. Exceeding this value leads to error message P-ERR-70397.

Probing signal

Description

With this control unit the PLC can provide the probing signal via the HLI. If this control unit is used the axis parameter kenngr.probing_signal_via_plc has to be set to 1. See also [Axis Parameter].

Control commands of an axis 21:Data type

MCControlBoolUnit, see descriptionControl Unit

Characteristics

Edge detection. The edge set up in axis parameter kenngr.mess_neg_flanke is used to overtake the probing value.

Access

PLC reads Request + State and writes Command + Enable

ST- Path

pAC[axis_idx]^.addr^.McControlLr_Data.MCControlBoolUnit_ProbingSignal

Commanded, requested and return values

ST element

.X_Command

.X_Request

. X_State

Data type

BOOL

Value range

[TRUE, FALSE]

Redirection

ST element

. X_Enable

OTC offset

Description

Using this wear offset the wear in orientation of this axis could be corrected.

Unit: 0.1µm

Data type

MCControlSGN32Unit, see descriptionControl Unit

Characteristics

Assigned offsets are adjusted over several cycles.

Access

PLC reads Request + State and writes Command + Enable

ST-Path

pAC[axis_idx]^.addr^.McControlLr_Data.MCControlSGN32Unit_OTCOffset

Commanded, requested and return values

ST element

. X_Command

.X_Request

.X_State

Data type

DINT

Value range

[-P-TOOL-00031, P-TOOL-00031]

Redirection

ST element

.X_Enable