ELM370x - Technical data
Technical data |
ELM3702-0000 |
ELM3704-000x, ELM3704‑0020, ELM3704‑1001 | |
Analog inputs |
2 channel (differential) |
4 channel (differential) | |
Time relation between channels to each other |
Simultaneous conversion of all channels in the terminal, synchronous conversion between terminals, if DistributedClocks will be used | ||
ADC conversion method |
ΔΣ (Delta-Sigma) with internal sample rate | ||
8 Msps |
8 Msps | ||
Cutoff frequency input filter hardware |
Before AD converter: Within ADC after conversion: | ||
Low pass |
Low pass | ||
Type sinc3/average filter The ramp-up time/ settling time/ delay caused by the filtering will be considered within the DistributedClocks-Timestamp. | |||
Resolution |
24 bit (including sign) | ||
Connection technology |
2/3/4/5/6-wire | ||
Sampling rate (per channel, simultaneous) |
100 µs/10 ksps Free down sampling by Firmware via decimation factor | ||
Oversampling |
1…100 selectable | ||
Supported EtherCAT cycle time (depending on the operation mode) |
DistributedClocks: min. 100 µs, max. 10 ms FrameTriggered/Synchron: min. 200 µs, max. 100 ms FreeRun: not yet supported | ||
Internal resistance |
> 500 kΩ (60 V); > 4 MΩ (other) ; 150 Ω (current) | ||
Operation range voltage measurement |
±60/10/5/2.5/1.25 V, 2-wire-connection | ||
Operation range current measurement |
±20 mA, 0/4…20 mA, NAMUR NE43 3) 2-wire-connection | ||
Operation range SG, measuring bridge |
Full bridge |
Full bridge (±2/4/8/32 mV/V) 3), 4/6-wire-connection, Bridge supply adjustable | |
Half bridge |
Half bridge (±2/16 mV/V) 3), internal switched bridge extension, 3/5-wire-connection Bridge supply adjustable | ||
Quarter bridge |
Quarter bridge 120 Ω and 350 Ω (±2/4/8/32 mV/V) 3), internal switched bridge extension, 2/3-wire-connection, Bridge supply adjustable | ||
Operation range IEPE |
Measuring ranges ±2.5/5/10 V 3) adjustable, Current supply/ / IEXCITE (IEPE Bias Current) 2 mA (shutdown not possible), Acquisition of the modulated alternating voltage, AC/DC coupling (configurable parameters of high pass), 2-wire-connection (note: TEDS Class 1 not supported) | ||
Operation range potentiometer |
Potentiometer ≥ 1 kΩ, power supply integrated and adjustable 0…5V 3) 3/5-wire-connection | ||
Operation range resistance measurement |
0…50 Ω, 0…200 Ω, 0…500 Ω, 0…2 kΩ, 0…5 kΩ 3) 2/3/4-wire-connection | ||
Operation range temperature (RTD) |
Pt100, Pt200, Pt500, Pt1000, Ni100, Ni120, Ni1000, div. KT/KTY 3) 2/3/4-wire-connection | ||
Operation range temperature (thermocouple) |
Typ K, J, L, E, T, N, U, B, R, S, C, cold junction measurement internal/external, 2-wire-connection | ||
Connection diagnosis |
Wire break/short cut | ||
Internal analog ground AGND |
Existing by external connection to -Uv | ||
Surge voltage protection of the inputs related to GND |
Value to follow | ||
Internal power supply |
via E-bus | ||
Current consumption E-bus |
typ. 530 mA |
typ. 890 mA | |
Current consumption power contacts |
Thermal power dissipation |
typ. 3 W | ||
Dielectric strength - destruction limit |
Max. permitted short-term/continuous voltage between each contact points ±I1, ±I2, +Uv and –Uv: non-supplied ±40 V, supplied ±36 V Note: -Uv corresponds to internal AGND | ||
Recommended operation voltage range to compliance with specification |
Max. permitted voltage during specified normal operation between ±I1 and ±I2: typ. ±35 V against –Uv within 60 V-measuring range ±10 V against –Uv in all other measurement ranges Note: -Uv corresponds to internal AGND |
Common data | ELM3702-0000 | ELM3704-000x, ELM3704‑0020, ELM3704‑1001 |
Distributed Clocks | Yes, with Oversampling n = 1…100, accuracy << 1 μs | |
Special features | Extended Range 107 %, freely configurable numeric filters, TrueRMS, integrator/differentiator, non-linear scaling, PeakHold | |
Functional diagnosis 1) | Yes | |
Electrical isolation channel/channel 2) | no | |
Electrical isolation channel/E-Bus 2) | Functional insulation, 707 V DC (type test) | |
Electrical isolation channel/SGND 2) | Functional insulation, 707 V DC (type test) | |
Configuration | via the EtherCAT Master, e.g. TwinCAT | |
Note to cable length | Signal cable lengths to the sensor / encoder over 3 m must be shielded, the shield design must be in line with the state of the art and be effective. For larger cable lengths > 30 m, a suitable surge protection should be provided if appropriate interference could affect the signal cable. |
1) see chapters Self-test and self-test report and Connection test/switchable connection diagnosis
2) see notes to potential groups within chapter Power supply, potential groups
3) Not adjusted for ELM3704-1001 (except thermocouple and bipolar measurement ranges of voltage and IEPE)
Basic mechanical properties | ELM3702-0000 | ELM3704-000x, ELM3704‑0020, ELM3704‑1001 |
Connection type | 6-pin push-in cage clamp, service plug | ELM3704‑0000, |
ELM3704-0001: | ||
Dimensions (W x H x D) | See chapter Housing | |
Mounting | on 35 mm rail conforms to EN 60715 | |
Note Mounting | Plug partly not within scope of delivery, see chapter | |
Weight | Approx. 350 g | |
Permissible ambient temperature range during operation | 0…+55 °C | |
Permissible ambient temperature range during storage | -25…+85 °C |
Environmental data | ELM3702-0000 | ELM3704-000x, ELM3704‑0020, ELM3704‑1001 |
Permissible operating altitude range | 0 up to 2000 m (derating at higher altitudes on request) | |
Relative humidity | max. 95%, no condensation | |
Protection class | IP 20 |
Normative data | ELM3702-0000 | ELM3704-000x, ELM3704‑0020, ELM3704‑1001 |
Vibration-/shock resistance | Conforms to EN 60068-2-6 / EN 60068-2-27 | |
EMC-resistance / emission | Conforms to EN 61000-6-2 / EN 61000-6-4 | |
Approvals/ markings *) | CE, UKCA, EAC, cULus | |
EMC notes | In case of push-in and mini-TC connectors, ESD air discharges conforming to EN 61000-6-4 into the connectors or to the lines connected there can lead to measurement deviations up to ±FSV within the respective channel or to other channels by crosstalk. Peak voltages (surge) conforming to EN 61000-6-2 that are applied to the cable shield can lead to measurement deviations up to ±FSV. |
Notice | |
Extended Range mode not available The Extended Range mode is not available for RTD measurement.
- ELM370x overview measurement ranges
- Measurement 5V/ 10V/ ±20 mV..±60 V
- Measurement ±20 mA/ 0..20 mA/ 4..20 mA/NAMUR
- Measurement resistance
- RTD measurement
- Potentiometer measurement
- Measurement SG 1/1 bridge (full bridge) 4/6-wire connection
- Measurement SG 1/2 bridge (half bridge) 3/5-wire connection
- Measurement SG 1/4 bridge (quarter-bridge) 2/3-wire connection
- Measurement IEPE 10 V / 20 V / ±2.5 V / ±5 V / ±10 V
- Thermocouple measurement