Object description EL3208-0010
![]() | EtherCAT XML Device Description The display matches that of the CoE objects from the EtherCAT XML Device Description. We recommend downloading the latest XML file from the download area of the Beckhoff website and installing it according to installation instructions. |
![]() | Parameterization via the CoE list (CAN over EtherCAT) The terminal is parameterized via the CoE - Online tab (double-click on the respective object) or via the Process Data tab (allocation of PDOs). Please note the following general CoE information when using/manipulating the CoE parameters: - Keep a startup list if components have to be replaced - Differentiation between online/offline dictionary, existence of current XML description - Use "CoE reload" for resetting changes |
![]() | Relevant objects The object description refers to the analog input terminals for Pt100 (RTD) in 1 to 8 channel versions. Observe the indices with regard to the objects relevant for the respective terminal (channel dependent). |
Introduction
- Objects required for parameterization and profile-specific objects required during commissioning
- Objects for indicating internal settings (may be fixed)
The following section first describes the objects required for normal operation, followed by a complete overview of missing objects.
Objects for commissioning
Index 1011 Restore default parameters
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default value |
1011:0 |
Restore default parameters |
UINT8 |
RO |
0x01 (1dec) |
1011:01 |
SubIndex 001 |
If this object is set to "0x64616F6C" in the set value dialog, all backup objects are reset to their delivery state. |
UINT32 |
RW |
0x00000000 (0dec) |
Index 80n0 RTD settings for 0 ≤ n ≤ 7 (Ch. 1 – 8)
![]() | The filter properties are set via index 0x8000:15 only The filter frequencies are set centrally for all channels of the EL32xx terminals via index 0x8000:15 (channel 1). |
80n0:0 | RTD Settings | Maximum subindex | UINT8 | RO | 0x1B (27dec) |
80n0:01 | User scaling is active. | BOOLEAN | RW | 0x00 (0dec) | |
80n0:02 | 0: Signed presentation 1: Absolute value with MSB as sign 2: High resolution (1/100°C) [default for EL3201/2-00x0 high-precision terminals, see note! | BIT3 | RW | 0x00 (0dec) | |
80n0:05 | The S5 bits are shown in the three low-order bits (“Value” 0x60n0:11) Bit 0 = 1 ("Overange" or "Underrange") | BOOLEAN | RW | 0x00 (0dec) | |
80n0:0A | Enabling of user calibration | BOOLEAN | RW | 0x00 (0dec) | |
80n0:0B | Enabling of the manufacturer calibration | BOOLEAN | RW | 0x01 (1dec) | |
80n00:11 | User scaling offset | INT16 | RW | 0x0000 (0dec) | |
80n0:12 | This is the gain of the user scaling. | INT32 | RW | 0x00010000 (65536dec) | |
80n0:15 | This object determines the digital filter settings, if it is activated via “Enable filter” (index 0x80n0:06). The possible settings are sequentially numbered. | UINT16 | RW | 0x0000 (0dec) | |
0: 50/60 Hz 120 ms 1: 4 ms 2: 8 ms 3: 16 ms 4: 32 ms 5: 40 ms 6: 48 ms 7: 60 ms 8: 101 ms 9: 120 ms 10: 50/60 Hz 11: 160 ms 12: 200 ms 13: 240 ms 14: 320 ms 15: 480 ms | |||||
80n0:17 | User calibration offset | INT16 | RW | 0x0000 (0dec) | |
80n0:18 | User calibration gain | UINT16 | RW | 0xFFFF (65535dec) |
80n0:19 | RTD element | UINT16 | RW | 0x0000 (0dec) | |
2: Pt1000 3: Pt500 5: Ni1000 6: Ni1000 8: Output in ohm 50: NTC1K8 51: NTC1K8 TK 52: NTC2K2 53: NTC3K 54: NTC5K 55: NTC10K 56: NTC10K PRE 57: NTC10k 3204 58: NTC10k Type 2 59: NTC10k Type 3 60: NTC10K Dale 61: NTC10K 3A221 62: NTC20K 99: B-parameter equation 100: potentiometer 0.1 ohm 0..5k 101: potentiometer 1 ohm res 102: potentiometer 10 ohm res 103: potentiometer 20 ohm res 200: NTC100K | UINT16 | RW | 0x0002 (2dec) | ||
80n0:1A | Connection technology 0: 2-wire connection | UINT16 | RW | 0x0000 (0dec) | |
80n0:1B | Calibration of the supply lines | INT16 | RW | 0x0000 (0dec) |
Index 8002 B-Parameter Equation
Index (hex) | Name | Meaning | Data type | Flags | Default value |
8002:0 | B_parameter Equation | Max. subindex | UINT8 | RO | 0x05 (5dec) |
8002:01 | Min Temperature |
| UINT16 | RW | - 50 |
8002:02 | Max Temperature |
| UINT16 | RW | 150 |
8002:03 | Rn 10 Ohm res. |
| UINT16 | RW | 1000 |
8002:04 | Tn |
| UINT16 | RW | 25 |
8002:05 | B-Parameter |
| UINT32 | RO | 3710.000000 |
Complete overview
Standard objects (0x1000-0x1FFF)
The standard objects have the same meaning for all EtherCAT slaves.
Index 1000 Device type
1000:0 | Device type | Device type of the EtherCAT slave: the Lo-Word contains the CoE profile used (5001). The Hi-Word contains the module profile according to the modular device profile. | UINT32 | RO | ( ) |
Index 1008 Device name
1008:0 | Device name | Device name of the EtherCAT slave | STRING | RO | ( ) |
Index 1009 Hardware version
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default value |
1009:0 |
Hardware version |
Hardware version of the EtherCAT slave |
STRING |
RO |
00 |
Index 100A Software version
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default value |
100A:0 |
Software version |
Firmware version of the EtherCAT slave |
STRING |
RO |
01 |
Index 1018 Identity
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default value |
1018:0 |
Identity |
Information for identifying the slave |
UINT8 |
RO |
0x04 (4dec) |
1018:01 |
Vendor ID |
Vendor ID of the EtherCAT slave |
UINT32 |
RO |
0x00000002 (2dec) |
1018:02 |
Product code |
Product code of the EtherCAT slave |
UINT32 |
RO |
1018:03 |
Revision |
Revision number of the EtherCAT slave; the low word (bit 0-15) indicates the special terminal number, the high word (bit 16-31) refers to the device description |
UINT32 |
RO |
1018:04 |
Serial number |
Serial number of the EtherCAT slave; the low byte (bit 0-7) of the low word contains the year of production, the high byte (bit 8-15) of the low word contains the week of production, the high word (bit 16-31) is 0 |
UINT32 |
RO |
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
10F0:0 |
Backup parameter handling |
Information for standardized loading and saving of backup entries |
UINT8 |
RO |
0x01 (1dec) |
10F0:01 |
Checksum |
Checksum across all backup entries of the EtherCAT slave |
UINT32 |
RO |
0x00000000 (0dec) |
Index 1A0n TxPDO Map for 0 ≤ n ≤ 7 (Ch. 1 - 8)
1A0n:0 | TxPDO Map Ch.1 | PDO Mapping TxPDO 1 | UINT8 | RW | 0x09 (9dec) |
1A0n:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x60n0 (RTD Inputs Ch.[n+1]), entry 0x01 (Underrange)) | UINT32 | RW | 0x60n0:01, 1 |
1A0n:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x60n0 (RTD Inputs Ch.[n+1]), entry 0x02 (Overrange)) | UINT32 | RW | 0x60n0:02, 1 |
1A0n:03 | SubIndex 003 | 3. PDO Mapping entry (4 bits align) | UINT32 | RW | 0x0000:00, 4 |
1A0n:04 | SubIndex 004 | 4. PDO Mapping entry (object 0x60n0 (RTD Inputs Ch.[n+1]), entry 0x07 (Error)) | UINT32 | RW | 0x60n0:07, 1 |
1A0n:05 | SubIndex 005 | 5. PDO Mapping entry (7 bits align) | UINT32 | RW | 0x0000:00, 7 |
1A0n:06 | SubIndex 006 | 6. PDO Mapping entry (object 0x180n (TxPDO-Par Ch.[n+1]), entry 0x07 (TxPDO-State)) | UINT32 | RW | 0x180n:07, 1 |
1A0n:07 | SubIndex 007 | 7. PDO Mapping entry (object 0x180n (TxPDO-Par Ch.[n+1]), entry 0x09 (TxPDO-Toggle)) | UINT32 | RW | 0x180n:09, 1 |
1A0n:08 | SubIndex 008 | 8. PDO Mapping entry (object 0x60n0 (RTD Inputs Ch.[n+1]), entry 0x11 (Value)) | UINT32 | RW | 0x60n0:11, 16 |
Index 1C00 Sync manager type
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default value |
1C00:0 |
Sync manager type |
Using the sync managers |
UINT8 |
RO |
0x04 (4dec) |
1C00:01 |
SubIndex 001 |
Sync-Manager Type Channel 1: Mailbox Write |
UINT8 |
RO |
0x01 (1dec) |
1C00:02 |
SubIndex 002 |
Sync-Manager Type Channel 2: Mailbox Read |
UINT8 |
RO |
0x02 (2dec) |
1C00:03 |
SubIndex 003 |
Sync-Manager Type Channel 3: Process Data Write (Outputs) |
UINT8 |
RO |
0x03 (3dec) |
1C00:04 |
SubIndex 004 |
Sync-Manager Type Channel 4: Process Data Read (Inputs) |
UINT8 |
RO |
0x04 (4dec) |
Index 1C12 RxPDO assign
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default value |
1C12:0 |
RxPDO assign |
PDO Assign Outputs |
UINT8 |
RW |
0x00 (0dec) |
Index 1C13 TxPDO assign
1C13:0 | TxPDO assign | PDO Assign Inputs | UINT8 | RW | 0x08 (8dec) |
1C13:01 | Subindex 001 | 1. allocated TxPDO (contains the index of the associated TxPDO mapping object) | UINT16 | RW | 0x1A00 (6656dec) |
1C13:02 | Subindex 002 | 2. allocated TxPDO (contains the index of the associated TxPDO mapping object) | UINT16 | RW | 0x1A01 (6657dec) |
1C13:03 | Subindex 003 | 3. allocated TxPDO (contains the index of the associated TxPDO mapping object) | UINT16 | RW | 0x1A02 (6658dec) |
1C13:04 | Subindex 004 | 4. allocated TxPDO (contains the index of the associated TxPDO mapping object) | UINT16 | RW | 0x1A03 (6659dec) |
1C13:05 | Subindex 005 | 5. allocated TxPDO (contains the index of the associated TxPDO mapping object) | UINT16 | RW | 0x1A04 (6660dec) |
1C32:06 | Subindex 006 | 6. allocated TxPDO (contains the index of the associated TxPDO mapping object) | UINT16 | RW | 0x1A05 (6661dec) |
1C13:07 | Subindex 007 | 7. allocated TxPDO (contains the index of the associated TxPDO mapping object) | UINT16 | RW | 0x1A06 (6662dec) |
1C13:08 | Subindex 008 | 8. allocated TxPDO (contains the index of the associated TxPDO mapping object) | UINT16 | RW | 0x1A07 (6663dec) |
Index 1C33 SM input parameter
1C33:0 | SM input parameter | Synchronization parameters for the inputs | UINT8 | RO | 0x20 (32dec) |
1C33:01 | Sync mode | Current synchronization mode:
1C33:02 | Cycle time | Cycle time (in ns):
| UINT32 | RW | 0x00000000 (0dec) |
1C33:03 | Shift time | Time between SYNC0 event and reading of the inputs (in ns, only DC mode) | UINT32 | RW | 0x00000000 (0dec) |
1C33:04 | Sync modes supported | Supported synchronization modes:
| UINT16 | RO | 0x8007 (32775dec) |
1C33:05 | Minimum cycle time | Minimum cycle time (in ns) | UINT32 | RO | 0x00000000 (0dec) |
1C33:06 | Calc and copy time | Time between reading of the inputs and availability of the inputs for the master (in ns, only DC mode) | UINT32 | RO | 0x00000000 (0dec) |
1C33:08 | Command |
The entries 0x1C33:03, 0x1C33:06, 0x1C33:09 are updated with the maximum measured values. | UINT16 | RW | 0x0000 (0dec) |
1C33:09 | Delay time | Time between SYNC1 event and reading of the inputs (in ns, only DC mode) | UINT32 | RO | 0x00000000 (0dec) |
1C33:0B | SM event missed counter | Number of missed SM events in OPERATIONAL (DC mode only) | UINT16 | RO | 0x0000 (0dec) |
1C33:0C | Cycle exceeded counter | Number of occasions the cycle time was exceeded in OPERATIONAL (cycle was not completed in time or the next cycle began too early) | UINT16 | RO | 0x0000 (0dec) |
1C33:0D | Shift too short counter | Number of occasions that the interval between SYNC0 and SYNC1 event was too short (DC mode only) | UINT16 | RO | 0x0000 (0dec) |
1C33:20 | Sync error | The synchronization was not correct in the last cycle (outputs were output too late; DC mode only) | BOOLEAN | RO | 0x00 (0dec) |
Profile-specific objects (0x6000-0xFFFF)
The profile-specific objects have the same meaning for all EtherCAT slaves that support the profile 5001.
Index 60n0 RTD Inputs for 0 ≤ n ≤ 7 (Ch. 1 - 8)
60n0:0 | RTD Inputs | Maximum subindex | UINT8 | RO | 0x11 (17dec) |
60n0:01 | Underrange | The measuring range is undershot. | BOOLEAN | RO | 0x00 (0dec) |
60n0:02 | Overrange | The measuring range is overshot. | BOOLEAN | RO | 0x00 (0dec) |
60n0:07 | Error | The error bit is set if the data is invalid. | BOOLEAN | RO | 0x00 (0dec) |
60n0:0F | TxPDO State | Validity of the data of the associated TxPDO (0 = valid, 1 = invalid). | BOOLEAN | RO | 0x00 (0dec) |
60n0:10 | TxPDO Toggle | The TxPDO toggle is toggled by the slave when the data of the associated TxPDO is updated. | BOOLEAN | RO | 0x00 (0dec) |
60n0:11 | Value | The analog input data | INT16 | RO | 0x0000 (0dec) |
Index 80nE RTD Internal data for 0 ≤ n ≤ 7 (Ch. 1 - 8)
80nE:0 | RTD Internal data | Maximum subindex | UINT8 | RO | 0x04 (4dec) |
80nE:01 | ADC raw value 1 | ADC raw value 1 | INT32 | RO | 0x00000000 (0dec) |
80nE:02 | Resistor 1 | Resistance 1 (measured value of resistance sensor, resolution 1/32 Ohm) | UINT16 | RO | 0x0000 (0dec) |
Index 80nF RTD Vendor data for 0 ≤ n ≤ 7 (Ch. 1 - 8)
80nF:0 | RTD Vendor data | Max. subindex | UINT8 | RO | - |
80nF:01 | Calibration offset | Vendor offset calibration | INT16 | RW | - |
80nF:02 | Calibration gain | Vendor gain calibration | UINT16 | RW | - |
80nF:03 | Calibration offset NTC1 | Vendor offset calibration NTC1 | INT16 | RW | - |
80nF:04 | Calibration gain | Vendor gain calibration NTC1 | UINT16 | RW | - |
80nF:05 | Calibration offset NTC2 | Vendor offset calibration NTC2 | INT16 | RW | - |
80nF:06 | Calibration gain | Vendor gain calibration NTC2 | UINT16 | RW | - |
80nF:07 | RefA_5k | Extended vendor calibration reference resistor 5k | UINT16 | RW | - |
80nF:08 | RefC_5k | Extended vendor calibration reference resistor 5k | UINT16 | RW | - |
80nF:09 | RefA_35k | Extended vendor calibration reference resistor 35k | UINT16 | RW | - |
80nF:0A | RefC_35k | Extended vendor calibration reference resistor 35k | UINT16 | RW | - |
F000:0 | Modular device profile | General information for the modular device profile | UINT8 | RO | 0x02 (2dec) |
F000:01 | Module index distance | Index spacing of the objects of the individual channels | UINT16 | RO | 0x0010 (16dec) |
F000:02 | Maximum number of modules | Number of channels | UINT16 | RO | 0x0008 (8dec) |
Index F008 Code word
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default value |
F008:0 |
currently reserved |
UINT32 |
RW |
0x00000000 (0dec) |
Index F010 Module list [for {n=1} (1-channel) to {n=1,..,n=8} (8-channel)]
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default value |
F010:0 |
Module list |
Maximum subindex |
UINT8 |
RO |
0x08 (ndec) |
F010:0n |
Subindex 00n |
Profile 320 |
INT32 |
RO |
0x00000140 (320dec) |