Settings and application notes for EL3201/2-0010/-0020/-0030
![]()  | Commissioning EL32xx-xxxx The basic EL32xx-xxxx notes in chapter "EL32xx settings" must be observed.  |
The EL3201/EL3202 series is designed for temperature or resistance measurement
- version -0010 offers enhanced measurement precision
 - version -0020 is the factory calibrated version of the EL32xx-0010
 - version -0030 is the variant with external calibration certificate of the EL32xx-0010
Notes regarding EL3201/2-0010/-0020/-0030 series (high-precision)
Due to special features in hardware and firmware, the mentioned terminals are able to measure the resistance value and thus, if necessary, the temperature with high accuracy. Please note:
![]()  | Increased accuracy EL320x-0010/-0020/-0030 In the case of the high-precision terminals the settings in the object 0x80n0 / RTD-Settings may not be changed! The high-precision resistance measurement/temperature measurement can only be performed in the range 10... 220 ohm, this corresponds to a Pt100 measuring range of -200 ... 320°C.   |
Default/factory setting
CoE Index  | EL32xx-0000  | EL320x-0010/-0020/-0030  |
0x80n0:1A (connection technology)  |
 for EL3214 and EL3218:
0x80n00:19 (RTD element)  |
0x80n00:02 (Presentation)  |
0x80n00:07/08 (Enable Limit 1/2) if present  |
0x8000:15 (Filter settings)  |
Area of application
The terminal is calibrated in the measuring range "1/16 Ω" (10 Ω ... 4 kΩ) and can be used in this resistance range. It provides a normal measurement uncertainty in a wide ambient temperature range, see specification.  | The high-precision version is calibrated in the measuring range "1/64 Ω" (10 Ω ... 1 kΩ) and over a measuring range of 18 ... 220 Ω and should only be used in this range or for Pt100 measurements. It provides a comparatively lower measurement uncertainty in the temperature range of a standard switch cabinet environment, see specification.  |