FB_BA_PIDControlSequenceLink
This function block represents the higher-level connection of a sequence control.
Data exchange sequence control
The data exchange between the sequence controllers FB_BA_SeqCtrl and the FB_BA_SequenceLinkBase takes place via the structure stSeqLink.
Start behavior of the sequence
A TRUE signal at input bEn activates the entire sequence control. The function block will initially activate the sequence controller that is known at nNumStartCtrl. All other sequence controller base their output value on the ranking of the active controller.
If the sequence controller specified at nNumStartCtrl is not ready for operation, the enum eNoStartCtrlFound defines the procedure to find a new start controller. This ensures that the sequence always starts.
Switching in the sequence
If a sequence controller reaches its maximum or minimum value, the system switches to the next controller in the sequence depending on the control direction, provided that the actual value falls below or exceeds the setpoint of the next controller.
4 cases are distinguished:
- The still active controller has a direct control direction (cooling, E_BA_Action.eDirect) and is at its maximum value: The next higher controller is selected in the ranking order if the actual value exceeds the setpoint of this controller.
- The still active controller has a direct control direction (cooling, E_BA_Action.eDirect) and is at its minimum value: The next lower controller in the ranking order is selected if the actual value falls below the setpoint of this controller.
- The still active controller has an indirect control direction (heating, E_BA_Action.eReverse) and is at its maximum value: The next lower controller in the ranking order is selected if the actual value falls below the setpoint of this controller.
- The still active controller has an indirect control direction (heating, E_BA_Action.eReverse) and is at its minimum value: The next higher controller is selected in the ranking order if the actual value exceeds the setpoint of this controller.
Switching to another sequence controller can be delayed by specifying the time nSwiOverTi.
Operational readiness of the sequence controllers
If a controller loses its operational readiness in the sequence (missing enable bEn), it is no longer available for the entire sequence.
If this is not the previously active controller, a temperature change may occur, depending on which control value this controller has output, which is compensated by the controller sequence, if possible.
However, if it is the active sequence controller, the enumeration eNoEnableSeqCtrl defines the procedure to find a new, active sequence controller.
If a sequence controller obtains its operational readiness in the running process, the controller is added to the sequence. Depending on the control direction E_BA_Action and its own sequence number nMyNum, it will be placed in the controller sequence and output its minimum or maximum value. The resulting temperature change is compensated by the controller sequence, if possible.
Error detection
The error messages listed below are detected by FB_BA_SequenceLinkBase.
The x in the text messages stands for a numerical specification of a sequence controller.
The error messages are output in the TwinCAT 3 development environment in the "Error list" window. This can be activated under the menu item View.
The error texts are output via the StateText property.
The enumeration eState additionally displays the messages.
![]() | Global parameter Tc3_BA2.BA_Param.nMaxSeqCtrl < 1 This message is the only one that disables sequence control. |
German | English |
Der nächste Sequenzsollwert ist kleiner als sein Vorgänger: x | Next sequence setpoint is smaller than its predecessor: x |
Globaler Parameter Tc3_BA2.BA_Param.nMaxSeqCtrl < 1 | Global parameter Tc3_BA2.BA_Param.nMaxSeqCtrl < 1 |
Mehrfache Wirkrichtung "eActn" in der Sequenzsteuerung | Multiple direction of action "eActn" of the sequence controller |
Startsequenzregler ist nicht freigegeben: nNumStartCtrl = x | Start sequence controller is not enabled: nNumStartCtrl = x |
Kein Sequenzregler ist betriebsbereit | No sequence controller is operational |
Sequenznummer mehrfach vergeben: x | Sequence number assigned multiple times: x |
FUNCTION_BLOCK FB_BA_SequenceLinkBase
bEn : BOOL;
nNumStartCtrl : UDINT;
{attribute 'parameterUnit':= 's'}
nSwiOverTi : UDINT(0..1800);
bSeqCtrlOperational : BOOL;
nActvSeqCtrl : UDINT;
fActvSeqCtrl_Y : REAL;
fActvSeqCtrl_X : REAL;
fActvSeqCtrl_W : REAL;
bActvSeqCtrlIsMaxLimit : BOOL;
bActvSeqCtrlIsMinLimit : BOOL;
bErr : BOOL;
eState : E_BA_StateSeqLink;
nRemTiSwiOvrTi : UDINT;
stSeqLink : ST_BA_SeqLink;
VAR_INPUT CONSTANT
fHys : REAL := 0.2;
eNoStartCtrlFound : E_BA_NoStartCtrlFound := E_BA_NoStartCtrlFound.eLastActionReverse;
eNoEnableSeqCtrl : E_BA_NoEnableSeqCtrl := E_BA_NoEnableSeqCtrl.eNextAction;
Name | Type | Description |
bEn | BOOL | Sequence control is activated when the function block is enabled. However, the sequence controllers must first be enabled. |
nNumStartCtrl | UDINT | Ordinal number of the sequence controller, which should be the start controller when the sequence is activated. An internal limitation allows only values from 1 - BA_Param.nMaxSeqCtrl. |
nSwiOverTi | UDINT | Switching to another sequence controller can be delayed by the time specification. An internal limitation only allows values from 0 - 1800 seconds. |
Outputs
bSeqCtrlOperational | BOOL | The sequence control is ready to operate or is in operation. |
nActvSeqCtrl | UDINT | The output variable shows the number of the active sequence controller. |
fActvSeqCtrl_Y | REAL | Control value of the active sequence controller. |
fActvSeqCtrl_X | REAL | Actual value of the active sequence controller. |
fActvSeqCtrl_W | REAL | Setpoint of the active sequence controller. |
bActvSeqCtrlIsMaxLimit | BOOL | The upper output limit of the active sequence controller has been reached. If it has not yet been advanced to the next sequence controller, bActvSeqCtrlIsMaxLimit is not set to FALSE until fActvSeqCtrl_Y has fallen below (fActvSeqCtrl_Y - fHys). |
bActvSeqCtrlIsMinLimit | BOOL | The lower output limit of the active sequence controller has been reached. If it has not yet been advanced to the next sequence controller, bActvSeqCtrlIsMinLimit is not set to FALSE until fActvSeqCtrl_Y has risen above (fActvSeqCtrl_Y + fHys). |
bErr | BOOL | Indicates that an error has been detected. More detailed information is provided by the property StateText. In addition, the enum eState displays further information. Further explanations on error analysis can be found at Error detection. |
eState | The enumeration shows the state of the FB_BA_SequenceLinkBase and the sequence control. | |
nRemTiSwiOvrTi | UDINT | Countdown of switching to the next sequence controller [s]. |
Inputs Outputs
stSeqLink | Data and command structure between the individual sequence controllers FB_BA_SeqCtrl and the function block FB_BA_SequenceLinkBase. |
Inputs CONSTANT
fHys | REAL | This hysteresis value sets a hysteresis around the upper and lower output limit bActvSeqCtrlIsMaxLimit / bActvSeqCtrlIsMinLimit of the active sequence controller. An internal limitation only allows values from 0 - 2. |
eNoStartCtrlFound | If during the running process the active sequence controller loses its operational readiness, then the enumeration defines the procedure to find a new, active sequence controller. | |
eNoEnableSeqCtrl | If the start controller at the input nNumStartCtrl is not available or enabled, the enumeration defines the procedure to find a new start controller. |
Properties
Name | Type | Access | Description |
FirstActvSeqCtrl | UDINT | Get | The property shows the number of the first sequence controller ready for operation. |
FirstActvSeqCtrlWithActionDirect | UDINT | Get | The property shows the number of the first sequence controller ready for operation with the control direction E_BA_Action.eDirect. |
LastActvSeqCtrl | UDINT | Get | The property shows the number of the last sequence controller ready for operation. |
LastActvSeqCtrlWithActionReverse | UDINT | Get | The property shows the number of the last sequence controller ready for operation with the control direction E_BA_Action.eReverse. |
NextActionActvSeqCtrl | UDINT | Get | Depending on the control direction of the active sequence controller nActvSeqCtrl the next sequence controller ready for operation is displayed here. Cooling/Direct control direction: next sequence controller ready for operation with the Cooling/Direct control direction (after 5 would come 6 or higher). If none is found, then E_BA_NoEnableSeqCtrl.eLastSeqNum is implemented. Heating/reverse control direction: previous operational sequence controller with heating/reverse control direction (after 5 would come 4 or lower). If none is found, then E_BA_NoEnableSeqCtrl.eFirstSeqNum is implemented. |
NextActvSeqCtrl | UDINT | Get | The property shows the number of the next sequence controller ready for operation after the last active one (after 5 would come 6 or higher). |
PreviousActvSeqCtrl | UDINT | Get | The property shows the number of the previous sequence controller ready for operation after the last active one (after 5 would come 4 or lower). |
ActvSeqCtrl | UDINT | Get | The property shows the number of the active sequence controller, see nActvSeqCtrl. |
ActvSeqCtrl_ControlValue | REAL | Get | The property shows the control value of the active sequence controller, see fActvSeqCtrl_Y. |
ActvSeqCtrl_IsMaxLimit | BOOL | Get | The property indicates that the upper output limit of the active sequence controller has been reached, see bActvSeqCtrlIsMaxLimit. |
ActvSeqCtrl_IsMinLimit | BOOL | Get | The property indicates that the lower output limit of the active sequence controller has been reached, see bActvSeqCtrlIsMinLimit. |
ErrorParamMaxSeqCtrl | T_MaxString | Get | The property displays the following text in case of error: "Global parameter Tc3_BA2.BA_Param.nMaxSeqCtrl < 1", see BA_Param.nMaxSeqCtrl. The global parameter must be adjusted in any case, because due to the wrong parameterization the sequence stops. |
ErrorStartSeqCtrlNotOperable | T_MaxString | Get | The property displays the following text in case of error: "Start sequence controller is not enabled: nNumStartCtrl = x". A check of the start sequence controller, which was specified with the input variable nNumStartCtrl, is required. |
MultiDirectionActionSeqCtrl | T_MaxString | Get | The property displays the following text in case of error: Multiple direction of action "eActn" of the sequence controller: x. Multiple direction of action of the sequence controller. It always looks from the sequence controller with the smallest number to the next largest one. It is possible to change the direction of action. |
NextSeqSpIsSmaller | T_MaxString | Get | The property displays the following text in case of error: "Next sequence setpoint is smaller than its predecessor: x". A check of the setpoints of the sequence controllers according to ascending order is required. |
NoSeqCtrlIsOperational | T_MaxString | Get | The property displays the following text in case of an error: "No sequence controller is operational". A check of the operational readiness of the sequence controllers is required. |
SeqNumMulti | T_MaxString | Get | The property displays the following text in case of error: "Sequence number assigned multiple times: x". A check of the displayed sequence number is necessary because it has been assigned several times in the sequence. |
TwinCAT from v3.1.4024.56 | Tc3_BA2 from v5.4.2.0 |