FB_DALI103ResetMemoryBank

FB_DALI103ResetMemoryBank 1:

The values of the selected memory bank of the DALI control device are set to their respective default values by the function block (see Memory banks).

During the reset, the DALI control device does not react to other commands.

The function block also resets the values that are write-protected by the lock byte.

The DALI commands ENABLE WRITE MEMORY, WRITE MEMORY LOCATION – NO REPLY and RESET MEMORY BANK are called internally.

FB_DALI103ResetMemoryBank 2:

The function block changes the DTR0 and the DTR1 of all connected DALI control devices.

FB_DALI103ResetMemoryBank 3:

The function block sends the DALI command RESET MEMORY BANK twice, as foreseen by the DALI standard for certain DALI commands.

FB_DALI103ResetMemoryBank 4:

The function block cannot be used when using the KL6811.

FB_DALI103ResetMemoryBank 5: Inputs

VAR_INPUT
  bStart            : BOOL;
  nAddress          : BYTE;
  eAddressType      : E_DALIAddressType := E_DALIAddressType.Short;
  eCommandPriority  : E_DALICommandPriority := E_DALICommandPriority.MiddleLow;
  nMemoryBank       : USINT := 2;
END_VAR

Name

Type

Description

bStart

BOOL

Execution of the DALI commands is triggered via a positive edge at this input.

nAddress

BYTE

Address of a DALI control device or a DALI group.

eAddressType

E_DALIAddressType

Defines whether the input nAddress contains a short address (0…63) or a group address (0…15). The input nAddress has no meaning if a broadcast or a broadcast to unaddressed devices (BroadcastUnaddr) has been selected.

eCommandPriority

E_DALICommandPriority

Priority (low, middle low, middle, middle high, high) with which the DALI commands are sent.

FB_DALI103ResetMemoryBank 6:

The command priorities are supported by the KL6821 from the firmware version BD.

Name

Type

Description

nMemoryBank

USINT

Specification of the memory bank. If a 0 is specified, all memory banks are reset (except for memory bank 0, as this is read-only). For all other values, only the respective memory bank is reset.

FB_DALI103ResetMemoryBank 7: Outputs

VAR_OUTPUT
  bError                  : BOOL;
  ipResultMessage         : I_TcMessage;
  bBusy                   : BOOL;
END_VAR

Name

Type

Description

bError

BOOL

This output is switched to TRUE if an error occurs during the execution. Further information about the error can be queried via the variable ipResultMessage. The output is set to FALSE again as soon as bBusy switches to TRUE.

ipResultMessage

I_TcMessage

Interface pointer (see error evaluation) that can be used to obtain detailed information about the processing of the function block (see runtime messages). The interface pointer is valid after bBusy has changed from TRUE to FALSE.

bBusy

BOOL

The output is set as soon as execution of the DALI commands has commenced. It remains active until all DALI commands have been processed.

For some errors (e.g. faulty parameters), bError is set immediately after the positive edge at bStart without bBusy switching to TRUE.

FB_DALI103ResetMemoryBank 8: Properties

Name

Type

Access

Initial value

Description

ipDALICommunication

I_DALICommunication

Get, Set

NULL

Interface Pointer to the communication block (see Transfer of the reference to the communication block).

Requirements

Development environment

Required PLC library

TwinCAT from v3.1.4024.10

Tc3_DALI from v3.4.0.0