FB_DALI_Steinel_HF360_II_IPD

FB_DALI_Steinel_HF360_II_IPD 1:

The function block represents the HF 360 II IPD DALI sensor from Steinel.

This outputs the measured brightness value (instance 0), an occupancy signal (instance 1), a temperature value (instance 2) and a value for the relative humidity (instance 3).

Further information on the supported instance types can be found here:

Part 303 (occupancy sensors) - Introduction

Part 304 (light sensors) - Introduction

The existing parameters can be overwritten by changing the properties listed below. All parameters are written to the DALI control device by a positive edge at bInitialize and stored there.

The outputs with the output values of the DALI device only contain valid values if the function block was executed without errors (bError = FALSE). If the output bError = TRUE, the outputs with the output values must not be evaluated.

The temperature measurement and humidity measurement are executed as Generic Inputs. These values can only be queried via a positive edge at the inputs bQueryTemperature and bQueryHumidity.

For the other instances, the reading can also be triggered directly via the inputs bQueryBrightness and bQueryOccupancy, even if the corresponding instance is not enabled.

FB_DALI_Steinel_HF360_II_IPD 2:

Set the times so that as few events as possible are sent. If too many events are sent, this can have a negative effect on the behavior of the application.

FB_DALI_Steinel_HF360_II_IPD 3:

The function block cannot be used when using the KL6811.

FB_DALI_Steinel_HF360_II_IPD 4: Inputs

VAR_INPUT
  bInitialize                 : BOOL  := FALSE;
  nShortAddress               : BYTE  := 0;
  nOptions                    : DWORD := 0;
  bQueryOccupancy             : BOOL  := FALSE;
  bQueryBrightness            : BOOL  := FALSE;
  bQueryTemperature           : BOOL  := FALSE;
  bQueryHumidity              : BOOL  := FALSE;
  bCancelHoldTimerOccupancy   : BOOL  := FALSE;
END_VAR

Name

Type

Description

bInitialize

BOOL

The configuration of the DALI control device is started by a positive edge at this input. During this time no DALI commands are processed.

nShortAddress

BYTE

Short address (0…63) of the DALI control device.

nOptions

DWORD

Reserved for future extensions.

bQueryOccupancy

BOOL

The occupancy is queried immediately by a positive edge at this input.

bQueryBrightness

BOOL

The brightness is queried immediately by a positive edge at this input.

bQueryTemperature

BOOL

The temperature is queried immediately by a positive edge at this input. The DALI device does not support transmission of the temperature per event.

bQueryHumidity

BOOL

The relative humidity is queried immediately by a positive edge at this input. The DALI device does not support transmission of the relative humidity per event.

bCancelHoldTimerOccupancy

BOOL

A positive edge at this input prematurely ends the Hold Timer and resets the output bOccupied.

FB_DALI_Steinel_HF360_II_IPD 5: Outputs

VAR_OUTPUT
  bError                     : BOOL;
  ipResultMessage            : I_TcMessage;
  bInitializing              : BOOL;
  bReadingOccupancy          : BOOL;
  bReadingBrightness         : BOOL;
  bReadingTemperature        : BOOL;
  bReadingHumidity           : BOOL;
  bOccupied                  : BOOL;
  nBrightnessLevel           : UINT;
  fTemperature               : LREAL;
  nHumidity                  : USINT;
END_VAR

Name

Type

Description

bError

BOOL

This output is switched to TRUE if an error occurs during the execution. Further information about the error can be queried via the variable ipResultMessage.

ipResultMessage

I_TcMessage

Interface pointer (see error evaluation) that can be used to obtain detailed information about the processing of the function block (see runtime messages).

bInitializing

BOOL

The output is set as soon as the initialization of the DALI control device has been started, and remains active until all DALI commands have been executed.

bReadingOccupancy

BOOL

The output is TRUE as long as values of the instance of the movement sensor are being read by the DALI control device.

bReadingBrightness

BOOL

The output is TRUE as long as values of the instance of the light sensor are being read by the DALI control device.

bReadingTemperature

BOOL

The output is TRUE as long as values of the instance of the temperature sensor are being read by the DALI control device.

bReadingHumidity

BOOL

The output is TRUE as long as values of the instance of the humidity sensor are being read by the DALI control device.

bOccupied

BOOL

If the output is TRUE, then occupancy has been detected in the detection range of the occupancy sensor.

nBrightnessLevel

UINT

Measured brightness value of the light sensor.

FB_DALI_Steinel_HF360_II_IPD 6:

This measured value must be compared with the measured reference values at the place of operation of the DALI control device.

Name

Type

Description

fTemperature

LREAL

Measured temperature value (-5.0…60.0 °C) of the temperature sensor.

nHumidity

USINT

Measured value of the relative humidity (0…100%).

FB_DALI_Steinel_HF360_II_IPD 7: Properties

All parameters that are written to the DALI control device via bInitialize are available as properties.

Name

Type

Access

Initial value

Description

bEnableBrightness

BOOL

Get, Set

TRUE

If this property is TRUE, the instance for brightness measurement is enabled. If this property is FALSE, sending of events from this instance is disabled. However, the actual value of the instance can still be queried via the input bQueryBrightness.

bEnableOccupancy

BOOL

Get, Set

TRUE

If this property is TRUE, the instance for the occupancy sensor is enabled. If this property is FALSE, sending of events from this instance is disabled. However, the actual value of the instance can still be queried via the input bQueryOccupancy.

bEnableTemperature

BOOL

Get, Set

FALSE

If this property is TRUE, the instance for temperature measurement is enabled. If this property is FALSE, the instance is not configured during initialization. The actual value of the instance can only be queried via the input bQueryTemperature.

bEnableHumidity

BOOL

Get, Set

FALSE

If this property is TRUE, the instance to measure relative humidity is enabled. If this property is FALSE, the instance is not configured during initialization. The actual value of the instance can only be queried via the input bQueryHumidity.

eEventPriorityBrightness

E_DALIEventPriority

Get, Set

MiddleLow

Setting of the event priority.

nReportTimerBrightness

USINT

Get, Set

30 s

Time (0...255 s) after which the pending event of the

light sensor is repeated if no other event has occurred in the meantime.

nDeadtimeTimerBrightness

UINT

Get, Set

1500 ms

Dead time (0...12750 ms) to ensure that not too many events are sent in succession. An event is only sent after expiry of the dead time timer. The dead time timer is restarted each time an event is sent.

nHysteresisBrightness

USINT

Get, Set

20 %

Value (0…25 %) for calculating a hysteresis value in order to prevent frequent and disruptive changes when measuring the brightness.

nHysteresisMinBrightness

USINT

Get, Set

10

As the percentage hysteresis can also lead to large fluctuations at low brightness, a minimum hysteresis can be specified using this property. The minimum hysteresis is an absolute value with a range from 0 to 255.

eEventPriorityOccupancy

E_DALIEventPriority

Get, Set

Middle

Setting of the event priority.

nDeadtimeTimerOccupancy

UINT

Get, Set

100 ms

Dead time (0...12750 ms) to ensure that not too many events are sent in succession. An event is only sent after expiry of the dead time timer. The dead time timer is restarted each time an event is sent.

nDetectionRangeOccupancy

UINT

Get, Set

100 %

Setting of the detection range of the occupancy sensor from 0 % (small detection range) to 100 % (large detection range).

nHoldTimerOccupancy

UINT

Get, Set

900 s

Hold time (1...2538 s) during which the occupancy is still active after no further motion was detected by the sensor.

nReportTimerOccupancy

USINT

Get, Set

20 s

Time (0…255 s) after which the pending event of the occupancy sensor is repeated if no other event has occurred in the meantime.

nSensitivityOccupancy

USINT

Get, Set

100 %

Setting of the sensitivity of the occupancy sensor from 0 % (low sensitivity) to 100 % (high sensitivity).

ipDALICommunication

I_DALICommunication

Get, Set

NULL

Interface pointer to the communication block (see Transfer of the reference to the communication block).

Requirements

Development environment

Required PLC library

TwinCAT from v3.1.4024.25

Tc3_DALI from v3.10.5.0