FB_DALI_Steinel_Hallway_IPD_ECO
The function block represents the Hallway IPD ECO DALI sensor from Steinel.
This outputs the measured brightness value (instance 0) and three occupancy signals (instances 1 to 3).
Further information on the supported instance types can be found here:
Part 303 (occupancy sensors) - Introduction
Part 304 (light sensors) - Introduction
The existing parameters can be overwritten by changing the properties listed below. All parameters are written to the DALI control device by a positive edge at bInitialize and stored there.
The outputs with the output values of the DALI device only contain valid values if the function block was executed without errors (bError = FALSE). If the output bError = TRUE, the outputs with the output values must not be evaluated.
The DALI sensor contains three occupancy sensors. One occupancy sensor (instance 2) is aligned in the direction "S" of the STEINEL lettering on the device, while the second occupancy sensor (instance 3) is aligned in the direction "L". The third occupancy sensor (instance 1) combines both sensors into a single instance.
Never activate all three instances at the same time, as this places an unnecessary load on the DALI bus. Either the two instances for direction "S" and "L" are active or the combined instance is active (default setting). Thus either the properties nXyzDirectionS / nXyzDirectionL or the properties nXyzCombined should be set, but not all at the same time. Setting the properties nXyzCombined overwrites the values of nXyzDirectionS / nXyzDirectionL.
The reading can be triggered immediately via the input variables bQueryBrightness, bQueryOccupancyCombined, bQueryOccupancyDirectionS and bQueryOccupancyDirectionL, even if the corresponding instance is not enabled.
![]() | Set the times so that as few events as possible are sent. If too many events are sent, this can have a negative effect on the behavior of the application. |
![]() | The function block cannot be used when using the KL6811. |
bInitialize : BOOL := FALSE;
nShortAddress : BYTE := 0;
nOptions : DWORD := 0;
bQueryOccupancyCombined : BOOL := FALSE;
bQueryOccupancyDirectionS : BOOL := FALSE;
bQueryOccupancyDirectionL : BOOL := FALSE;
bQueryBrightness : BOOL := FALSE;
bCancelHoldTimerOccupancyCombined : BOOL := FALSE;
bCancelHoldTimerOccupancyDirectionS : BOOL := FALSE;
bCancelHoldTimerOccupancyDirectionL : BOOL := FALSE;
bInitialize | BOOL | The configuration of the DALI control device is started by a positive edge at this input. During this time no DALI commands are processed. |
nShortAddress | BYTE | Short address (0…63) of the DALI control device. |
nOptions | DWORD | Reserved for future extensions. |
bQueryOccupancyCombined | BOOL | The value of the combined occupancy sensor is queried immediately by a positive edge at this input. |
bQueryOccupancyDirectionS | BOOL | The value of the occupancy sensor for direction "S" is queried immediately by a positive edge at this input. |
bQueryOccupancyDirectionL | BOOL | The value of the occupancy sensor for direction "L" is queried immediately by a positive edge at this input. |
bQueryBrightness | BOOL | The brightness is queried immediately by a positive edge at this input. |
bCancelHoldTimerOccupancyCombined | BOOL | A positive edge at this input prematurely ends the hold timer of the combined occupancy sensor and resets the output bOccupiedCombined. |
bCancelHoldTimerOccupancyDirectionS | BOOL | A positive edge at this input prematurely ends the hold timer of the occupancy sensor for direction "S" and resets the output bOccupiedDirectionS. |
bCancelHoldTimerOccupancyDirectionL | BOOL | A positive edge at this input prematurely ends the hold timer of the occupancy sensor for direction "L" and resets the output bOccupiedDirectionL. |
Outputs
bInitializing : BOOL;
bReadingOccupancyCombined : BOOL;
bReadingOccupancyDirectionS : BOOL;
bReadingOccupancyDirectionL : BOOL;
bReadingBrightness : BOOL;
bOccupiedCombined : BOOL;
bOccupiedDirectionS : BOOL;
bOccupiedDirectionL : BOOL;
nBrightnessLevel : UINT;
bError | BOOL | This output is switched to TRUE if an error occurs during the execution. Further information about the error can be queried via the variable ipResultMessage. |
ipResultMessage | I_TcMessage | Interface pointer (see error evaluation) that can be used to obtain detailed information about the processing of the function block (see runtime messages). |
bInitializing | BOOL | The output is set as soon as the initialization of the DALI control device has been started, and remains active until all DALI commands have been executed. |
bReadingOccupancyCombined | BOOL | The output is TRUE as long as values of the instance of the combined motion sensor are being read by the DALI control device. |
bReadingOccupancyDirectionS | BOOL | The output is TRUE as long as values of the instance of the motion sensor for direction "S" are being read by the DALI control device. |
bReadingOccupancyDirectionL | BOOL | The output is TRUE as long as values of the instance of the motion sensor for direction "L" are being read by the DALI control device. |
bReadingBrightness | BOOL | The output is TRUE as long as values of the instance of the light sensor are being read by the DALI control device. |
bReadingTemperature | BOOL | The output is TRUE as long as values of the instance of the temperature sensor are being read by the DALI control device. |
bOccupiedDirectionS | BOOL | If the output is TRUE, then occupancy has been detected in the detection range of the occupancy sensor for direction "S". |
bOccupiedDirectionL | BOOL | If the output is TRUE, then occupancy has been detected in the detection range of the occupancy sensor for direction "L". |
nBrightnessLevel | UINT | Measured brightness value of the light sensor. |
![]() | This measured value must be compared with the measured reference values at the place of operation of the DALI control device. |
Properties
All parameters that are written to the DALI control device via bInitialize are available as properties.
bEnableBrightness | BOOL | Get, Set | TRUE | If this property is TRUE, the instance for brightness measurement is enabled. If this property is FALSE, sending of events from this instance is disabled. However, the actual value of the instance can still be queried via the input bQueryBrightness. |
bEnableOccupancyCombined | BOOL | Get, Set | TRUE | If this property is TRUE, the instance for the combined occupancy sensor is enabled. If this property is FALSE, sending of events from this instance is disabled. However, the actual value of the instance can still be queried via the input bQueryOccupancyCombined. |
bEnableOccupancyDirectionS | BOOL | Get, Set | FALSE | If this property is TRUE, the instance for motion detection in direction "S" is enabled. If this property is FALSE, sending of events from this instance is disabled. However, the actual value of the instance can still be queried via the input bQueryOccupancyDirectionS. |
bEnableOccupancyDirectionL | BOOL | Get, Set | FALSE | If this property is TRUE, the instance for motion detection in direction "L" is enabled. If this property is FALSE, sending of events from this instance is disabled. However, the actual value of the instance can still be queried via the input bQueryOccupancyDirectionL. |
eEventPriorityBrightness | E_DALIEventPriority | Get, Set | MiddleLow | Setting of the event priority. |
nReportTimerBrightness | USINT | Get, Set | 30 s | Time (0...255 s) after which the pending event of the light sensor is repeated if no other event has occurred in the meantime. |
nDeadtimeTimerBrightness | UINT | Get, Set | 1500 ms | Dead time (0...12750 ms) to ensure that not too many events are sent in succession. An event is only sent after expiry of the dead time timer. The dead time timer is restarted each time an event is sent. |
nHysteresisBrightness | USINT | Get, Set | 20 % | Value (0…25 %) for calculating a hysteresis value in order to prevent frequent and disruptive changes when measuring the brightness. |
nHysteresisMinBrightness | USINT | Get, Set | 10 | As the percentage hysteresis can also lead to large fluctuations at low brightness, a minimum hysteresis can be specified using this property. The minimum hysteresis is an absolute value with a range from 0 to 255. |
eEventPriorityOccupancyCombined | E_DALIEventPriority | Get, Set | Middle | Setting of the event priority. |
nDeadtimeTimerOccupancyCombined | UINT | Get, Set | 100 ms | Dead time (0...12750 ms) to ensure that not too many events are sent in succession. An event is only sent after expiry of the dead time timer. The dead time timer is restarted each time an event is sent. |
nDetectionRangeOccupancyCombined | UINT | Get, Set | 100 % | Setting of the detection range of the occupancy sensor from 0 % (small detection range) to 100 % (large detection range). |
nHoldTimerOccupancyCombined | UINT | Get, Set | 900 s | Hold time (1...2538 s) during which the occupancy is still active after no further motion was detected by the sensor. |
nReportTimerOccupancyCombined | USINT | Get, Set | 20 s | Time (0…255 s) after which the pending event of the occupancy sensor is repeated if no other event has occurred in the meantime. |
nSensitivityOccupancyCombined | USINT | Get, Set | 100 % | Setting of the sensitivity of the occupancy sensor from 0 % (low sensitivity) to 100 % (high sensitivity). |
eEventPriorityOccupancyDirectionS | E_DALIEventPriority | Get, Set | Middle | Setting of the event priority. |
nDeadtimeTimerOccupancyDirectionS | UINT | Get, Set | 100 ms | Dead time (0...12750 ms) to ensure that not too many events are sent in succession. An event is only sent after expiry of the dead time timer. The dead time timer is restarted each time an event is sent. |
nDetectionRangeOccupancyDirectionS | UINT | Get, Set | 100 % | Setting of the detection range of the occupancy sensor from 0 % (small detection range) to 100 % (large detection range). |
nHoldTimerOccupancyDirectionS | UINT | Get, Set | 900 s | Hold time (1...2538 s) during which the occupancy is still active after no further motion was detected by the sensor. |
nReportTimerOccupancyDirectionS | USINT | Get, Set | 20 s | Time (0…255 s) after which the pending event of the occupancy sensor is repeated if no other event has occurred in the meantime. |
nSensitivityOccupancyDirectionS | USINT | Get, Set | 100 % | Setting of the sensitivity of the occupancy sensor from 0 % (low sensitivity) to 100 % (high sensitivity). |
eEventPriorityOccupancyDirectionL | E_DALIEventPriority | Get, Set | Middle | Setting of the event priority. |
nDeadtimeTimerOccupancyDirectionL | UINT | Get, Set | 100 ms | Dead time (0...12750 ms) to ensure that not too many events are sent in succession. An event is only sent after expiry of the dead time timer. The dead time timer is restarted each time an event is sent. |
nDetectionRangeOccupancyDirectionL | UINT | Get, Set | 100 % | Setting of the detection range of the occupancy sensor from 0 % (small detection range) to 100 % (large detection range). |
nHoldTimerOccupancyDirectionL | UINT | Get, Set | 900 s | Hold time (1...2538 s) during which the occupancy is still active after no further motion was detected by the sensor. |
nReportTimerOccupancyDirectionL | USINT | Get, Set | 20 s | Time (0…255 s) after which the pending event of the occupancy sensor is repeated if no other event has occurred in the meantime. |
nSensitivityOccupancyDirectionL | USINT | Get, Set | 100 % | Setting of the sensitivity of the occupancy sensor from 0 % (low sensitivity) to 100 % (high sensitivity). |
ipDALICommunication | I_DALICommunication | Get, Set | NULL | Interface pointer to the communication block (see Transfer of the reference to the communication block). |
TwinCAT from v3.1.4024.25 | Tc3_DALI from v3.10.5.0 |