MP_EPIV_R6

MP_EPIV_R6 1:

This function block is used to control a control ball valve of series EP..R-R6+BAC.

MP_Address is used to specify the MP-Bus device with which the function block is to communicate. bStart activates communication with the MP-Bus device. bBusy indicates that the function block is active. If bStart remains TRUE, the device is addressed cyclically with a period specified by the time in TMPolling. The time should be set longer than 1 second. bError is used to indicate an error in communication with the drive. The type of the error can be read with iErrorID.

MP_EPIV_R6 2: Inputs

VAR_INPUT
  MP_Address             : USINT := 1;
  bStart                 : BOOL := TRUE;
  strDataKL6771          : DataKL6771;
  TMpolling              : TIME := t#10s;
  nOverrideControl_Write : E_MPBus_Override_6wayMPIV := MPBus_6wayMPIV_None;
  rSetpoint_Write        : LREAL;
END_VAR

Name

Type

Description

MP_Address

USINT

MP-Bus address of the slave.

bStart

BOOL

A positive edge starts the function block. If this remains continuously TRUE, the function block will be activated cyclically with a period specified by the time in TMPolling.

strDataKL6771

DataKL6771

The data structure with which the KL6771() function block must be linked.

TMpolling

TIME

The time for which the function block should address the actuator. Default 10 s, minimum time 1 s.

nOverrideControl_Write

E_MPBus_Override_6wayMPIV

The relative setpoint is ignored in override control mode. Overriding is disabled if the command is not repeated within 120 minutes.

rSetpoint_Write

LREAL

Setpoint in % (0...100).

MP_EPIV_R6 3: Outputs

VAR_OUTPUT
  bBusy                            : BOOL;
  bError                           : BOOL;
  iErrorId                         : MP_Error;
  nOverrideControl_Read            : E_MPBus_Override_6wayMPIV;
  rSetpoint_Read                   : LREAL;
  rRelativePos_Read                : LREAL;
  rAbsolutePos_Read                : LREAL;
  rRelativeFlow_Read               : LREAL;
  bErrorStateFlowSensorErr         : BOOL;
  bErrorStateActuator_can_not_move : BOOL;
  st_StateEV                       : st_StateEV;
  rAbsoluteFlow_UnitSel            : LREAL;
END_VAR

Name

Type

Description

bBusy

BOOL

This bit is set for as long as the function block is active.

bError

BOOL

This output goes TRUE as soon as an error occurs. This error is described via the iErrorId variable.

iErrorId

MP_ERROR

This output outputs an error code in the event of an error. bError goes TRUE at the same time.

nOverrideControl_Read

E_MPBus_Override_6wayMPIV

Override mode.

rSetpoint_Read

LREAL

Setpoint in % (0...100 %)..

rRelativePos_Read

LREAL

Relative position in % (0...100 %).

rAbsolutePos_Read

LREAL

Absolute position in °.

rRelativeFlow_Read

LREAL

Relative flow rate in % (0...100 %).

bErrorStateFlowSensorErr

BOOL

Flow sensor is faulty.

bErrorStateActuator_can_not_move

BOOL

Actuator cannot move.

st_StateEV

St_StateEV

Only devices from 27 March 2014.

rAbsoluteFlow_UnitSel

LREAL

Absolute flow rate in UnitSel (0...4294967295).

Requirements

Development environment

PLC library to include

TwinCAT from v3.1.4022.14

Tc2_MPBus from 3.4.8.0