ST_StateEV
Information on the state of the EV.
TYPE ST_StateEV :
STRUCT
bFlow_with_closed_valve : BOOL;
bAir_bubbles : BOOL;
bFlow_not_reached : BOOL;
bPower_not_realized : BOOL;
bGear_disengaged : BOOL;
END_STRUCT
END_TYPEbFlow_with_closed_valve: Flow rate when the valve is closed. Check valve.
bAir_bubbles: Too many air bubbles (system venting inadequate). Flow measurement no longer exact. EV switches from volume flow control to position control.
bFlow_not_reached: Flow rate not reached, despite the fact that the ball valve is fully open. Check hydraulics, switch on pump or increase pump pressure.
bPower_not_realized: Power not achieved. In addition to position control and volume flow control, the EV can be used to supply power. Primary side provides too little flow or dT.
bGear_disengaged: Gear disengagement active. Manual adjustment possible on site. For other MP drives this information can be read with MP_Get_State.
Development environment | PLC library to include |
TwinCAT from v3.1.4020.32 | Tc2_MPBus from 3.4.6.0 |