MP_EnergyValveV4_2_Process
This function block is suitable for Energy Valve actuators EV..R2+.. with firmware 4.2.0 or higher. For more information please visit www.belimo.com.
MP_Address is used to specify the MP-Bus device with which the function block is to communicate. bStart activates communication with the MP-Bus device. bBusy indicates that the function block is active. If bStart remains TRUE, the device is addressed cyclically with a period specified by the time in TMPolling. The time should be set longer than 1 second. bError is used to indicate an error in communication with the actuator. The type of the error can be read with iErrorId.
MP_Address : USINT := 1;
bStart : BOOL;
strDataKL6771 : DataKL6771;
TMpolling : TIME := t#10s;
rSetpoint : LREAL;
rAbsoluteDiffWaterPressureSetpoint_Write : LREAL;
nOverrideControl : E_MP_EV_V4_OverrideControl
nCommand : E_MP_EV_V4_Command;
nDataRead : DWORD := 16#000F_FFFF;
MP_Address | USINT | MP-Bus address of the slave. |
bStart | BOOL | A positive edge starts the function block. If this remains continuously TRUE, the function block will be activated cyclically with a period specified by the time in TMPolling. |
strDataKL6771 | The data structure with which the KL6771() function block must be linked. | |
TMpolling | TIME | The time for which the function block should address the actuator. Default 10 s, minimum time 1 s. |
rSetpoint | LREAL | Setpoint in % (0...100). |
rAbsoluteDiffWaterPressureSetpoint_Write | LREAL | Absolute difference water pressure setpoint in kPa (10..400). |
nOverrideControl | Override the setpoint with defined values. | |
nCommand | Command for service and test functions of the actuator. | |
nDataRead | DWORD | 0x000F_FFFF - Read all data |
Outputs
iErrorId : MP_Error;
strMP_Serial_Number : MP_Serial_Number;
rSetpoint_Read : LREAL;
nOverrideControl_Read : E_MP_EV_V4_OverrideControl;
nCommand_Read : E_MP_EV_V4_Command;
rAbsoluteDiffWaterPressureSetpoint_Read : LREAL;
rAbsoluteVolumetricFlowSelUnit : LREAL;
st_MalfunctionService : ST_MP_EV_V4_2_MalfunctionServiceInfo;
rRelativePosition : LREAL;
rAbsolutePosition : LREAL;
nSensor1Value : DINT;
rSetpointAnalog : LREAL;
rRelativeVolumetricFlow : LREAL;
rAbsoluteVolumetricFlow : LREAL;
rGlycolConcentration : LREAL;
rTemperature1_Remote : LREAL;
rTemperature2_Integrated : LREAL;
rDeltaTemperature : LREAL;
rRelativePower : LREAL;
rAbsoluteCoolingPower : LREAL;
rAbsoluteHeatingPower : LREAL;
rTotalVolume : LREAL;
nCoolingEnergy : DINT;
nHeatingEnergy : DINT;
rNominalDiffWaterPressure : LREAL;
rAbsoluteDiffWaterPressure : LREAL;
rRelativeDiffWaterPressure : LREAL;
bBusy | BOOL | This bit is set for as long as the function block is active. |
bError | BOOL | This output goes TRUE as soon as an error occurs. This error is described via the iErrorId variable. |
iErrorId | This output outputs an error code in the event of an error. bError goes TRUE at the same time. | |
strMP_Serial_Number | Structure for the serial number. | |
rSetpoint_Read | LREAL | Setpoint in % (0…100). |
nOverrideControl_Read | Overridden setpoint. | |
nCommand_Read | Command. | |
rAbsoluteDiffWaterPressureSetpoint_Read | LREAL | Absolute difference water pressure setpoint in kPa (10…400). |
rAbsoluteVolumetricFlowSelUnit | LREAL | Absolute volumetric flow in selected unit. |
st_MalfunctionService | ST_MP_EV_V4_2_MalfunctionServiceInfo | Error state. |
rRelativePosition | LREAL | Relative position in % (0…100). A value of -1 means that the data is disabled (see VAR_INPUT nDataRead.0 = TRUE). |
rAbsolutePosition | LREAL | Absolute position in ° (0…96). A value of -1 means that the data is disabled (see VAR_INPUT nDataRead.1 = TRUE). |
nSensor1Value | DINT | Sensor 1 value in mV/ohm (0…65535). A value of -1 means that the data is disabled (see VAR_INPUT nDataRead.2 = TRUE). |
rSetpointAnalog | LREAL | Analog setpoint in % (0…100). A value of -1 means that the data is disabled (see VAR_INPUT nDataRead.3 = TRUE). |
rRelativeVolumetricFlow | LREAL | Relative volume flow rate in % (0…100). A value of -1 means that the data is disabled (see VAR_INPUT nDataRead.4 = TRUE). |
rAbsoluteVolumetricFlow | LREAL | Absolute volume flow rate in l/s (0…100). A value of -1 means that the data is disabled (see VAR_INPUT nDataRead.5 = TRUE). |
rGlycolConcentration | LREAL | Glycol concentration in % (0…100). A value of -1 means that the data is disabled (see VAR_INPUT nDataRead.6 = TRUE). |
rTemperature1_Remote | LREAL | Temperature1 remote in °C (-20…+12). A value of -273 means that the data is disabled (see VAR_INPUT nDataRead.7 = TRUE). |
rTemperature2_Integrated | LREAL | Temperature2 integrated in °C (-20…+12). A value of -273 means that the data is disabled (see VAR_INPUT nDataRead.8 = TRUE). |
rDeltaTemperature | LREAL | Temperature delta in K (0…14). A value of -1 means that the data is disabled (see VAR_INPUT nDataRead.9 = TRUE). |
rRelativePower | LREAL | Relative power in % (0…100). A value of -1 means that the data is disabled (see VAR_INPUT nDataRead.10 = TRUE). |
rAbsoluteCoolingPower | LREAL | Absolute cooling power in kW (0…21.5). A value of -1 means that the data is disabled (see VAR_INPUT nDataRead.11 = TRUE). |
rAbsoluteHeatingPower | LREAL | Absolute heating power in kW (0…21.5). A value of -1 means that the data is disabled (see VAR_INPUT nDataRead.12 = TRUE). |
rTotalVolume | LREAL | Total volume in m³ (0…214748.36). A value of -1 means that the data is disabled (see VAR_INPUT nDataRead.13 = TRUE). |
nCoolingEnergy | DINT | Cooling energy in kWh (0…21474836). A value of -1 means that the data is disabled (see VAR_INPUT nDataRead.14 = TRUE). |
nHeatingEnergy | DINT | Heating energy in kWh (0…21474836). A value of -1 means that the data is disabled (see VAR_INPUT nDataRead.15 = TRUE). |
rNominalDiffWaterPressure | LREAL | Nominal water differential pressure in kPa (0…600). A value of -1 means that the data is disabled (see VAR_INPUT nDataRead.16 = TRUE). |
rAbsoluteDiffWaterPressure | LREAL | Absolute water differential pressure in kPa (0…600). A value of -1 means that the data is disabled (see VAR_INPUT nDataRead.17 = TRUE). |
rRelativeDiffWaterPressure | LREAL | Relative water differential pressure in kPa (0…100). A value of -1 means that the data is disabled (see VAR_INPUT nDataRead.18 = TRUE). |
Prerequisites
TwinCAT from v3.1.4024.66 | Tc2_MPBus from 3.7.1.0 |