MP_TEM_Process
This function block is suitable for the Thermal Energy Meter type 22PE-.. and 22PEM-.. . For more information please visit www.belimo.com.
MP_Address is used to specify the MP-Bus device with which the function block is to communicate. bStart activates communication with the MP-Bus device. bBusy indicates that the function block is active. If bStart remains TRUE, the device is addressed cyclically with a period specified by the time in TMPolling. The time should be set longer than 1 second. bError is used to indicate an error in communication with the actuator. The type of the error can be read with iErrorId.
MP_Address : USINT := 1;
bStart : BOOL;
strDataKL6771 : DataKL6771;
TMpolling : TIME := t#10s;
MP_Address | USINT | MP-Bus address of the slave. |
bStart | BOOL | A positive edge starts the function block. If this remains continuously TRUE, the function block will be activated cyclically with a period specified by the time in TMPolling. |
strDataKL6771 | The data structure with which the KL6771() function block must be linked. | |
TMpolling | TIME | The time for which the function block should address the actuator. Default 10 s, minimum time 1 s. |
Outputs
iErrorId : MP_Error;
strMP_Serial_Number : MP_Serial_Number;
rSensor1Value : LREAL;
rRelativeVolumetricFlow : LREAL;
rAbsoluteVolumetricFlow : LREAL;
rGlycolConcentration : LREAL;
rTemperature1_Remote : LREAL;
rTemperature2_Integrated : LREAL;
rDeltaTemperature : LREAL;
rAbsoluteCoolingPower : LREAL;
rAbsoluteHeatingPower : LREAL;
rTotalVolume : LREAL;
nCoolingEnergy : DINT;
nHeatingEnergy : DINT;
bBusy | BOOL | This bit is set for as long as the function block is active. |
bError | BOOL | This output goes TRUE as soon as an error occurs. This error is described via the iErrorId variable. |
iErrorId | This output outputs an error code in the event of an error. bError goes TRUE at the same time. | |
strMP_Serial_Number | Structure for the serial number. | |
rSensor1Value | LREAL | Sensor 1 Value in mV/ohm (0...65535). |
rRelativeVolumetricFlow | LREAL | Relative volume flow rate in % (0...100). |
rAbsoluteVolumetricFlow | LREAL | Absolute volume flow rate in l/s (0...100). |
rGlycolConcentration | LREAL | Glycol concentration in % (0...100). |
rTemperature1_Remote | LREAL | Temperatur1 remote in °C (-20...12). |
rTemperature2_Integrated | LREAL | Temperature2 integrated in °C (-20...12). |
rDeltaTemperature | LREAL | Temperature delta in K (0...14). |
rAbsoluteCoolingPower | LREAL | Absolute cooling power in kW (0...21.5). |
rAbsoluteHeatingPower | LREAL | Absolute heating power in kW (0...21.5). |
rTotalVolume | LREAL | Total volume in m³ (0...214748.36). |
nCoolingEnergy | DINT | Cooling energy in kWh (0...21474836). |
nHeatingEnergy | DINT | Heating energy in kWh (0...21474836). |
Development environment | PLC library to include |
TwinCAT from v3.1.4024.26 | Tc2_MPBus from 3.4.14.0 |