MP_VRU_Configuration
MP_VRU_Configuration 1:
This function block is used to configure the VAV actuators VRU-D3-BAC, VRU-M1-BAC and VRU-M1R-BAC (max. 8 slaves). For more information please visit www.belimo.com.
MP_Address is used to specify the MP-Bus device with which the function block is to communicate. bStart activates communication with the MP-Bus device. bBusy indicates that the function block is active. bError is used to indicate an error in communication with the actuator. The type of the error can be read with iErrorId.
MP_VRU_Configuration 2: Inputs
  MP_Address       : USINT := 1;
  bStart           : BOOL;
  bRead_Write      : BOOL;
  dwPassword       : DWORD;
  strDataKL6771    : DataKL6771;
  rMax             : LREAL := 100;
  rMin             : LREAL;
  bSetpointSource  : BOOL;
  bOperationMode   : BOOL := TRUE;
  nSensor1Type     : E_MP_VRU_Sensor1Type := MPBus_VRU_Sensor_Active;
Type
MP_Address
USINT
MP-Bus address of the slave.
bStart
A positive edge starts the function block.
bRead_Write
If FALSE then READ only; if TRUE then READ and WRITE.
dwPassword
DWORD
The password for the actuators. Usually 0x0000.
strDataKL6771
DataKL6771
The data structure with which the KL6771() function block must be linked.
rMax
LREAL
Max in % (20...100 %).
rMin
LREAL
Min in % (0...rMax). rMin must be smaller than rMax.
bSetpointSource
TRUE = bus; FALSE = analog
bOperationMode
TRUE = overpressure; FALSE = underpressure
nSensor1Type
Sensor 1 type
MP_VRU_Configuration 3: Outputs
  bBusy                  : BOOL;
  bError                 : BOOL;
  iErrorId               : MP_Error;
  rNominalVolumeticFlow  : LREAL;
  rNominalDeltaPressure  : LREAL;
  rMinRead               : LREAL;
  rMaxRead               : LREAL;
  bSetpointSourcesRead   : BOOL;
  bOperationModeRead     : BOOL;
  nSensor1TypeRead       : E_MP_VRU_Sensor1Type;
  nApplication           : E_MP_VRU_Application;
  bControlMode           : BOOL;
  nRoomPressureCascade   : E_MP_VRU_RoomPressureCascade;
Type
bBusy
This bit is set for as long as the function block is active.
This output goes TRUE as soon as an error occurs. This error is described via the iErrorId variable.
iErrorId
MP_ERROR
This output outputs an error code in the event of an error. bError goes TRUE at the same time.
LREAL
Nominal volume flow in m³/h (0...60,000).
LREAL
Nominal differential pressure in Pa (0...10,000).
rMinRead
LREAL
rMaxRead
LREAL
bOperationModeRead
nSensor1TypeRead
Sensor 1 type
nApplication
Visualization of the application selected by the manufacturer.
bControlMode
Visualization of the control function selected by the manufacturer. TRUE = volume flow rate control; FALSE = position control.
Room pressure cascade control
Development environment
PLC library to include
TwinCAT from v3.1.4024.22
Tc2_MPBus from 3.4.13.0