FB_DALIV2QueryFailureStatus
FB_DALIV2QueryFailureStatus 1:
The variable FAILURE STATUS is read from the control gear.
Bit
Error in the control gear circuit. 0: no.
1
Battery operation time fault. 0: no.
2
Battery fault. 0: no.
3
Emergency lamp fault. 0: no.
4
Timeout during function test. 0: no.
5
Timeout during duration test. 0: no.
6
Function test failed. 0: no.
7
Duration test failed. 0: no
FB_DALIV2QueryFailureStatus 2:
This command belongs to the application extended commands for DALI emergency lighting. These only work if they are preceded by the Enable Device Type 1 command, which can be sent with the function block FB_DALIV2EnableDeviceType. The Enable Device Type 1 command is internally placed automatically before all application extended commands for DALI emergency lighting.
FB_DALIV2QueryFailureStatus 3: Inputs
  bStart           : BOOL;
  nAddr            : BYTE;
  eAddrType        : E_DALIV2AddrType := eDALIV2AddrTypeShort;
  eCommandPriority : E_DALIV2CommandPriority := eDALIV2CommandPriorityMiddle;
Type
bStart
The function block is activated by a positive edge at this input.
nAddr
BYTE
The address of a device or of a group
eAddrType
E_DALIV2AddrType
Short address, group address or broadcast
eCommandPriority
Priority (high, medium or low) with which the command is processed by the library.
FB_DALIV2QueryFailureStatus 4: Inputs/outputs
  stCommandBuffer : ST_DALIV2CommandBuffer;
Type
stCommandBuffer
Reference to the internal structure for communication with FB_KL6811Communication (KL6811) or FB_KL6821Communication (KL6821).
FB_DALIV2QueryFailureStatus 5: Outputs
  bBusy          : BOOL;
  bError         : BOOL;
  nErrorId       : UDINT;
  nFailureStatus : BYTE;
Type
bBusy
This output is switched to TRUE as soon as an error occurs during the execution of a command. The command-specific error code is contained in nErrorId. Is reset to FALSE by the execution of a command at the inputs.
nErrorId
UDINT
Contains the command-specific error code of the most recently executed command. Is reset to 0 by the execution of a command at the inputs (see error codes).
nFailureStatus
BYTE
Control gear failure status (see table above)
Development Environment
PLC library to include
TwinCAT from v3.1.4020.14
Tc2_DALI from v3.4.3.0