FB_KL6821Communication
The function blocks for the DALI commands do not directly access the process image of the DALI Bus Terminal, but store the individual DALI commands in three different buffers. The function block FB_KL6821Communication sequentially reads the DALI commands from these three buffers and forwards the DALI commands to the KL6821. This prevents several function block accessing the process image of the bus terminal at the same time. Each of these three buffers is processed with a different priority (high, medium or low). The parameter eCommandPriority, which is available for most function blocks, can be used by the PLC library user to influence the priority with which the respective DALI command is processed by the function block FB_KL6821Communication.
All buffers in which the DALI commands are stored are associated with a variable of type ST_DALIV2CommandBuffer. For each KL6821 there is one instance of the function block FB_KL6821Communication and one variable of type ST_DALIV2CommandBuffer. If possible, the function block FB_KL6821Communication should be called in a separate, faster task.
The extent to which the buffers are utilized can be determined from the outputs of the function block. Three arrays are output for this in which each element (0, 1 or 2) represents one of the three buffers (high, middle or low). If you find that one of the three buffers overflows on a regular basis, you should consider the following measures:
How heavily are the individual PLC tasks utilized? The TwinCAT System Manager offers various appropriate utilities for the analysis.
- Try to reduce the cycle time of the task in which the function block FB_KL6821Communication is called. The value should not exceed 6 ms. Ideally it should be 2 ms.
- Check the cycle time of the PLC task in which the function blocks for the individual DALI commands are called. This value should be between 10 ms and 60 ms.
- If possible avoid polling (regular reading) of values. Only read values when they are actually required.
- Distribute the individual control gears evenly over several DALI lines. Overall data throughput is increased by the fact that several DALI lines are processed simultaneously during each PLC cycle.
bResetMaximumDemandCounter : BOOL;
bResetOverflowCounter : BOOL;
bResetInactiveProcessImage : BOOL;
nOptions : DWORD := 0;
Name | Type | Description |
bResetMaximumDemandCounter | BOOL | A positive edge resets the stored value of the maximum command buffer utilization, arrBufferMaximumDemandMeter (0 - 100 %, see VAR_OUTPUT). |
bResetOverflowCounter | BOOL | A positive edge resets the stored value of the number of command buffer overflows, arrBufferOverflowCounter (see VAR_OUTPUT). |
bResetInactiveProcessImage | BOOL | A positive edge cancels the blocking of the process image of the terminal. The outputs bProcessImageInactive, bDigitalInput1Active and bDigitalInput2Active are again set to FALSE. The lock is activated when one of the two digital inputs on the terminal is activated. |
nOptions | DWORD | Reserved for future developments. |
Inputs/outputs
stInData : ST_KL6821InData;
stOutData : ST_KL6821OutData;
stInData | ST_KL6821InData | Structure in the input process image of the KL6821. It is used for communication from the KL6821 to the PLC. When using FB_KL6821Config, this structure is linked to the parameter stInData. |
stOutData | ST_KL6821OutData | Structure in the output process image of the KL6821. It is used for communication from the PLC to the KL6821. When using FB_KL6821Config, this structure is linked to the parameter stOutData. |
stCommandBuffer | ST_DALIV2CommandBuffer | Reference to the internal structure for communication with the DALI function blocks. |
Outputs
nErrorId : UDINT;
arrBufferDemandMeter : ARRAY [0..2] OF BYTE;
arrBufferMaximumDemandMeter : ARRAY [0..2] OF BYTE;
arrBufferOverflowCounter : ARRAY [0..2] OF UINT;
bLineIsBusy : BOOL;
bLineIsInitialized : BOOL;
bDigitalInput1Active : BOOL;
bDigitalInput2Active : BOOL;
bProcessImageInactive : BOOL;
bCollisionError : BOOL;
bPowerSupplyError : BOOL;
bShortCircuit : BOOL;
bBusy | BOOL | When the function block is activated the output is set, and it remains active until execution of the command has been completed. |
bError | BOOL | This output is switched to TRUE as soon as an error occurs during the execution of a command. The command-specific error code is contained in nErrorId. Is reset to FALSE by the execution of a command at the inputs. |
nErrorId | UDINT | Contains the command-specific error code of the most recently executed command. Is reset to 0 by the execution of a command at the inputs (see error codes). |
arrBufferDemandMeter | ARRAY OF BYTE | Demand of the respective buffer (0 - 100 %) |
arrBufferMaximumDemandMeter | ARRAY OF BYTE | Previous maximum demand of the respective buffer (0 - 100 %) |
arrBufferOverflowCounter | ARRAY OF BYTE | Number of buffer overflows so far |
bLineIsBusy | BOOL | The output is set as long as the function block FB_KL6821Communication is active. |
bLineIsInitialized | BOOL | If the function block is called for the first time (e.g. when starting the controller), initialization is carried out. No DALI commands can be processed during this time. |
bDigitalInput1Active | BOOL | The digital input 1 on the terminal was or is actuated (see also terminal documentation). The output bProcessImageInactive is set and no further DALI commands can be processed by the controller. |
bDigitalInput2Active | BOOL | The digital input 2 on the terminal was or is actuated (see also terminal documentation). The output bProcessImageInactive is set and no further DALI commands can be processed by the controller. |
bProcessImageInactive | BOOL | One of the two digital inputs was actuated at the terminal. No further DALI commands can be processed by the controller. The blockage must be released again via the input bResetInactiveProcessImage. |
bCollisionError | BOOL | A data collision on the DALI bus was detected while a command was sent. |
bPowerSupplyError | BOOL | The KL6821 has detected an error in the internal DALI power supply. |
bShortCircuit | BOOL | Short circuit on the DALI bus |
TwinCAT from v3.1.4022.4 | Tc2_DALI from v3.6.2.0 |
