Supply voltage output X60 (only EP7402-0057 and EP7402-0067)
The supply voltage output is intended for EtherCAT devices that are connected to EtherCAT junction X40.
CAUTION
The outgoing peripheral voltage Up' is not switched off if you switch off the incoming peripheral voltage UP.
(EP7402-0057 from hardware 03, EP7402-0067 from hardware 00)
Actuators at the supply voltage output remain active.
  • To safely switch off actuators at the supply voltage output, use TwinSAFE components.
Notice
The outgoing supply voltages are not electrically isolated.
The analog specifications of EtherCAT Box modules with analog inputs or outputs may not be met under certain circumstances.
Supply voltage output X60 (only EP7402-0057 and EP7402-0067) 1:
Fig.2: M8 socket
Contact
Symbol
Wire color
1
24V Us'
Control voltage
Brown
2
24V Up'
Peripheral voltage 1)
White
3
GND
Common ground potential for both output voltages 2)
Blue
4
GND
Black
1) Up‘ is branched off from different supply voltages, depending on the hardware version:
  • From hardware version 03:
    Up‘ is branched off from the incoming control voltage US at X70.
  • Up to and including hardware version 02:
    Up‘ is branched off from the incoming peripheral voltage UP at X70.
2) Up to and including hardware version 02: GNDS is connected to pin 3, GNDP to pin 4. Starting with hardware version 03, both pins are connected to the same ground potential GNDS.
Suitable connection cables can be found in the chapter Accessories.